Converting round ceiling box to outlet???

vertguy

Well-known member
Joined
Apr 6, 2010
Messages
1,260
Location
SE WI
Time to upgrade the garage lighting and trying to find the right way to convert the existing round boxes with single ceramic fixtures to an outlet. Since my garage is already finished, I would prefer to do something on the surface. I am planning to use plug-in 4ft LED fixtures and I want this done right.

Scanning the local box stores electrical (no surprise) along with some online searches have come up with no real option aside from swapping in a lamp assembly with a outlet. I am really hoping this is not my only option as it would result in still needing something in the empty socket.

What are my options??
 
To avoid these ads, REGISTER NOW!

Theruse

Well-known member
Joined
Aug 12, 2012
Messages
341
Location
Maryland
I wanted to do the same thing when I purchased my four LED lights from Costco. At first I bought a nice recessed outlet so the plugs would be recessed. That's when I learned a round box doesn't work with an outlet. I wound up reinstalling the ugly single socket ceramic light and then screwed in a plug adapter and then plugged in a right angle triple outlet. The two plugs now sit flush with the wall. Not ideal, but I like the flat plate shown in the earlier post. Couldn't find it at HD or Lowes and then began wondering if it really existed. I'll probably buy one but might cut it out a little bit to fit a decora outlet to give a more updated look.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
31,910
Location
Coronado, CA
The big box stores generally stock only the fastest moving items in any given product line.
It has been my experience that if I want something out of the ordinary I have to look for a specialty outlet.

What it seems to boil down to is that in any given product line, 20% of the line has 80% of the sales. Big box stores seem to stock 80% of that 20%. They make their money by quickly turning over their inventory.

I have seen round box covers with receptacles in them, but I can not recall where or when.
 
OP
V

vertguy

Well-known member
Joined
Apr 6, 2010
Messages
1,260
Location
SE WI
I actually saw those covers, but the outlet I tried in the ceiling box did not fit as it was physically too long and hit along the threaded area of the box. Maybe it is the outlet as I had some left over from when I finished the basement. I will check a few combinations on my next trip to Menards.
 

rsanter

Well-known member
Joined
Dec 22, 2007
Messages
18,492
Location
visalia ca
OP
V

vertguy

Well-known member
Joined
Apr 6, 2010
Messages
1,260
Location
SE WI
you have to cut the tabs off the outlet

That is not the issue... the body of the outlet hits the indented area in the box where the screw threads are molded in. I will snap a couple pictures, but assume it is design of this specific outlet. Time to test fit a few combinations at the store with a metal plate. Worse case, I can always just go with the bulb socket that has the 3-prong outlet... but at $8 each, hoping to find a more cost effective solution.

Thanks for all the feedback!!
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
Starting with the 1999 NEC, receptacles are no longer allowed to be fastened with a single attachment screw.

The 4-O covers shown above are technically prohibited.
 

thewatusi

Well-known member
Joined
Dec 27, 2013
Messages
1,256
Location
Philly Burbs
Remove the round box and install a two-gang old work square box in its place.

If you're careful (particularly with the removal of the old box) jumbo outlet cover should hide any drywall irregularities.
 

gungatim

Well-known member
Joined
Jan 8, 2013
Messages
8,101
Location
west mich
don't they still sell the outlets that screw into a lightbulb socket? i've got a box of those sitting around collecting dust. some are just a single outlet, others have dual outlets with an extended lamp socket and pull string...brown plastic...anyone remember those? any way, that's what I used until I put in new switched plug outlets in my woodshop...
 

Oggy

Well-known member
Joined
Jan 2, 2011
Messages
1,295
Location
Central New York
Code aside, (I know very little about code, just going off previous post) you could try an outlet box extension, and then the cover.

just an example, there's other out there.
 

dw1

Well-known member
Joined
Jan 26, 2015
Messages
1,335
Location
Ky
Starting with the 1999 NEC, receptacles are no longer allowed to be fastened with a single attachment screw.

The 4-O covers shown above are technically prohibited.

Oops, brian lapse on my part!!
Thanks for the clarification
But you are correct.
 
OP
V

vertguy

Well-known member
Joined
Apr 6, 2010
Messages
1,260
Location
SE WI
So something like this is not compliant with current electrical codes? Leviton 1288

417MWJVW7PL.gif
 
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
(C) Receptacles Mounted on Covers. Receptacles mounted
to and supported by a cover shall be held rigidly against the
cover by more than one screw or shall be a device assembly or
box cover listed and identified for securing by a single screw
.

The Leviton 1228 probably qualifies because it is an ASSEMBLY and is covered under the last sentence of the paragraph given above. As you can see HERE it is UL listed.

the OP's problem is that there are both 3½ and 4 inch octogon boxes. The cover for a 4 inch Oct box can easily accommodate the end screw of a receptacle if you wanted to drill it for them. The 3½ inch box cover will certainly need to be bought as an assembly, as the receptacles used in them are quite small on the back side, in comparison to most receptacles.

