Concealed duct mini splits, do I need duct work?

PirateToast

Active member
Joined
Dec 6, 2021
Messages
37
Hey, I'm looking at a concealed duct mini split system (I can't seem to find a 60K BTU single zone system with low temperature handling with any other type of handler). Link to what I'm looking at below. Do I actually need to install duct work? Or could I just hang this inside the garage and go?

 
To avoid these ads, REGISTER NOW!

kyrbz

Well-known member
Joined
Jan 30, 2012
Messages
1,305
Location
midwest US
There won’t be duct work, but you‘ll have a line set that runs to your outdoor unit
 
OP
P

PirateToast

Active member
Joined
Dec 6, 2021
Messages
37
Is this for a garage?
As is you will need to build a box around it, or duct to make it more estheticly pleasing. Also this type is less efficient then the usual wall mounted units .

Like I said, I can't find one. The aesthetics look fine for me, it is for a garage.
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,047
you'll need to see if it has a filter rack of if you need to provide one. I think it's the latter, and I'd suggest something like a standard 2" filter at an angle. e.g. QTY 2, 24"x24" filters at an angle to maintain low profile.

something that looks like this:
1726847585228.png
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,660
Location
Austin, TX
That works out just fine then.
How big is your garage? 60k makes me think you've got something BIG. Ductless systems are a bit directional... It might be better to split it into 2 x 30K systems in a larger space.

I'll bet someone will come by with a "hack" for low temperature handling... (assuming you want these to turn on below allowable set temperatures).

Make sure the unit is efficient in low temps. My units are not. Overlooking that could blow this whole thing up.
 
OP
P

PirateToast

Active member
Joined
Dec 6, 2021
Messages
37
How big is your garage? 60k makes me think you've got something BIG. Ductless systems are a bit directional... It might be better to split it into 2 x 30K systems in a larger space.

I'll bet someone will come by with a "hack" for low temperature handling... (assuming you want these to turn on below allowable set temperatures).

Make sure the unit is efficient in low temps. My units are not. Overlooking that could blow this whole thing up.
48X32 with 11' ceilings. I've gotten all sorts of mixed messages on what sizing to go with. Keep in mind this is in Minnesota, so it gets cold. 60K seems to be the biggest I can get with a single zone.
 
OP
P

PirateToast

Active member
Joined
Dec 6, 2021
Messages
37
you'll need to see if it has a filter rack of if you need to provide one. I think it's the latter, and I'd suggest something like a standard 2" filter at an angle. e.g. QTY 2, 24"x24" filters at an angle to maintain low profile.

something that looks like this:
1726847585228.png
I'm not really following the context of this? What does the filter rack mean?
 
OP
P

PirateToast

Active member
Joined
Dec 6, 2021
Messages
37
Your not going to find one, you make it or leave the electric connections and lineset exposed.
I found just one, but it was out of stock. I'm fine leaving the electric and line set exposed. I'm sure I can run that into the ceiling so it's more subtle.
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,660
Location
Austin, TX
48X32 with 11' ceilings. I've gotten all sorts of mixed messages on what sizing to go with. Keep in mind this is in Minnesota, so it gets cold. 60K seems to be the biggest I can get with a single zone.
Insulation?

I have a 2400 sqft shop and I was "shopping" for a solution just like you (course, it's more about cooling). What I found was that I could do multiple smaller systems for below the cost of a larger one. Multiple systems help work around the "directionality" problem of ductless units, you can spread them out. And certainly 60k will be way overkill for MN if you ever use it for cooling.

Again, it's super important that you watch that unit's ability to heat. 60K BTU may not be what it puts out at 20 degrees. I ended up supplementing with ductless propane wall units (a few hundred bucks) but we get very few cold days.
 
Last edited:
OP
P

PirateToast

Active member
Joined
Dec 6, 2021
Messages
37
Insulation?

I have a 2400 sqft shop and I was "shopping" for a solution just like you (course, it's more about cooling). What I found was that I could do multiple smaller systems for below the cost of a larger one. Multiple systems help work around the "directionality" problem of ductless units, you can spread them out. And certainly 60k will be way overkill for MN if you ever use it for cooling.

Again, it's super important that you watch that unit's ability to heat. 60K BTU may not be what it puts out at 20 degrees. I ended up supplementing with ductless propane wall units (a few hundred bucks) but we get very few cold days.
Right, kind of apples to oranges to compare a warm weather climate vs cold. I'm not worried about A/C at all, calculations show I'm way overboard there. Heating is the main issue. I know people talk about multiple smaller systems, but pricing it out, I find it more expensive. Plus I have to install it multiple times then...

I guess my main question is the original, do I need any duct work on that thing? :)
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,047
I'm not really following the context of this? What does the filter rack mean?
coils need clean air. units meant to be concealed are often "installer provided" for filters.

you can't just run it without a filter. well, ok, you can. but if you've ever paid someone to clean a coil in an AC in a wood shop, well, you'd rather have the filter.
 
To avoid these ads, REGISTER NOW!

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,660
Location
Austin, TX
I guess my main question is the original, do I need any duct work on that thing? :)
For heating? Assuming this is "open" 1200 sqft, I'd say that you'd just need some ceiling fans running in reverse to distribute the air, but it will be warmer on the "heated end" of the shop.
 

Firebrick43

Well-known member
Joined
May 12, 2015
Messages
14,004
Location
West central Indiana
Hey, I'm looking at a concealed duct mini split system (I can't seem to find a 60K BTU single zone system with low temperature handling with any other type of handler). Link to what I'm looking at below. Do I actually need to install duct work? Or could I just hang this inside the garage and go?

