conduit size

Sp180

Member
Joined
Jul 29, 2013
Messages
15
Location
Nowthen, MN
If I am pulling 2, 2, 2, 4 Aluminum feeder, what size conduit do I need for 240 feet and one 90 degree turn?
 
To avoid these ads, REGISTER NOW!

kd3pc

Well-known member
Joined
Aug 10, 2013
Messages
3,630
Location
Northern Neck
local code and electric company may dictate diameter....

here in TN,per the local utility (sub TVA) an underground feeder has to be Schedule 80, buried 2.5 ft or deeper, or incased in concrete with 3' sweeps and 2.5" minimum diameter for 200 amp service. 400 amp has larger diameter, deeper burial and wider sweeps

YMMV
 
To avoid these ads, REGISTER NOW!

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
Local codes for state / city will apply. Where you at ??

Now would be good time to Update GJ Profile with City / State. That way you'll get the best advice.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
By NEC you'd be okay with 1-1/2 inch. But I highly suggest at least 2 inch. Also Sch40 PVC is okay below ground and Sch80 PVC for above ground where exposed that the conduit may be subject to damage. Also 18 inches of cover is required for buried. Do check with your local authority for any variation they may require.
 