Chuckster in NJ
Well-known member
I have a friend of mine who has a stand alone garage with a dedicated single phase overhead service. The electrical contractor used 200 amp SEU Aluminum service cable (4/0) feeding a 200 amp main breaker. I believe this is a violation because you can only "de-rate" service conductors (83%) on a residential DWELLING as per the NEC……. NOT on a "stand alone garage" with a commercial electric rate.
I interpret that service feeder conductors to a "stand alone garage" shall be sized as per the main breaker rating and NOT de-rated like a residential dwelling…….. So I say given that the job is done in order to make it "code compliant" (least expensive way) he should change the existing 200 amp main breaker to a 175 amp main breaker.
The service was inspected and approved by the local inspector and my friend feels the electrical contractor "exceeded" minimum requirements set by the NEC.
What are your thoughts?
I interpret that service feeder conductors to a "stand alone garage" shall be sized as per the main breaker rating and NOT de-rated like a residential dwelling…….. So I say given that the job is done in order to make it "code compliant" (least expensive way) he should change the existing 200 amp main breaker to a 175 amp main breaker.
The service was inspected and approved by the local inspector and my friend feels the electrical contractor "exceeded" minimum requirements set by the NEC.
What are your thoughts?