Have you read the specs on the link you provided?????

The title says 60k but it says 24k much further down and then 36k heating and 36k cooling in the spec block while still saying it’s a 5 ton system.

I would not trust a thing that retailer is advertising.
 

chinboys

Well-known member
Joined
Jun 20, 2011
Messages
434
Why not buy a 5 ton heat pump that can drive multiple zones that add up to 5 tons?

A rule of thumb in commercial cooling is to have 400 ft3 of air per ton of cooling at the blower output.
That means 2000 ft3 of air leaving the induct evaporator squirrel cage fan assembly. make sure the blower can manage this volume of air.
However, if you distribute the cooling load across 3-4 zones using multiple wall-hanging evaporator units, their blower output can be lower.
 

ratflinger

Well-known member
Joined
Jul 7, 2016
Messages
322
Location
South Central Texas
Here's a 36K Pioneer - 2 of them come in cheaper than that questionable unit you are looking at.

 

Firebrick43

Well-known member
Joined
May 12, 2015
Messages
14,004
Location
West central Indiana
Here's a 36K Pioneer - 2 of them come in cheaper than that questionable unit you are looking at.

And gives some capacity if one breaks down to boot!
 
OP
P

PirateToast

Active member
Joined
Dec 6, 2021
Messages
37
Have you read the specs on the link you provided?????

The title says 60k but it says 24k much further down and then 36k heating and 36k cooling in the spec block while still saying it’s a 5 ton system.

I would not trust a thing that retailer is advertising.

I've talked with multiple people on the phone. Seems like just a bug on their site confusing which model you selected. The website has pretty solid reviews from what I've seen.

Here's a 36K Pioneer - 2 of them come in cheaper than that questionable unit you are looking at.


This advertises to -13, the other says to -22. Seems about the same price, but more work.

Why not buy a 5 ton heat pump that can drive multiple zones that add up to 5 tons?

A rule of thumb in commercial cooling is to have 400 ft3 of air per ton of cooling at the blower output.
That means 2000 ft3 of air leaving the induct evaporator squirrel cage fan assembly. make sure the blower can manage this volume of air.
However, if you distribute the cooling load across 3-4 zones using multiple wall-hanging evaporator units, their blower output can be lower.
Why do I need multiple zones for a single space? That's what I struggle with understanding.
 

ratflinger

Well-known member
Joined
Jul 7, 2016
Messages
322
Location
South Central Texas
I've talked with multiple people on the phone. Seems like just a bug on their site confusing which model you selected. The website has pretty solid reviews from what I've seen.



This advertises to -13, the other says to -22. Seems about the same price, but more work.


Why do I need multiple zones for a single space? That's what I struggle with understanding.
-22?? ****, I'd move.
 
OP
P

PirateToast

Active member
Joined
Dec 6, 2021
Messages
37
-22?? ****, I'd move.
Haha. I want to be able to use it in winter!

What do those low temps advertised mean exactly anyways? If it says -13, will it still work below -13, just inefficiently? Or is it a complete shutoff? Does it still work well at -10?
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,047
Haha. I want to be able to use it in winter!

What do those low temps advertised mean exactly anyways? If it says -13, will it still work below -13, just inefficiently? Or is it a complete shutoff? Does it still work well at -10?
the 5 ton LG split at work says works down to -15F. it works down to -20F in practice, errored out at -22F.
 

T444e

Well-known member
Joined
Feb 25, 2016
Messages
448
Why do I need multiple zones for a single space?
You don't. If you want, you could duct it to get more even air distribution.
I'm working on installing a 1.5t split system with a fan coil unit ducting it out for better air distribution, only in half the 1800 sf building, I may stub it into the other half if needed.
 

Firebrick43

Well-known member
Joined
May 12, 2015
Messages
14,004
Location
West central Indiana
I've talked with multiple people on the phone. Seems like just a bug on their site confusing which model you selected.
Great, so they aren't lying, just incompetent and not able to fix the issue, its not a "bug", that is an issue with a computer program. Its that they uploaded the wrong material, plain and simple.
The website has pretty solid reviews from what I've seen.
You do know that its easy to fake reviews and many sites do.

Why do I need multiple zones for a single space? That's what I struggle with understanding.
Redundancy, if one breaks down your not SOL while your waiting on parts or on vacation and all your pipes break.

Much better circulation

Much higher efficiency. 15 seer for the unit you linked is terrible. Most mini splits are running around 20-23 seer. Plus during the shoulder seasons you can run just one at full or close to full load which helps efficiency even more. Multiple others have already pointed that out :headscrat
 

jskicet

Well-known member
Joined
Apr 26, 2020
Messages
216
Location
Western NC Mtns
Hey, I'm looking at a concealed duct mini split system (I can't seem to find a 60K BTU single zone system with low temperature handling with any other type of handler). Link to what I'm looking at below. Do I actually need to install duct work? Or could I just hang this inside the garage and go?

I have a small Gree Ducted unit in my upstairs loft/bedroom. Mine needed an inlet ductwork with filter attached. The duct work attaches to the rear of the unit. Some do have a filter near that inlet but it would be difficult to get to once installed. It works very. It runs on A/C year round being heat rises up to the loft master bedroom and gets very warm in the winter. I've never needed the heat. I didn't like the look of a wall mounted unit in the house. I'm pleased with it.
 