Dedicated outlet in the garage

Draztik

New member
Joined
Dec 12, 2015
Messages
3
I moved to a new house and need to get my compressor up and running again. I have an existing out I believe to be dedicated. Its currently on a tandem 20 amp breaker and I want to move it over to a new double pole 20 amp for my compressor. (I have space in my panel)

I turned off the breaker and checked every light/outlet in my house and the only one without power is the outlet I believe to be the dedicated outlet.

This outlet is also roughly 2 feet away from another outlet giving me another reason to believe its dedicated. Just above it is the central vac that was plugged into it. The reason I have not done this is because its labeled as bathroom receptacle which it is not as I tested all of them.

What say you? Is it safe to rewire it?

I've attached the outlet in question.
 

Attachments

  • 20160716_132542.jpg
    20160716_132542.jpg
    141.3 KB · Views: 83
To avoid these ads, REGISTER NOW!

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,267
Location
Penngrove, California
I agree that looks like a single (non duplex) 20 Amp receptacle that I suspect was provided to power the central vac. Are you going to no longer use the central vac?

It sounds like since you are suggesting a double pole breaker that you want 240VAC for your compressor. I see no reason to not change it to 240 VAC assuming the current requirements are within the limits of the 12 gauge wire it should now be wired with, and if a receptacle is used it is a proper 240vac receptacle. Put black tape on existing neutral conductor, which will no longer be neutral.

I am assuming the garage is attached since there appears to be multiple circuits to it.
 
OP
D

Draztik

New member
Joined
Dec 12, 2015
Messages
3
The central vac was plugged into this outlet, but i moved the vac over to the outlet next to it and works fine which you can see that it, and a refrigerator is plugged in. (vac is 110V 15amp)

Correct that I need 240 for my compressor and will tape the white end black to indicate hot. Just trying to avoid running running conduit to where I would like my compressor.
 

md21722

Well-known member
Joined
Nov 30, 2015
Messages
1,840
Location
Mt Juliet, TN
2HP compressor is the largest you can run on #12 NM-b.

3HP requires #10 NM-b (Romex) or #12 THHN in conduit.

5HP requires #8 NM-b (Romex) or #10 THHN in conduit.
 
To avoid these ads, REGISTER NOW!

sendokatum

Member
Joined
Jul 16, 2016
Messages
10
2HP compressor is the largest you can run on #12 NM-b.
g.png

3HP requires #10 NM-b (Romex) or #12 THHN in conduit.

5HP requires #8 NM-b (Romex) or #10 THHN in conduit.

How much is it?
 

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
...i moved the vac over to the outlet next to it and works fine which you can see that it, and a refrigerator is plugged in. (vac is 110V 15amp)...

So you have a central vac rated at 15 amps, and a fridge rated at ?? amps on the same circuit? Unless that fridge is a very small one, I sense trouble there. And probably the central vac is spec'ed for a dedicated circuit.
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Did you check to see if bathroom outlets go off when breaker is off. Alot of times the gfi is put in garage and then ran to bathrooms to protect those outlets,someone may have replaced the gfi.
 