Connecting Subpanel Ground Bars Together?

Beemer

Well-known member
Joined
Jun 21, 2020
Messages
1,424
Location
Northeast
Are there guidelines on a wire (or wires) size to interconnect two ground bars in a subpanel?
I saw another older post and there were opinions both ways on whether or not it was required, but if it were done, any thoughts on wire size requirements?
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,903
Location
Richmond, VA
If you have multiple neutral bars, they do need to be connected, but should have been from the factory. Make sure your ground bars have no connection to the neutrals in a subpanel. No jumpers, no bonding screws, no grounds on the neutral bar and no neutrals on the ground bar
 
OP
B

Beemer

Well-known member
Joined
Jun 21, 2020
Messages
1,424
Location
Northeast
If you have multiple neutral bars, they do need to be connected, but should have been from the factory. Make sure your ground bars have no connection to the neutrals in a subpanel. No jumpers, no bonding screws, no grounds on the neutral bar and no neutrals on the ground bar
There were mounting holes in the can for the ground bars so they needed to be added.
I'll check for continuity of the neutral bars and the can to see if I am missing something. There were two short ones stacked connected with a bolt through them. I assume they used two because the number of wire places for each is much less than the number of breaker slots.
 
Last edited:
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,903
Location
Richmond, VA
There were mounting holes in the can for the ground bars so they needed to be added.
I'll check for continuity of the neutral bars and the can to see if I am missing something. There were two stacked and I assume they are both neutral bars because they are pretty short compared to the number of slots for breakers.
Make sure you only land one neutral per hole. Grounds can have more than one, but not neutrals
 
OP
B

Beemer

Well-known member
Joined
Jun 21, 2020
Messages
1,424
Location
Northeast
Make sure you only land one neutral per hole. Grounds can have more than one, but not neutrals
Mike, there are two stacked neutral bars connected together and the main feeder neutral connected to a lug between the two.
The ground wires are now on separate ground strips on the enclosure, but I get continuity between the ground bars and the neutral bars.
I don't see a jumper.
Is that normal?
It's a Square D QOC-20M panel.
If it's not correct to have continuity can you see anything in the photo indicating a bond?
 

Attachments

  • shed panel.jpg
    shed panel.jpg
    541.2 KB · Views: 31
Last edited:

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,009
Location
Central Iowa
Mike, there are two stacked neutral bars connected together and the main feeder neutral connected to a lug between the two.
The ground wires are now on separate ground strips on the enclosure, but I get continuity between the ground bars and the neutral bars.
I don't see a jumper.
Is that normal?
It's a Square D QOC-20M panel.
If it's not correct to have continuity can you see anything in the photo indicating a bond?
You will get continuity between the neutral and ground because they are tied together in the main panel. If it's a concern, disconnect the ground from the feeder then check for continuity. If I were to guess, I would think that the bonding screw went right through the open hole in the middle and since it's gone, you should be ok.
 
Last edited: