I want to put a big ladder to my attic, which uses 24" on center prefab trusses.

I thought you could cut the bottom chord of a truss, as long as you frame it properly. I expected the truss company to tell me how to do this. They must deal with this all the time, right?

Instead, they said it's impossible to cut the bottom chord and wouldn't help me with the engineering. Yet, I see that I can buy 25" and 30" wide ladders all day long.

I'm thinking about buying a 25" ladder and just shifting a truss over a couple inches, but nobody will tell me this is OK either.
 
To avoid these ads, REGISTER NOW!

ptt49er

Well-known member
Joined
Jun 28, 2018
Messages
305
Location
Rock Hill, SC
The PO cut the trusses to install the attic ladder in our house.

I spoke with a structural engineer and there are ways to frame a diaphragm of plywood around the penetration.

I haven't gotten a stamped plan from him but have installed ply around the opening.

Find a local residential structural PE, they'll likely be able to help.
 

Uncle murph

Well-known member
Joined
Jan 28, 2021
Messages
1,461
Location
Harford county
This is a joke, right?
I want to put a big ladder to my attic, which uses 24" on center prefab trusses.

I thought you could cut the bottom chord of a truss, as long as you frame it properly. I expected the truss company to tell me how to do this. They must deal with this all the time, right?

Instead, they said it's impossible to cut the bottom chord and wouldn't help me with the engineering. Yet, I see that I can buy 25" and 30" wide ladders all day long.

I'm thinking about buying a 25" ladder and just shifting a truss over a couple inches, but nobody will tell me this is OK either.
You’ve got 22.5” between your trusses,buy a ladder that fits.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,402
Location
VT
The PO cut the trusses to install the attic ladder in our house.

One of mine is cut, thankfully in a low load spot (cantilever, cut spot is past the support). The ceiling was sagging over an inch until I re-framed it.
 

BurtEggley

Well-known member
Joined
Oct 8, 2024
Messages
861
I had to cut a truss to put in a whole house fan. Needed an engineering drawing with a stamp to get it approved, and when the city came out to inspect it, they even verified the nail size, type and placement on that part of the drawing. The engineer wanted a lot more than just the plywood sistering I was suggesting.

As suggested, I'd look for a ladder that fits.
 

tarmy

Well-known member
Joined
May 28, 2014
Messages
4,662
Location
Nor Cal
Cut and trusses are not two words that should be used in the same question😎

As noted, get or build something that fits in between them.
 

TRWham

Well-known member
Joined
Aug 11, 2017
Messages
1,958
Location
East Cobb County, Georgia
We have modified or repaired trusses per engineer instruction, but not very often. You would need some path to carry that tension without just transferring it to the adjacent trusses, and the connections would be critical.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,420
Location
Richmond, VA
Is this building done? If so, how are you planning to move a truss over?

If not, get the trusses designed for this need, or just buy a ladder that fits
 

LopezBart

Well-known member
Joined
Oct 13, 2023
Messages
2,526
Location
Lopez Island, WA
Some quick estimate numbers to show why this is not simple: each 16p common nail is good for ~130 lbs in single shear; douglas fir is rated for ~300 psi in tension. Sistering in a 2x4 bottom member would then take 12 16p nails at each end, a 2x6 obviously more. Plywood, unless glued as well as nailed, would fail in bearing unless many many nails are used.

Getting 1.5" inches more width is pretty doable, but you need an engineered solution. More gets harder quickly.
 

wssix99

Well-known member
Joined
Mar 2, 2011
Messages
5,156
Location
Chicago, IL
Instead, they said it's impossible to cut the bottom chord and wouldn't help me with the engineering.

Here is the translation of this statement from your truss company to English:
"We are sorry but our engineering services and help come free of charge with new truss purchases.

If you desire additional support and assistance beyond warranty repairs, you will need to pound sand and go hire your own engineer.

I want to hang up on you now so I can go fishing."
 
OP
J

JackOfDiamonds

Well-known member
Joined
Jul 31, 2020
Messages
706
Location
Idaho (USA)
Here is the translation of this statement from your truss company to English:
"We are sorry but our engineering services and help come free of charge with new truss purchases.

If you desire additional support and assistance beyond warranty repairs, you will need to pound sand and go hire your own engineer.

I want to hang up on you now so I can go fishing."
Well I was asking for the $3000 worth of trusses I have on order with them.

