Compact manual transfer switches
mike93lx
Richmond, VA
This is part of the planning for the automated battery backup I have a thread going on.
The inverter will do the automated switching, but I want to have a way to bypass the inverter and keep the circuits powered up. I am tight on space, so I am hoping to find something fairly compact. Could be rated as low as 50a 120v (inverter will be 120v and either 3kva or 5kva)
Not interested in no-name imported junk on Amazon or Ali-x.
Any suggestions?
larry4406
Northern Virginia
Mike - do any of this work? No experience with any of them, just google-fu
PCustoms
VT
I'm probably not understanding correctly, but a small sub panel and a manual interlock?
mike93lx
Richmond, VA
I think I need to sketch this out.
I dont think an interlock will work. The feed into that breaker would be from the main panel, then the inverter would feed the lugs in the sub. Problem is that the line from the inverter would be energized if I flip the interlocked breaker.
I have to disconnect the inverter feed and switch over to utility feed in one throw
mike93lx
Richmond, VA
Thanks. The reliance picture was distorted and made it look really tall. That size is about perfect
mike93lx
Richmond, VA
This Pic from a user on diysolar shows what I'm thinking, I'm just planning on a single inverter and 120v
mike93lx
Richmond, VA
If you're sure how many circuits you want to back up (don't want to add any in the future), these units from Reliance Controls perform that function all-in-one. Unless you don't want to individually switch each load. Just connect the inverter via the generator connection. Integrates the function of the transfer switch and subpanel.
https://www.reliancecontrols.com/products/category/pro-tran-transfer-switches/8
No, that won't work. The inverters cut over automatically when power is lost, so tying it into the generator input will make it a manual cutover
jimbee
The circuits in the Pro/Tran transfer box would normally be set to generator(inverter) feed. Analogous to the "A" position the 100 Amp Manual Transfer Switch in your diagram.
larry4406
Northern Virginia
Mike - I thought I saw that some of the Victron units have generator input in addition to grid input along with battery. It’s smarts then select the input to use. 🤷‍♂️.
mike93lx
Richmond, VA
Ah, I got you now, my bad. Yes, that's a good idea..
I was planning to use a homeline sub so I can reuse all the breakers in my current panels. I'll have to see how it all compares on cost and sizing. One panel would be great
mike93lx
Richmond, VA
Yes, they do. The goal with this transfer switch is to be able to take the victron out of the system entirely. Thinking about a failure on the inverter or something needs to be worked on, and I don't want to take the critical circuits down
larry4406
Northern Virginia
Neat and clean.
Following along….
mike93lx
Richmond, VA
In my last two houses, I installed Reliance Controls main panels that had integrated transfer switches (xrr1003c, IIRC). 100a main, 30a generator breaker, and they were around 24 spacesz accepted breakers from several manufacturers.
That line's discontinued, but they replaced it with something similar, just a 200a main... And the price went up a bunch. This one is about $700. Considering my space constraints, I might go for it, though. Being able to use my existing homeline breakers is nice.
larry4406
Northern Virginia
In your first post you said could be as low as 50A 120V minimum.
This Reliance panel has a 240V 30A generator breaker. Are you now thinking of a 240V battery system?
mike93lx
Richmond, VA
No, still 120v. The 50a rating was to have room to upgrade.
The reliance panels are available with a 50a generator breaker as well. I was just noting that I had previously used 30a inlets.
I am very likely going to install a single 3kva inverter and if I want to expand, I'd add a second and do split phase at that point