Truss framed ceiling with 3/4 strapping and 5/8 fire rated drywall....

I mounted my blue poly light boxes as low as I could go on the bottom cord of the truss.

They do not extend fully to the bottom of the hole in the drywall... leave about 1/4" to 3/8" of the drywall holes showing.

Is this not big deal?

Or do I need to put an extension on the boxes?

If extension is required, do they even make them for the blue poly boxes?

Thanks in advance for any tips.
 
To avoid these ads, REGISTER NOW!

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Article 370-20 states they can set back no more than 1/4" from the finish surface. I don't understand why you could not have brought them down more, plus they make adjustable boxes. They do make box extensions for the blue boxes. It is a code violation if they set back more. its up to you if you want to use extensions or not.


https://www.lowes.com/pd/CARLON-Blu...dard-Box-Extender-Wall-Electrical-Box/4411965
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
1/4" is the max allowed by the NEC that the front edge of the box can be back from the drywall finished surface.
 
OP
M

Mainiac Mat

Well-known member
Joined
Sep 2, 2020
Messages
402
Location
Maine
Thanks for the help.

I bought the standard (inexpensive) Carlin blue 4" diameter boxes and nailed them as close to the bottom of the truss as I could get... which (unbeknownst to me at the time) doesn't span the 1-3/8" needed to bridge both the strapping and sheet rock.

box.JPG


I didn't mount the boxes to the strapping because the attic deck is already in, so I had to install insulation from the bottom (staple up kraft faced fiberglass) and it's a lot easier to put that in before the strapping.... but rough wiring had to be done before the insulation....

Once I got the strapping up I could see that the boxes were going to be high... and sure enough, now that I have half of the rock up... there's a gap.

Seems like a non-issue and I've already had my rough wiring inspection... not sure if I'll just use as is, or get the Carlon extensions.
 
Last edited:

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Thanks for the help.

I bought the standard (inexpensive) Carlin blue 4" diameter boxes and nailed them as close to the bottom of the truss as I could get... which (unbeknownst to me at the time) doesn't span the 1-3/8" needed to bridge both the strapping and sheet rock.

box.JPG


I didn't mount the boxes to the strapping because the attic deck is already in, so I had to install insulation from the bottom (staple up kraft faced fiberglass) and it's a lot easier to put that in before the strapping.... but rough wiring had to be done before the insulation....

Once I got the strapping up I could see that the boxes were going to be high... and sure enough, now that I have half of the rock up... there's a gap.

Seems like a non-issue and I've already had my rough wiring inspection... not sure if I'll just use as is, or get the Carlon extensions.

What I linked was for device boxes, I would imagine they would make a extender for round plastic as well
 
OP
M

Mainiac Mat

Well-known member
Joined
Sep 2, 2020
Messages
402
Location
Maine
This is the product Carlon makes.... they call it a "Plaster Ring" and it steps down from 4" dia. to 3" dia. and they come with either a 1/2" step or a 5/8" step.

carlon.jpg

Looks like a workable option....
 
To avoid these ads, REGISTER NOW!
OP
M

Mainiac Mat

Well-known member
Joined
Sep 2, 2020
Messages
402
Location
Maine
You had me scared there for a minute....

Though not ideal, it appears that I'm code compliant...

attachment.php


attachment.php


fire1.JPG

fire2.JPG
 

66cj225

Well-known member
Joined
Nov 4, 2011
Messages
332
Location
NH
Thanks for the info, I was just guessing. Now I'm going to toss a blue box in the wood stove for chuckles.
 

66cj225

Well-known member
Joined
Nov 4, 2011
Messages
332
Location
NH
The box that went into the stove had a UL BH122 and kind of a glass mat finish. It didn't support combustion but became a totally different shape by melting (blob) within 5 minutes.
 
OP
M

Mainiac Mat

Well-known member
Joined
Sep 2, 2020
Messages
402
Location
Maine
The box that went into the stove had a UL BH122 and kind of a glass mat finish. It didn't support combustion but became a totally different shape by melting (blob) within 5 minutes.

Not exactly UL or ASTM testing standards... but a little unsettling just the same. But if you have that type of intense fire, I think you're screwed regardless.
 

mobetta

Well-known member
Joined
Feb 10, 2010
Messages
370
Location
twin cities, mn
Yeah i think its pretty funny that I had to make a "firewall"(5/8 gyp both sides to roof deck) on my lot line wall but theres is absolutely no care given to the wiring/boxes/penetrations on that wall.