I am trying to plan for the future on a conduit run from my main panel to a garage sub panel, so I want to put in a pull box or conduit body T:
- Run ~8' of 2" FMC to a 2" T conduit body under the house, main panel is recessed in wall so FMC will be behind stucco.
- One side of the T (the 90*) will reduce down to 1 1/2" rigid conduit and run all the way to the garage (parts will need to be buried)
- The other side (straight from the 2" FMC entrance) of the T will be capped off for now (possible run for an electrical car charger at the driveway (opposite side of property from garage)
-Will be running 4g wire from the panel to the garage
Reading how to do pull box calculations, I need 8 times the largest race way: 2" x 8 = 16" length. But a 2" T is only 10" long. Do I need to up size the T?
Also, when I do run 2 circuits, can they share the ground wire, and how would I connect them in the T? Three 4g wires is to big for a wire nut, can I use a 3 wire grounding bar? would there be enough room to fit the grounding bar?
- Run ~8' of 2" FMC to a 2" T conduit body under the house, main panel is recessed in wall so FMC will be behind stucco.
- One side of the T (the 90*) will reduce down to 1 1/2" rigid conduit and run all the way to the garage (parts will need to be buried)
- The other side (straight from the 2" FMC entrance) of the T will be capped off for now (possible run for an electrical car charger at the driveway (opposite side of property from garage)
-Will be running 4g wire from the panel to the garage
Reading how to do pull box calculations, I need 8 times the largest race way: 2" x 8 = 16" length. But a 2" T is only 10" long. Do I need to up size the T?
Also, when I do run 2 circuits, can they share the ground wire, and how would I connect them in the T? Three 4g wires is to big for a wire nut, can I use a 3 wire grounding bar? would there be enough room to fit the grounding bar?