Critique my PEX Layout
Just put down the Pex runs in my addition and need some confirmation.
It is a 30x38 with a hallway and living area in the back. The rest is garage. I am running 3 loops of Pex in the garage area. They are on 8" centers and loops are ~270' each. With the last loop running under the stairs and a closet in the living space.
There are 2 loops in the living area both 260' and on 10" centers. My Heat calc that I had done by FW Webb called for 3 225's in the garage and 2 longer circuits in the living area all on 12" spacing. I closed up the spacing because I had the extra tube anyway and thought it would be a more even heat.
Will it be ok to leave this setup this way with different spacing in the separate zones? I didn't really think about it before I put it in. The plumber I am working with isn't all that knowledgeable with radiant so I just wanted to get a second opinion that laying my PEX this way won't cause any issues except maybe the need for a little more pump to get through the longer runs in the garage?
Just put down the Pex runs in my addition and need some confirmation.
It is a 30x38 with a hallway and living area in the back. The rest is garage. I am running 3 loops of Pex in the garage area. They are on 8" centers and loops are ~270' each. With the last loop running under the stairs and a closet in the living space.
There are 2 loops in the living area both 260' and on 10" centers. My Heat calc that I had done by FW Webb called for 3 225's in the garage and 2 longer circuits in the living area all on 12" spacing. I closed up the spacing because I had the extra tube anyway and thought it would be a more even heat.
Will it be ok to leave this setup this way with different spacing in the separate zones? I didn't really think about it before I put it in. The plumber I am working with isn't all that knowledgeable with radiant so I just wanted to get a second opinion that laying my PEX this way won't cause any issues except maybe the need for a little more pump to get through the longer runs in the garage?