Only buy a generator if you have thought long and hard about it.If you have ever thought about a generator, now is the time.
Before we throw the electrician under the bus and that was my first reaction. Let’s make a list of the Amp rating for the current 240-volt breakers
I agree that a 100 Amp panel will easily supply more than 100 amps of breakers. But without a list of the loads how will you decide what is needed?That's not how a load calc works
You have a lot to learn………. NOT even close to calculating loads.Before we throw the electrician under the bus and that was my first reaction. Let’s make a list of the Amp rating for the current 240-volt breakers and what they run and a second list for proposed new loads.
Let’s guess the that the current 200-amp house panel is maxed out and cannot feed the new garage.
If the new 2500 sqf garage needs
30A Heat pump
50 A heat strips
30 A water heater
50 A air compressor
20 A lift
50 A RV outlet
60 A electric car charger maybe 2
Plus, some shop equipment and 120V loads.
Is a 200-amp panel really over the top for the garage?
If you are adding solar in the future now is the time to make room for it in the service.
Walta
that is nowhere near how to do a load calc. youre doing exactly what the OPs electrician did. totally wrong.Before we throw the electrician under the bus and that was my first reaction. Let’s make a list of the Amp rating for the current 240-volt breakers and what they run and a second list for proposed new loads.
Let’s guess the that the current 200-amp house panel is maxed out and cannot feed the new garage.
If the new 2500 sqf garage needs
30A Heat pump
50 A heat strips
30 A water heater
50 A air compressor
20 A lift
50 A RV outlet
60 A electric car charger maybe 2
Plus, some shop equipment and 120V loads.
Is a 200-amp panel really over the top for the garage?
If you are adding solar in the future now is the time to make room for it in the service.
Walta
One of the electricians I'm talking to about wiring my to-be-built shop (500' from the pole) suggested that we combine the house and garage meters into one service and have the PoCo install a "ranch meter" somewhere between the pole and the shop. That way we're guaranteed to get full voltage at that meter that's hopefully significantly closer to the shop, and the PoCo will pay for trenching it to the meter. I think. It might help that it's a farm.
It may be worth asking your electrician if it's an option.
Without a list of the loads how will even begin to decide what is needed?You have a lot to learn………. NOT even close to calculating loads.
Without a list of the loads how will even begin to decide what is needed?that is nowhere near how to do a load calc. youre doing exactly what the OPs electrician did. totally wrong.
Without a list of the loads how will even begine to decide what is needed?
Agreed the breaker going to at least 20% higher than the load but it is data that one can collect quickly and any data is better than guessing. How much time can one invest in a free estimate.The breaker size is not the load.
thats up to the OP but simply adding up breaker ratings is definitely NOT the way to do a load calc.Without a list of the loads how will even begin to decide what is needed?
naw. you add up all the breakers in a panel youll be many times over the rating of the service. again, adding up breakers is completely pointless due to diversity of loads....Agreed the breaker going to at least 20% higher than the load but it is data that one can collect quickly and any data is better than guessing. How much time can one invest in a free estimate.


Any update on this?Thanks. I have another electrician coming over for bid and now I’m better informed on what to ask and look for and will ask all the questions from your guys recommendation. Appreciate it thanks. W.