This must be a regional thing. I swear back east all you had to do was ask and the truss companies would give you a pre-engineered framing plan for an attic staircase. But things generally get more lawyerfied over time so maybe that's a bygone era.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,420
Location
Richmond, VA
Well I was asking for the $3000 worth of trusses I have on order with them.

This must be a regional thing. I swear back east all you had to do was ask and the truss companies would give you a pre-engineered framing plan for an attic staircase. But things generally get more lawyerfied over time so maybe that's a bygone era.
Do they already have them in production? If not, they **** for not working with you on a solution
 

wssix99

Well-known member
Joined
Mar 2, 2011
Messages
5,156
Location
Chicago, IL
Do they already have them in production? If not, they **** for not working with you on a solution
+1 If not in production, I would talk to your salesman.

I would expect that if you want wider spacing, they would NOT give you a repair solution for new trusses. (They would only want to engineer intact trusses for your installation from a liability perspective.) That being said, they should be able to re-design your trusses for wider spacing, but that will likely cost you more money (for hefty trusses) and could change the shape of your roof to make the options economical.
 

TurnipTruck

Well-known member
Joined
Aug 28, 2005
Messages
1,552
Location
Southcentral Alaska
I seriously doubt that truss loading doesn’t have at least a small safety margin such that you couldn’t scoot one truss over 2 or 3 inches to make room for your stairway. Blocking and sheathing will have to accommodate the odd spacing, of course. **** it’s OK****

I would FAR prefer to scoot rather than cut or modify a stressed truss member.
IMG_7591.jpeg
I asked my truss designer friend to design a four foot gap in my 40’ trusses for a spiral staircase; the attic truss (LEFT) merely required the nail plates to be upsized ($8) while the other side he just doubled the standard truss.
 
Last edited:

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,038
Location
Minneapolis
It's not worth the truss company's time to do the engineering for one homeowner to modify one truss, plus there's the potential liability if the modified truss fails. That's why they said no. You may be able to find a structural engineer who's willing to do an initial inspection, then do the calculations and make drawings, then do a final inspection, but most will either decline the work or charge you more than you think it's worth. I was a consulting engineer for many years, unfortunately that's how it works for small jobs like this.
 
To avoid these ads, REGISTER NOW!

finn

Well-known member
Joined
Mar 27, 2005
Messages
16,203
Location
The UP, God's country
I have a narrow pull down ladder similar to that to get to my attic storage. In a word, it *****.

The narrow opening is too restrictive to get anything with any bulk through the opening, the stairs are too steep to safely navigate while carrying anything, and the stairs depth is too short to comfortably fit your feet where the plywood closure sheet closes in the raised stairs.

I’ve said it before, but the money I spent for the storage trusses and aluminum stairs is largely wasted in my opinion.

You’d be better off adding a foot or two to the footprint with that money and put up metal shelving on your concrete floor.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,420
Location
Richmond, VA
It's not worth the truss company's time to do the engineering for one homeowner to modify one truss
It's not a modification, it would be a new truss and it's their job.

Not all truss companies want to only deal with big jobs. I got trusses for a 16x16 shed and two local companies were happy to quote exactly the details I wanted, without trying to get me to go to anything "standard"

This company would lose my business over that response
 

Skooterj

Well-known member
Joined
Mar 11, 2021
Messages
749
Location
Indiana
If the building hasn't been built yet, and you are just getting the trusses ordered, changing the spacing between just 2 of the trusses should be a non issue. If your truss company won't do that simple engineering, find another truss company. If the building has already been built, or the trusses already been manufactured, you are going to need to hire your own structural engineer to modify your existing trusses.
 

CraigStu

Well-known member
Joined
May 22, 2014
Messages
4,014
Location
Blacksburg, Va
I framed a hole between 2 trusses 4ft long. Then I put a hinged cover over it on the top of trusses w/ a rope going through pulleys up to the roof area and over one to a hanging weight. Got the weight so I could push the lid up w/ my little finger or my head. Then I bought a 10ft step ladder. I hung the top of the ladder from 2 eyebolts. I ran a rope from the bottom of the ladder to a pulley in the ceiling to another pulley at the wall and down to a cleat on the wall. I would undo the rope at the cleat, drop the ladder, open the ladder so it sit on it's normal 4 feet so no stress on the eyebolts while I was climbing. both the rope from eyebolt to eyebolt and the rope to the bottom of the ladder attached w/ dog leash hooks. So I could undo the ladder and carry it anywhere else I needed it. Storing it against the ceiling kept it out of the way. The step ladder was WAY better than a pull down ladder in the previous house.
 

