Does anyone have a 2005 or previous code book laying around?

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,136
Location
Central Iowa
I need the code reference that a three wire feeder needs to have the neutral bonded.

I have a friend that was telling me about a service call he went on to add a circuit for a compressor. It's a pole barn built in the 90's. He was telling me how he couldn't believe some idiot ran a three wire feeder to it and actually bonded the neutral, so he took the bonding screw out and installed a separate ground bar to isolate the grounds. I told him he needs to get back out there asap and put the screw back in. It turned into a bit of an argument which ended with he wasn't going to drive all the way back out there unless I could prove it to him.

I thought I had a 2005 NEC on the shelf, but I don't. The oldest code book I have is a 2008, and I believe that's the first edition that required four wire feeders. I did show him 250.32(B)(1) exception #1 in the 2020, but that isn't good enough even though it speaks of previous editions of the NEC allowing the grounded conductor being used as a ground fault return path.
 
To avoid these ads, REGISTER NOW!

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
2005 NEC>
250.21
(B) Alternating-Current Systems of 50 Volts to 1000Volts.
Alternating-current systems of 50 volts to 1000 volts
that supply premises wiring and premises wiring systems
shall be grounded under any of the following conditions:
(1) Where the system can be grounded so the maximum voltage to ground on ungrounded conductors does not exceed 150 volts.

It's the same wording as in the 2002 NEC
 
Last edited:

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,892
Location
NW Iowa
I don't know why it's hard to understand. Shouldn't even need a code reference to get it.

A ground wire always needs to return to the neutral connection at the transformer. It has to connect to neutral in order to clear a fault. Dirt doesn't carry fault current. If the ground doesn't connect back to the neutral at some point it's wrong and dangerous, simple as that.
 
OP
S

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,136
Location
Central Iowa
I know that. You know that. Almost all of us know that. I agree, it's pretty easy to understand and I really don't know what the problem is. He was even dropping names of the instructors that taught him that the neutral doesn't get bonded when he went through the IBEW apprenticeship in the 90's. (before I get jumped on that the IBEW wouldn't teach such a thing, I know. He's mistaken). The kind of funny part is that he told me the ground rods are usually good enough, but admitted that they aren't so good if the ground is dry.
 
OP
S

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,136
Location
Central Iowa
I don't know why it's hard to understand. Shouldn't even need a code reference to get it.

A ground wire always needs to return to the neutral connection at the transformer. It has to connect to neutral in order to clear a fault. Dirt doesn't carry fault current. If the ground doesn't connect back to the neutral at some point it's wrong and dangerous, simple as
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
I don't have a 2005 NEC, what I do have is my 2008 analysis of changes. Looks like 215.6. Pretty much starting in 2008 requires a 4-wire feeder, but all existing 3-wire is grandfathered by the exception in 250.32(B). which still reads like that in the 2017 NEC. Im sure the 2020 is same, just don't have the edition yet
 

Attachments

  • Scan_20211202.pdf
    150.6 KB · Views: 18
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Your buddy sounds like someone that will continue to come up with excuses why he is right and you are wrong. A code reference probably won't change anything
 
Last edited:

BigGarage

Well-known member
Joined
Jun 5, 2019
Messages
2,347
Location
Just south of Detroit, MI.
2005 NEC>
250.21
(B) Alternating-Current Systems of 50 Volts to 1000Volts.
Alternating-current systems of 50 volts to 1000 volts
that supply premises wiring and premises wiring systems
shall be grounded under any of the following conditions:
(1) Where the system can be grounded so the maximum voltage to ground on ungrounded conductors does not exceed 150 volts.

It's the same wording as in the 2002 NEC
In my 2005 NEC codebook this above info is from the 250.20 . The 250.21 info is different.

To answer the OP, yes I have a 2005 NEC National Electrical Code book.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
In my 2005 NEC codebook this above info is from the 250.20 . The 250.21 info is different.

To answer the OP, yes I have a 2005 NEC National Electrical Code book.
Yes, I made another mistake (that's the story of my life). The correct cite is 250.20
 
Last edited:
OP
S

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,136
Location
Central Iowa
I don't have a 2005 NEC, what I do have is my 2008 analysis of changes. Looks like 215.6. Pretty much starting in 2008 requires a 4-wire feeder, but all existing 3-wire is grandfathered by the exception in 250.32(B). which still reads like that in the 2017 NEC. Im sure the 2020 is same, just don't have the edition yet
That did it. He claims to be going out to put it back today. Thank you.
How about the online free version on the NFPA’s website?
I didn't know there was such a thing.
Your buddy sounds like someone that will continue to come up with excuses why he is right and you are wrong. A code reference probably won't change anything
Almost. The picture in the 2008 analysis Terry posted is what finally did it.
Yes, I made another mistake (that's the story of my life). The correct cite is 250.20
It didn't matter. It was nothing but an argument with him telling me that that cite meant it had to have ground rods. In the end, it required a picture.
 

4xdog

Well-known member
Joined
Aug 18, 2012
Messages
5,669
Location
Santa Fe, NM
I found a copy of the 1975 NEC yesterday on the shelves as I‘m cleaning out my parents’ old home. Almost certainly my brother’s when he was in high school.

Lemme know if you need a specific section, @sparky 1971.

i-gWjJxPd-X3.jpg
 