Detached Shop Wire Size

Bevis

Well-known member
Joined
Jan 10, 2006
Messages
808
Location
Moore Haven, Florida
Getting some conflicting answers on what size copper wire to run thru my conduit to my detached shop. From my house 200 amp panel to the shop is 65' - 70', I want 100 amp to the shop panel. I have a 125 panel in the shop now, and will put a 100 amp breaker in the main house panel.
So should I run #1 or #2 for the distance / amp ?
 
To avoid these ads, REGISTER NOW!

JoeFin

Well-known member
Joined
Sep 13, 2013
Messages
717
Location
NorCal - where the Rednecks Race
Getting some conflicting answers on what size copper wire to run thru my conduit to my detached shop. From my house 200 amp panel to the shop is 65' - 70', I want 100 amp to the shop panel. I have a 125 panel in the shop now, and will put a 100 amp breaker in the main house panel.
So should I run #1 or #2 for the distance / amp ?

#2 awg
Voltage drop: 3.13
Voltage drop percentage: 1.30%
Voltage at the end: 236.87

under 3%
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
Who puts Aluminum in their own house

I figured it for 2 copper


I did, the SE conductors, house subfeed, & shop feeder are all AL. Aluminum is a great way to cut costs,and copper, or aluminum conductors installed improperly will cause problems, bias against aluminum conductors is just ignorance. BTW, #10 & 12 AWG AL conductors are still allowed by the NEC, if anyone was selling it. :shocking::shocking: And no, I would not use it..
 
To avoid these ads, REGISTER NOW!
OP
B

Bevis

Well-known member
Joined
Jan 10, 2006
Messages
808
Location
Moore Haven, Florida
Guess I could've just went back and reread older posts ... I had a shop rebuild this year, after a neighbor walked away from a burn pile that got away from him. Overgrown lot behind my shop lit up and ran in all direstions... I get a call from the Vol. fire chief telling me to get home and help fight my shop fire :shocking:
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Since you don't want aluminum, you only need #3 copper. 65-70' is nothing as far as voltage drop is concerned.

3-#3's and 1-#8 green is what you want. It will fly through 2" pipe.
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
Getting some conflicting answers on what size copper wire to run thru my conduit to my detached shop. From my house 200 amp panel to the shop is 65' - 70', I want 100 amp to the shop panel. I have a 125 panel in the shop now, and will put a 100 amp breaker in the main house panel.
So should I run #1 or #2 for the distance / amp ?

I ran 2-2-2-4 and breakered at 70A. Run is 120'. No problems with two AC units, heater, welding, etc, etc.

As wfor who put aluminum in their own house, I'd say people that learn the proper installation requirements to make a safe install. All utility runs to houses here are 4/0 AL. Nobody seems to be having problems with it.
 