Good day folks,
Had two questions:

1) need to run wiring from the panel to the sump pump in the crawlspace. The wire has to run perpendicular to the floor joists. I don’t want to drill holes in every single joist. Is there another code approved option to run it? Perhaps a conduit or metal casing wire or a busway with furring strips?

2) Crawlspace has about 3’-4’ headroom (it varies). Want to install lightening. Would you recommend low voltage led lightening all around or couple of high output led bulbs screwed into ceiling mounted outlets? Crawlspace is not used for any storage, so, not accessed frequently but would be nice to have some good lighting.

the run between panel and sump is about 50’.

No water in the crawlspace. The sump pump runs may be in Jan/Feb when water table rises from long rainy days.

Thank you!
 
Last edited:
To avoid these ads, REGISTER NOW!

acer66

Well-known member
Joined
Dec 4, 2010
Messages
4,418
Location
Western North Carolina
1)Busway and emt would be code compliant in the US.
2) I would use 4‘ led fixtures that can be daisy chained close to the foundation, girders etc so they are out of the way.
 

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,554
Location
East Bay SFO
Here’s what I did.
I used EMT and these gasketted fixtures. Light is emitted to all sides as well as straight down over my sump.

.
2A772882-B978-400B-A593-46A571EFA772.jpegI used EMT and these gasketted fixtures. Light is emitted to all sides as well as straight down over my sump.
 
OP
M

Mike1903

Well-known member
Joined
Jan 16, 2021
Messages
139
Location
Suburbs
If not running through bored holes you can use running boards to affix the cable to.
You mean running furring strips (say 1x3) perpendicular to the joist and then attaching the wire with staples to the strips?
 
OP
M

Mike1903

Well-known member
Joined
Jan 16, 2021
Messages
139
Location
Suburbs
Here’s what I did.
I used EMT and these gasketted fixtures. Light is emitted to all sides as well as straight down over my sump.

.
2A772882-B978-400B-A593-46A571EFA772.jpegI used EMT and these gasketted fixtures. Light is emitted to all sides as well as straight down over my sump.
Looks good. What kind of wire did you run in that EMT?
 
OP
M

Mike1903

Well-known member
Joined
Jan 16, 2021
Messages
139
Location
Suburbs
Thanks
Southwire THHN 14ga.
Three individual solid wires, black white and green. Run in half inch EMT. I have a bender and taught myself how to use it by watching YouTube videos.
Did you choose EMT instead of pvc so that you can make custom bends?
 
OP
M

Mike1903

Well-known member
Joined
Jan 16, 2021
Messages
139
Location
Suburbs
I wonder if I can glue furring strips to the foundation with construction adhesive just below the joists and then staple the wiring? Besides the concern of adhesive failing over concern, any concerns with this approach?
 
To avoid these ads, REGISTER NOW!

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,459
Location
Northern Virginia
Good info! My kitchen extension has a crawl space that will need to be wired, lit, and power for a sump pump so I am following along.

My access to the crawl space is a former basement window. I plan to put the light switch at the new (former window) entrance. Also, if the inspector requires me to wire the sump outlet with GFI protection, I plan to use a GFCI dead front mounted at the entrance so it can be easily inspected for power and reset without crawling in there.

 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
You may also attach a MC cable to the underside of the joists as long as it is supported at every joist and not subject to physical damage. NEC 330.15
 

SlappyWhite

Well-known member
Joined
Oct 3, 2012
Messages
1,819
Location
Upper Canada
Any reason not to drill? No right -angle drill or just the effort?

If it is effort, once you are in there I bet it turns out to be less work than most other methods. If you take the time to align the holes that cable pulls fairly easily.
 

65ranchero

Well-known member
Joined
Dec 16, 2020
Messages
5,087
Location
Danville, VT left NJ forever
I wonder if I can glue furring strips to the foundation with construction adhesive just below the joists and then staple the wiring? Besides the concern of adhesive failing over concern, any concerns with this approach?
If your going to do that what about using Tapcons or similar to hold wood to the foundation
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
I see it run along the bottom all the time -- ideally along a wall or if there are central beams keeps it out of the way. Crawl is not an active space ..... even in basements it's common. My nephew just had to add strips (metal in his case) to get under all the wires and pipes in his newly built house
 

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
FYI the receptacles need GFCI protection (210.8 (A)(4)), and the lighting, including hardwired lighting, also needs GFCI protection (210.8 (C)).
 
OP
M

Mike1903

Well-known member
Joined
Jan 16, 2021
Messages
139
Location
Suburbs
ZB
Any reason not to drill? No right -angle drill or just the effort?

If it is effort, once you are in there I bet it turns out to be less work than most other methods. If you take the time to align the holes that cable pulls fairly easily.
it is both. Plus the underside has insulation supposed with strings… so, need to mess around with it as well.
Great info in this thread… thx!
 
OP
M

Mike1903

Well-known member
Joined
Jan 16, 2021
Messages
139
Location
Suburbs

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,905
Good info! My kitchen extension has a crawl space that will need to be wired, lit, and power for a sump pump so I am following along.

My access to the crawl space is a former basement window. I plan to put the light switch at the new (former window) entrance. Also, if the inspector requires me to wire the sump outlet with GFI protection, I plan to use a GFCI dead front mounted at the entrance so it can be easily inspected for power and reset without crawling in there.


Use a GFCI breaker, and you won't have to go outside to check.
 

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
Gray PVC is cheap and easy. I'd use that with THWN Stranded wire. Later on if you want to add more wire....just pull them.

I always leave a pull string in my conduit just in case
 