Are there a lot of unit that are not pre-charged? I have this assumption that all of them are.
Would there be an issue if use the whole length of the refrigerant copper line and just wind up and leave it ouside what I don't need extended? It shouldn't need an adjustment in freon I suppose since it is what's supplied.
Yes, You can do that, or bleed some out. Might want to consult a HVAC guy for that. They pre-charge these things by weight. I’m not sure how you would measure the amount you are bleeding out.
AC pro's are adamant about a proper vacuum of the lines, pressure testing with nitrogen to dry them out, and vac to 500microns. I still don't get what a micron gauge does, but that's what the use.
And you need power, so either diy wiring or hire an electrician.
I was thinking the same thing. My instuctions stated if there was a leak after operating the unit, the entire system would have to be purged and refilled to the specific weight. In my opinion, the charged lines are more of a sales pitch. I can’t imagine an install not having to cut the lines to the proper length, or coil up. Your either going to have too much, or too little! Lol It sounds like you are a pro. I am fortunate to have an HVAC tech in my neighborhood. I trimmed the lines, single flared the ends and torqued to spec. My neighbor pressurized the lines, then pulled a vacuum. Do you have a ballpark what someone would charge for that service? Seems like a better option than just coiling them up and possibly kinking a line.
Curious, but will this pump do the job as well?
https://www.harborfreight.com/25-cfm-vacuum-pump-98076.html
I put a Mr Cool DIY unit in the in law suite above my shop. Attic trusses with 2 6' wide dormers both front and rear so around 600 sq ft. Seems to be working fine for me. I called 3 local companies for bids, 2 didn't even respond and the 3rd wanted $9k. I asked why so high since the I could get a kit for less than $2k and his response was "we use a better unit, a Mitsubishi". When I told him I could get the Mitsubishi for less than $3k and I knew it was much less than a full day job to install it he did some mumbling and hung up on me. The "industry" is really protective of their turf and I'll remember that, especially since I had to spend 4 hours helping their technician troubleshoot a failed valve in our less than a year old furnace.
Specs on that pump says it will vacuum down to 75 microns? The specs on my unit said to vacuum to 500 microns. I’m not up to par on the whole micron thing. I used to work on cars for a living. Back in the day, we would vacuum an a/c system down to 29 inches of mercury. This would ensure there was no moisture in the lines. Water vaporizes under vacuum. We always looked for 29. Not really sure why. Lol I’m assuming that would be enough vacuum at any ambient temp. to vaporize the moisture.
29inhg means absolutely nothing. You were doing it wrong.
Since when do we trust HF claimed numbers?
You only need to go under 500 microns, saw some youtube with "chinese" pump have quite a bit of problem getting down there, getting too hot, need to change oil, etc, I think he had to triple evac it to get there, but he did.
Educate me. Are microns and inhg not the same thing? I assumed microns were just a more accurate measurement.29inhg means absolutely nothing. You were doing it wrong.
In a vague sense, yes. Inches of vacuum are a measurement of negative pressure relative to ambient atmospheric pressure--a higher number is a stronger vacuum. On a "standard" day at sea level, a perfect vacuum would be 29.92". Microns are a measurement of absolute pressure (so 0 microns would be a perfect vacuum), and are still measured on the mercury scale. One micron is 0.001 mm--or put differently, 1000 microns = 1 mm. Since this usage measures absolute pressure, a smaller number is a stronger vacuum.Are microns and inhg not the same thing?
In a vague sense, yes. Inches of vacuum are a measurement of negative pressure relative to ambient atmospheric pressure--a higher number is a stronger vacuum. On a "standard" day at sea level, a perfect vacuum would be 29.92". Microns are a measurement of absolute pressure (so 0 microns would be a perfect vacuum), and are still measured on the mercury scale. One micron is 0.001 mm--or put differently, 1000 microns = 1 mm. Since this usage measures absolute pressure, a smaller number is a stronger vacuum.
On that standard day at sea level, 29" of vacuum would equate to 0.92" absolute pressure, or 23.368 mm, or 23,368 microns. To be equivalent to 500 microns, you'd need to read 29.90" of vacuum.
Standard atmospheric pressure at sea level is 29.92", so 30" of vacuum would be impossible under those conditions--and in any event, your dial vacuum gauge doesn't have anywhere near the resolution needed to do this properly. Could you get away with it? Probably. But it isn't the right way to do it.Would you say that pulling a continuous vacuuum at 30” would be sufficient enough to evacuate the lines then?
Standard atmospheric pressure at sea level is 29.92", so 30" of vacuum would be impossible under those conditions--and in any event, your dial vacuum gauge doesn't have anywhere near the resolution needed to do this properly. Could you get away with it? Probably. But it isn't the right way to do it.
In a vague sense, yes. Inches of vacuum are a measurement of negative pressure relative to ambient atmospheric pressure--a higher number is a stronger vacuum. On a "standard" day at sea level, a perfect vacuum would be 29.92". Microns are a measurement of absolute pressure (so 0 microns would be a perfect vacuum), and are still measured on the mercury scale. One micron is 0.001 mm--or put differently, 1000 microns = 1 mm. Since this usage measures absolute pressure, a smaller number is a stronger vacuum.
On that standard day at sea level, 29" of vacuum would equate to 0.92" absolute pressure, or 23.368 mm, or 23,368 microns. To be equivalent to 500 microns, you'd need to read 29.90" of vacuum.
If it does what its specs say it will do, it should work.
Some of the more obscure brands coming into the states...
AUX
Mirage
Midea
Soleus
Pioneer
Blueridge
Gree - not so obscure, but a huge manufacturer that rebrands, like for Lennox, Carrier
One can find really inexpensive product online, ebay and through direct distributors and importers. It's prudent to actually talk to them to vet them, if you intend to buy and expect any kind of support or warranty coverage. Some are simply call centers shipping cartons out of a warehouse, some are a garage operation.
MRCOOL is the only one I'm aware of the doesn't exclude owner installs in warranty coverage fine print. And Ingrams Water and Power is the primary distribution arm for them, the importer is in Miami - I've talked to them. Last year they brought 4000 units in and sold out mid-season. They initially tried to sell through conventional HVAC channels but got so much resistance they went their own way. The traditional industry only sells Mitsubishi, LG, Daikin, and Freidrich. And they charge a LOT for them.
It helps to understand that these units get installed all over the world. Local installers charge about $50 to install one in third world countries, like middle-east, poor asian countries, south american and africa. Only in the US do you find contractors wanting thousands of dollars to do the same job. The HVAC industry here is quite mature and steeped in traditional forced-air systems that are complex and expensive. The whole business model is built on that, so the profit model for cheap air simply doesn't work for them. Instead of embracing it and developing a profit model, they rail against them as ugly, cheap, poor quality, inefficient, and undependable. All of which is untrue. My favorite one is that women don't like the look of the inside air handler - sure, they don't even know what it is, and no worse looking than a floor fan. LOL