CSST in a wall?

To avoid these ads, REGISTER NOW!

Rockhead261

Well-known member
Joined
Aug 28, 2013
Messages
1,911
Location
10509
For safety purposes? Yes. Per code? Check with your local Big Brother.

Make sure you ground CSST whenever you use it.
 
To avoid these ads, REGISTER NOW!

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,411
Location
N CA
Ground the first fitting. Use all of the appropriate nail plates etc. they also have a termination piece for exiting the wall.
 

Rockhead261

Well-known member
Joined
Aug 28, 2013
Messages
1,911
Location
10509
Ground the first fitting.

Actually, you need to jumper across the pipe itself to the first fitting on the rigid pipe. CSST fitting are/can be dielectric. In other words, the CSST is isolated from the piping and creates a gap in electrolysis. You need a clamp on the CSST fitting to a clamp on the rigid pipe in order to maintain ground continuity.

CSSTGround.jpg
 

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
That's an interesting diagram IMO.

Usually, that final connection between black pipe is a CSST appliance connector. At least here, bonding is not required nor suggested for an appliance connector.

I have all copper LP line, except a new CSST that goes up to the attic for a new furnace. I wonder if it should have a jumper around it according to code?
 