wyliesdiesels
Well-known member
The neutral? 480 corner ground has two pole breaker, ground and neutral tied to one phase, (breaker not to break Grounded phase) four wire would be 240/480 four wire. 240 volt stuff connected to phase to ground two phases , wild leg for three phase stuff, three pole breaker.
More common to use 277/480 four wire, more common equipment. Light ballast, exit lights and such. Haven't see much 240V equipment. (240V would probally work at 277V +- 10%)
There is no neutral on a corner grounded delta.
By NEC definition the grounded phase on a corner grounded delta is NOT a neutral.
And you cant have a grounded neutral on a corner grounded delta.