Compressor Disconnect Switch question

Steevo

Well-known member
Joined
Aug 18, 2009
Messages
8,738
Location
43.49600, -112.04300
I have a compressor location wired with 8/2+G from my load center, and have a 50A breaker installed currently to feed this circuit.

I may use a compressor that requires this much amperage, or I may not. Assuming I install a compressor that needs a 30A breaker, I'd downsize the breaker accordingly.

I want/need to have a disconnect switch at the compressor location, which is 40' from the load center, but not line-of-sight due to the bathroom poking out of that side wall.

I own a 100A single-phase fused disconnect switch that I'd like to utilize for the compressor disconnect, since I already have it. Given that the load center breaker will be sized properly for the compressor, is there any issue with the disconnect being fused at 100A?
 
To avoid these ads, REGISTER NOW!
To avoid these ads, REGISTER NOW!
OP
S

Steevo

Well-known member
Joined
Aug 18, 2009
Messages
8,738
Location
43.49600, -112.04300
8 AWG NM (Romex) is only rated for 40A.

No problem. I do not see me putting in a 7HP compressor, more likely something around 5HP, so probably in the 30A start-up range.

I was just wondering if using the fused disconnect was going to be an issue.

I forgot to mention, but obviously I am talking a two-pole breaker and 230v motor.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,774
With proper overcurrent protection at the panel, as long as the lugs on the switch are rated to accept the 8 AWG, I see no issue w/ a 100A disco.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
What they are trying to say is that with the #8 wire, you should not have over a 40 amp breaker at the panel. The breaker is there to protect the wire, not the device at the end (compressor). The compressor most likely has a thermal overload in the motor that will shut it off if it gets too hot.

You should change the 50 amp breaker to a 40, to properly protect the #8 wire. As far as the disconnect, it doesn't even have to have fuses, it only needs to be a switch rated to carry at least the same amperage as the supply breaker. The 100 amp fuses are like having no fuse at all, and just a switch, so it is not an issue.

Charles
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,774
What they are trying to say is that with the #8 wire, you should not have over a 40 amp breaker at the panel. The breaker is there to protect the wire, not the device at the end (compressor). The compressor most likely has a thermal overload in the motor that will shut it off if it gets too hot.

You should change the 50 amp breaker to a 40, to properly protect the #8 wire. As far as the disconnect, it doesn't even have to have fuses, it only needs to be a switch rated to carry at least the same amperage as the supply breaker. The 100 amp fuses are like having no fuse at all, and just a switch, so it is not an issue.

Charles

If the compressor motor is a 5 HP, & has overload protection, then the 50A is OK, in that case the circuit breaker is only there for short circuit protection.
 