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,283
Location
Illinois near St. Louis, Missouri
Well I was asking for the $3000 worth of trusses I have on order with them.

This must be a regional thing. I swear back east all you had to do was ask and the truss companies would give you a pre-engineered framing plan for an attic staircase. But things generally get more lawyerfied over time so maybe that's a bygone era.
Have you committed to getting them? They may have already started on making them. This is something that should have been discussed up front and not tacked on after you ordered them. Guessing a bit on exactly what "have on order" means...

If discussed early I don't see why they shouldn't be able to design trusses for whatever spacing you want. Truss companies around here seem to be pretty willing to do such things although mine were pretty standard and they may want more money for engineering for complex cases. They could even do 2 heavier trusses for a bigger spacing (double normal spacing for example) and the framing between them for a bigger ceiling opening and support for roof framing between. Then again, maybe your truss company only does fairly standard truss designs - you can order standard trusses from some lumber companies and even Menards here in the midwest but you don't get any extra engineering from Menards. Might need to go to a different truss supplier.

You can't just cut the lower member of the truss. It has serious tension stress. And as others have noted bracing to other trusses isn't enough unless they are designed for the extra load and the bracing is done properly.
 

firebirdparts

Well-known member
Joined
Jun 8, 2016
Messages
10,586
Location
Kingsport, TN
You cannot cut the bottom chord of a truss, ever (that would be insane), but if all you want is 24" on center, then obviously that's not very difficult. I mean it's not difficult for a wooden structure to hold up 25" of roof. I daresay they would happily give you a framing plan that involved uncut trusses. I could be wrong.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,703
Location
NW Iowa
Pretty common to laminate a couple trusses on either side of a large opening. Then you just frame in support for your roof sheathing
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,073
Location
Northern Virginia
OP states 24" O/C trusses in the opening thread. Wants a presumed folding ladder.

As many have said, there are many premade folding ladders that slip right in the 22.5" net spacing which results from 24" OC trusses. Standard off the shelf product.

Seems like a trolling thread...
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,420
Location
Richmond, VA
To be fair, 22" attic ladders make it really hard to move stuff. If I was starting from scratch, I'd also be looking at something at least 30"
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,073
Location
Northern Virginia
To be fair, 22" attic ladders make it really hard to move stuff. If I was starting from scratch, I'd also be looking at something at least 30"
It was also asked if the trusses were ordered such that they could accommodate storage and I don't recall an answer ever posted.

Asking to modify non-storage rated trusses for a wider stair opening to then add storage to, I can see why a truss vendor would not want to advise.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,872
Location
NJ
It was also asked if the trusses were ordered such that they could accommodate storage and I don't recall an answer ever posted.

Asking to modify non-storage rated trusses for a wider stair opening to then add storage to, I can see why a truss vendor would not want to advise.
I hope the truss mfr was given floor loading as part of the design input.......otherwise, I bet they were only planning on holding up sheetrock with the bottom chord.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,872
Location
NJ
Yeah but op says he's thinking of buying a 25" ladder. Easier to use than 22.5 but a long ways from 30
Still doable @ 22.5" RO, IF the trusses can support storage. Storage capability is the bigger red flag for me.
1773439156075.png
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,872
Location
NJ
It was also asked if the trusses were ordered such that they could accommodate storage and I don't recall an answer ever posted.

Asking to modify non-storage rated trusses for a wider stair opening to then add storage to, I can see why a truss vendor would not want to advise.
That's when 16" or 19.2"OC could come into play aside from each truss being upgraded.
 

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,283
Location
Illinois near St. Louis, Missouri
Storage loading has been brought up and that's typically what happens with easy access like a folding stair. I put cross pieces just above the insulation in my shop attached to the center 2 diagonals and then put some sheeting on for a walkway and easy access to things like wiring. It's not easy enough to get there that storage isn't practical. St. Louis county has a rule that if the bottom cord isn't rated slightly more than minimum (I forget what the needed loading is) they require you to attach framing around the upper side of the opening to make openings small enough that storage (and a person getting in to do anything) is nearly impossible and a warning sign about no storage allowed. I was planning to build there so asked the truss company to add that so I could have reasonable access. Turns out the trusses already met that so they just had to add a note to the drawings. I didn't end up moving there but built the shop where I currently live with those trusses even though the requirements here were minimal.

I didn't see where the OP ever clarified if the trusses were already ordered and committed to.
 