I'm going to set new 200 amp main breaker panel 80 Ft from meter base. I can use aluminum wire. I need help with size and type. It will also be 3 individual conductors. Thanks Wes.
The existing panel already has a main breaker is there any reason to use a breaker in the new box? The existing boxes connected to a meter now it will be disconnected and wired accordingly to function as a sub panel. Thanks for your replies. Wes
Noticed that in the panel picture, the TOP, RH breaker (15a) appears to have two wires landed under the screw. Double tapping breaker is a no-no.
CT
For 200a u will need 250Kcmil AL.
Where is the new box going? It will be the new main service panel? If so it will need a main breaker IF there will be more than 6 branch breaker handles.
I'm not able to find anywhere to buy, or even price 250Kcmil AL wire. Is there something I'm missing. I need a little more help. Still thanks guys.
RESI is rated at 80%, not 100% as Commercial/Industrial. 4/0 Al is what I see/use for RESI 200 amp service. Someone can chime in if I am wrong. I do not have my NEC book handy here. I have never ran 3/0 Cu or 250mcm Al for RESI. Only 2/0 Cu and 4/0 Al...
Someone please advise.
CT
This is what I found.
National Electric Code Tables 310.15 B6 and 310.16
States 2/0 Cu or 4/0 Al... 250mcm is excessive for this application.
CT
I found some 4/4/2 urd service entrance cable. Will that work?
I'm about 500ft from the boat ramp.
Thanks. Looks like that needs to be in conduit? Can it be direct burial?
What are u referring to?
the 250KCmil?
yes it needs to be in conduit.
no it cannot be direct buried.
I made a call to the poco this am. I was told to speak to Engineering. I had to leave a message. Hopefully they will call back. Thanks for everyone help. I will keep you folks informed. Wes
Why are u calling them?
Isnt all your work past the meter pan?
They only care about up to the meter pan.
I want to add new meter, wire, and panel. Then I will disconnect newly acquired park model from 50amp panel (dbl. 50 and single 20 amp breaker).
New panel will have more space.
If poco allows me to go from new panel to existing 125 amp panel I will configure 125amp panel so it will be a sub panel. I will hah poco pull that meter
I will then have 1 meter and 2 breaker panels.
If poco deems newly acquired park model to be 2nd residence they will not allow 1 meter. I hope that helps to clear things up a little bit.
I probably have a very unique situation, compared to what you guys are used to.

this is the breaker fort the newly acquired park model it will no longer be used when new panel is set up.
the meter on the right is attached to that breaker panel. It will be move to empty meter base in next picture
this is where I will set new meter( the one on the right belongs to the neighbors
this is where I will set new 200amp thru lug breaker panel
from where new panel will be is about 30ft to existing 125amp panel I will use thru lugs to attach new panel to this panel.
this is the meter for existing 125amp panel it will be removed also. That will leave me 1 meter for my property. 
Hi everyone just now getting back to my project.
Added a sub panel to my little cabin. I have a few questions.
I ran an 8/2 with ground from a 30amp breaker in the main panel to the sub panel in the cabin. I put the black wire on one hot lug w/ a jumper to the other hot lug. I put the white wire on the neutral lug. I put the bare ground wire on the ground lug. Please let me know if that is correct.
I still need to pound my ground rods. What is the correct way to connect the rods.![]()
So... I assume you are feeding with a 30 1 pole breaker.
The way you have wired the subpanel line terminals has created a 120v only subpanel... Was this your intent?
CT
#8 can be breakered at 40a.