Charles
 
Last edited:

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
The Leviton 1228 probably qualifies because it is an ASSEMBLY and is covered under the last sentence of the paragraph given above. As you can see HERE it is UL listed.
Charles


That particular one qualifies because it has a manufacturer installed receptacle in it :thumbup:

But the covers alone with field mounted receptacles don't.
 

Syberia

Well-known member
Joined
Jan 13, 2014
Messages
1,451
Location
Perris, CA
That particular one qualifies because someone ponied up the $$$ for it to qualify. The only difference between a company putting it together and the OP putting it together himself (provided he finds an outlet that fits) is who paid more.

Just speaking in practical terms here.
 

smedly

Well-known member
Joined
Jan 11, 2009
Messages
403
Location
Savage, Mn
Funny, I just ran into this exact problem and then came inside and googled "convert around ceiling box to outlet" and here I am. When I was at Home Depot and pick up Somehing like this.

http://www.menards.com/main/electri...1-gang-ent-box-extender/p-1420176-c-6427.html

So the adapter is held in place by the screws that are holding the outlet in the ceiling box.

It worked out fine I'm not sure if it's up to code though, can anyone Chime in?
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
When receptacles are installed in a garage ceiling, GFCI protection is required. See 210.8(A)(2), no exceptions for lighting.
 

landyacht

Well-known member
Joined
Mar 26, 2011
Messages
71
Location
Langley BC
You could still put the round covers in and say you did it before the code changed. Code isn't retroactive. And the intention of the code was to require both screws on an outlet are used in normal application. It's not like those plates were safe a year ago, but are unsafe this year because of a code rule change.
 

smedly

Well-known member
Joined
Jan 11, 2009
Messages
403
Location
Savage, Mn
I imagine I'm good with the GFI since the lights and opener outlets in the ceiling are on the same circuit. The adaptor plate and cover just look a bit jank.

and I'm a bit disappointed in the Costco led lights, bright for sure, but a but harsh.
 

Badger05

Well-known member
Joined
Jan 11, 2013
Messages
66
Location
WI
I imagine I'm good with the GFI since the lights and opener outlets in the ceiling are on the same circuit. The adaptor plate and cover just look a bit jank.

and I'm a bit disappointed in the Costco led lights, bright for sure, but a but harsh.

BUMP.

Just running into this same issue myself. I want to convert from a single incandescent light fixture in my garage ceiling to some led shop lights that need a receptacle.

Several options were discussed in this thread but it doesn't seem like anyone came to a solid resolution. I agree the octagon cover plate over a round ceiling box looks a bit "off" but I don't see any better options...don't really want to tear out the round work box and install an "old work" outlet box.
 

Jazz1

Well-known member
Joined
Jan 3, 2016
Messages
4,184
Location
Thunder Bay On.

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
As for the 1 screw 2 screw issue,,,,,,,,,,, I understand why and drill holes for them if needed especially at ground level where they are being used like they do. It is a grounded outlet, this doesn't concern me so much when all this is fixed in place with no one yanking on it all.
There is probably good reason for the ceiling gfci too, you can find all kinds of **** plugged in to these if you give someone an opportunity. I don't use it on lights so far in my shop and storage which are recept and cord but its all 20 ft in the air. I even have some non gfci in some spots but there is gfci available. I found the other day I might change out or could simply remove.
 

Gerald O

Well-known member
Joined
Mar 5, 2013
Messages
1,884
Location
NC
Personally I wouldn't use plug-in light fixtures unless you already have them.
Get hard-wired fixtures and run EMT or FMC to the box.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,581
Location
Long Island
That particular one qualifies because someone ponied up the $$$ for it to qualify. The only difference between a company putting it together and the OP putting it together himself (provided he finds an outlet that fits) is who paid more.

Just speaking in practical terms here.

Not necessarily. I've seen several ways that companies may thread the center hole of their receptacles.

On really cheap outlets, I've seen a threaded insert pressed into the plastic. I can only suppose it has an internal conductivity path to the ground (I can't say I've tested it) to ground a metal plate via the screw, but it probably isn't all that strong.

On decent outlets, the central hole is a threaded tube either riveted or welded to the back strap that passes through the whole outlet assembly. A screw through that will hold things together just fine.
 

exmaxima1

Well-known member
Joined
Jun 25, 2011
Messages
6,339
Location
Midwest
Personally I wouldn't use plug-in light fixtures unless you already have them.
Get hard-wired fixtures and run EMT or FMC to the box.

+1
I installed new led fixtures in my garage a few weeks ago, and bought the kind that daisy chain end-to-end. Though they came with cords, it was simple to punch a hole in the back of one (for wires) and a couple of small holes to mate up to the overhead light fixture box. Nice clean install.
 