Conduit body sizing and grounds

Paulski

Well-known member
Joined
Sep 29, 2017
Messages
119
I am trying to plan for the future on a conduit run from my main panel to a garage sub panel, so I want to put in a pull box or conduit body T:

- Run ~8' of 2" FMC to a 2" T conduit body under the house, main panel is recessed in wall so FMC will be behind stucco.
- One side of the T (the 90*) will reduce down to 1 1/2" rigid conduit and run all the way to the garage (parts will need to be buried)
- The other side (straight from the 2" FMC entrance) of the T will be capped off for now (possible run for an electrical car charger at the driveway (opposite side of property from garage)
-Will be running 4g wire from the panel to the garage

Reading how to do pull box calculations, I need 8 times the largest race way: 2" x 8 = 16" length. But a 2" T is only 10" long. Do I need to up size the T?

Also, when I do run 2 circuits, can they share the ground wire, and how would I connect them in the T? Three 4g wires is to big for a wire nut, can I use a 3 wire grounding bar? would there be enough room to fit the grounding bar?
 
To avoid these ads, REGISTER NOW!

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,612
Location
BC
I suggest not using a T. Do a dedicated run for each. Awkward/tight areas are worth pre-rdrilling, leaving space, and/or stubbing some conduit thru. I most often use outdoor-rated cable anyway.
 
OP
P

Paulski

Well-known member
Joined
Sep 29, 2017
Messages
119
I agree but unfortunately all the other knock outs are used up already.
 

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
Condulets don't follow the pull box rules, you just install the same size condulet as your conduit. If you need to share a ground wire, that becomes problematic in a condulet. Best solution would be change to a pullbox where you can install a ground bar, or many other options of terminal blocks, splices, etc., or run 2 ground wires into the condulet and not share.
 
OP
P

Paulski

Well-known member
Joined
Sep 29, 2017
Messages
119
Thanks, I think pulling 2 grounds when it comes time will be easier then. My city build code allows for 12 #4g's in a 2" conduit so I should be good
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
Ground bars are usually 6 AWG or smaller, lug kits are used to adapt them for larger conductors, but depending on the manufacturer two lug kits may be all that can be done, another way is use a 4-port Polaris connector & running a conductor from it to a lug bolted to the can to bond it, removing any paint under it.
 

ycgoat

Well-known member
Joined
Mar 28, 2020
Messages
971
Location
S.E. Va
I think pulling through a T will be difficult especially later on with cable already in it.
 
OP
P

Paulski

Well-known member
Joined
Sep 29, 2017
Messages
119
I am orientating the T so the later pull will be straight and not the turn to make it a little easier. It is also less than 10' away from the main panel, so I could just pull back the first set of wires, than pull all the wires together into the main panel.

If not a good idea, any suggestions on a pull box to use instead of the T?
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
I am orientating the T so the later pull will be straight and not the turn to make it a little easier. It is also less than 10' away from the main panel, so I could just pull back the first set of wires, than pull all the wires together into the main panel.

If not a good idea, any suggestions on a pull box to use instead of the T?
If your using flexible metal conduit, I would not use plastic, hell if you were nearby I would give you a used one that need to find a home for as need to clean up stuff, been collecting too much ****, came close to kicking the bucket a few months ago & amazing how being close to making a trip to the mortuary can change ones outlook, but still get winded super easy as lungs heal slowly.
 
To avoid these ads, REGISTER NOW!
OP
P

Paulski

Well-known member
Joined
Sep 29, 2017
Messages
119
If your using flexible metal conduit, I would not use plastic, hell if you were nearby I would give you a used one that need to find a home for as need to clean up stuff, been collecting too much ****, came close to kicking the bucket a few months ago & amazing how being close to making a trip to the mortuary can change ones outlook, but still get winded super easy as lungs heal slowly.
Sorry to hear about your close encounter with the mortuary Norcal, hope your lungs are getting better. I do plan to order a metal one from McMaster Carr, I can't find a 2" T locally and McMaster seems to have the best price, even with shipping
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,593
Location
Fullerton, CA
A tee is a real PITA when it comes to pulling wire on the hub perpendicular to the other 2.
There isn't enough room to feed the wires.
 
OP
P

Paulski

Well-known member
Joined
Sep 29, 2017
Messages
119
something like this? I would have to enlarge the knock outs to 2" and 1 1/2"
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,903
Location
Richmond, VA
something like this? I would have to enlarge the knock outs to 2" and 1 1/2"
Yes. It will have to be large, but I bet you won't regret having the space.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
I would not use a T. If they are straight through pulls, use a 12x12x4 or a 14x14x4 J-box. Get one with no knockouts so you can put your own in where needed. You will need a knockout set or a hole saw will work, but thet tend to make the hole to large at times. You will be much happier with a J-box. T's have their purpose, but this is not one of them.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,593
Location
Fullerton, CA
If they are straight through pulls, use a 12x12x4 or a 14x14x4 J-box.
Because it's a straight pull with 2"..... It needs to at least 16" long.

1) Straight Pulls. In straight pulls, the length of the box or
conduit body shall not be less than eight times the metric desig‐
nator (trade size) of the largest raceway.
It's the 90 degree portion if the "tee" that only needs to be 12"
 
Last edited:

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Because it's a straight pull with 2"..... It needs to at least 16" long.

1) Straight Pulls. In straight pulls, the length of the box or
conduit body shall not be less than eight times the metric desig‐
nator (trade size) of the largest raceway.
You are correct, I had it backwards
 