Conduit sweeps with direct bury

HaiKarate

Well-known member
Joined
Oct 20, 2020
Messages
314
Location
Seattle
I am installing a long (close to 300') run of 4/0 MHF to my detached shop and am using 2.5" conduit at both ends where I come up out of the ground. I have some schedule 80 to go from the LB entering the house/\shop down into the ground, but I am unable to source a schedule 80 sweep anywhere around here.

Is a sweep required in this instance? If so I am probably just going to dig super deep by the house/shop and use a sch 40 sweep. If not can I just run out the bottom of the 'raw' PVC? Or do I need a bell end or some type of transition?

I'm not concerned about damage due to where the cable runs, (near an 'inside' corner on the outside of the house) but want to make sure I meet code and pass inspection with no issues.

HK
 
To avoid these ads, REGISTER NOW!
OP
H

HaiKarate

Well-known member
Joined
Oct 20, 2020
Messages
314
Location
Seattle
That is why I'm asking - I have no idea what the inspector might consider "subject to damage".

*I* know it isn't, but I want to make sure that any inspector that shows up will pass this thing.
 
OP
H

HaiKarate

Well-known member
Joined
Oct 20, 2020
Messages
314
Location
Seattle
I guess the bigger question I have is about the sweeps as I know I can get the sch80 18" down with the straight piece I have - is it kosher just to have a 'down pipe' without a sweep with the MHF?
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,777
Location
NW Iowa
I guess the bigger question I have is about the sweeps as I know I can get the sch80 18" down with the straight piece I have - is it kosher just to have a 'down pipe' without a sweep with the MHF?

It's normal. I've never seen anyone put a sweep on the bottom. No reason to.
 

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,299
Location
Illinois near St. Louis, Missouri
That is why I'm asking - I have no idea what the inspector might consider "subject to damage".

*I* know it isn't, but I want to make sure that any inspector that shows up will pass this thing.

Better ask the AHJ. I lived in one location that expected sch 80 for any outdoor conduit risers. I lived in the next county that didn't have any inspections but most of the suppliers were in the strict county so they tried to tell me it had to be sch 80.
 
To avoid these ads, REGISTER NOW!

jh87

Well-known member
Joined
Dec 24, 2011
Messages
155
Location
Indiana
When I built my house all the power company required for my underground service was a straight piece of 3” that ran 18” underground.
 

sky jumper

Well-known member
Joined
Mar 13, 2018
Messages
127
my AHJ requires RMC for the elbow/sweep and everything up through the metal LB. nothing in the code says this, but they require it. I had to cut out my PVC elbows and replace with Rigid.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,074
Location
Modesto, CA
my AHJ requires RMC for the elbow/sweep and everything up through the metal LB. nothing in the code says this, but they require it. I had to cut out my PVC elbows and replace with Rigid.

Do they have local WRITTEN amendments for these requirements? If not then they cant enforce them...
 
OP
H

HaiKarate

Well-known member
Joined
Oct 20, 2020
Messages
314
Location
Seattle
Thanks for all the input - I think I'll just go Sched 80 straight down 18"+ then.

The varied responses also show why I ask this question - enforcement/interpretation of this seems to be all over the place!

Also, the schedule 80 to 18" down section from the NEC is specifically called out in the inspection 'cheat sheet' they publish on items people often miss. That being said, I'm 95% sure the service entrance conduit going up to my meter is sched 40 (it's been painted over, but definitely doesn't seem as thick/stiff/strong as 80). Go Figure. I'm guessing it's due to age of the house (~40 years).

Hope to get this wrapped up over the weekend and call for inspection early next week.

Thanks,
HK
 