2HP 230V 12A 1PH Sears compressor on wheels (See photos).
Motor has built in overcurrent protection (Red button).
Motor is continuous duty 40C, insul. B.
Panel is 20' from receptacle.
In addition to cord on the machine, I will be using a 40' extension cord of #12.
First, sizing the branch circuit conductors:
I see that in 430.238, a 2HP 230V 1PH motor is rated at 12FLA. At 125% that's a 15A circuit and #14 wire.I'd like to use a 20A circuit and #12 THHN in PVC conduit. That should take care of conductor sizing.
For Branch-circuit protection for short-circuits and ground-faults, the breaker can't exceed 250% of nameplate FLA. Here that is 12A so breaker max is 30A.
Are we good so far?
What 20A outlet may I use for this circuit? Must it be rated for a 2HP motor?
Bill
Motor has built in overcurrent protection (Red button).
Motor is continuous duty 40C, insul. B.
Panel is 20' from receptacle.
In addition to cord on the machine, I will be using a 40' extension cord of #12.
First, sizing the branch circuit conductors:
I see that in 430.238, a 2HP 230V 1PH motor is rated at 12FLA. At 125% that's a 15A circuit and #14 wire.I'd like to use a 20A circuit and #12 THHN in PVC conduit. That should take care of conductor sizing.
For Branch-circuit protection for short-circuits and ground-faults, the breaker can't exceed 250% of nameplate FLA. Here that is 12A so breaker max is 30A.
Are we good so far?
What 20A outlet may I use for this circuit? Must it be rated for a 2HP motor?