Well-known member
I have a compressor location wired with 8/2+G from my load center, and have a 50A breaker installed currently to feed this circuit.
I may use a compressor that requires this much amperage, or I may not. Assuming I install a compressor that needs a 30A breaker, I'd downsize the breaker accordingly.
I want/need to have a disconnect switch at the compressor location, which is 40' from the load center, but not line-of-sight due to the bathroom poking out of that side wall.
I own a 100A single-phase fused disconnect switch that I'd like to utilize for the compressor disconnect, since I already have it. Given that the load center breaker will be sized properly for the compressor, is there any issue with the disconnect being fused at 100A?