Compressor switched through lighting.

MFortie

Well-known member
Joined
Aug 9, 2010
Messages
921
Location
San Diego County
Decided to start a separate thread so as not to distract too much from the OP's thread: https://www.garagejournal.com/forum/threads/on-off-light-for-compressor.490716/#post-9355337

I would like to setup my compressor to be 'switched' along with the lighting. This is the contactor I found: https://www.amazon.com/gp/product/B07GSC14G4/?tag=atomicindus08-20 for the project. My compressor is on the other side of the MH and there isn't any room to walk in front/behind, so I have to exit and go in the other door to turn it on/off.

This is my wiring diagram (along with a couple of questions):
Comp Layout.jpg


Am I on the right track?

The contactor will be housed in a j-box mounted just under the subpanel (surface mounted on a backboard).

The compressor is a Quincy QT-54, 5HP, 24A, 5' (+/-) from the subpanel.

TIA.
 
To avoid these ads, REGISTER NOW!

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
18,008

easier IMO.
 
OP
M

MFortie

Well-known member
Joined
Aug 9, 2010
Messages
921
Location
San Diego County
Well, more wiring would be required to add the switch by the door (where the light switches are). Plus I have O/H rollup doors to navigate that aren't shown. The lighting j-box (for that bank) is only 15' or so from the subpanel. My lighting is split into (3) 'bays' and I have multiple 4-lamp T8 fixtures in each bay. I typically only flip on two of the lamps at a time (they're independently wired in sets of two), so I was going to use the switch for the lamps I don't usually turn on for the compressor contactor.
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
18,008
Well, more wiring would be required to add the switch by the door (where the light switches are). Plus I have O/H rollup doors to navigate that aren't shown. The lighting j-box (for that bank) is only 15' or so from the subpanel. My lighting is split into (3) 'bays' and I have multiple 4-lamp T8 fixtures in each bay. I typically only flip on two of the lamps at a time (they're independently wired in sets of two), so I was going to use the switch for the lamps I don't usually turn on for the compressor contactor.

bring the pressure switch wires up to an overhead light and use a 120-120 contactor there to control it.
 
To avoid these ads, REGISTER NOW!

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,996
Location
Fargo, ND
Looks ok to me, but as far as code? I don't know.

I assume the motorized valve is to shut off the air outlet on the compressor? I assume the valve take very little power.
 

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
3,030
Location
Peace Valley,mo
Use a 24vac contactor at the compressor, at light switch 40 va transformer 120 x24vac run 18 gauge thermostat wire from transformer to contactor. Light świtch change it to a two pole switch one pole for lights one for transformer.
 
OP
M

MFortie

Well-known member
Joined
Aug 9, 2010
Messages
921
Location
San Diego County
Thank you for the alternate suggestions, but I’m planning to go with the relay off the lighting circuit as I posted. I already have most everything (the relay will be here this week).

My pathways are existing as well.

What I basically needed to know is whether my wiring diagram is correct, and less importantly, if my plan to pass the conductors through the panel is acceptable. Not having this inspected, but prefer to be code compliant.
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
18,008
312.8 nec covers panelboards as raceways. given its not low voltage i personally would wire it up and not give a ****.

only one is required to break the circuit

the motorized valve: it spring closes when power cut? is it 100% duty cycle rated for when its on?
 
OP
M

MFortie

Well-known member
Joined
Aug 9, 2010
Messages
921
Location
San Diego County
Thank you. I figured as much.

As to the valve, yes, spring loaded. It's made for the application, so I presume 100% duty cycle. Cutsheet below:
1639531345217.png
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
18,008
yup. just making sure it wasn't a solenoid valve. those have a duty cycle rating and can burn out.

side thought: it'd be interesting to use a photo eye to trigger this. would need to invert the signal somehow. but it could be localized to the compressor area and just point up at your lights.
 
Last edited: