Dual 6-50R Receptacles

bad_idea

Well-known member
Joined
Jun 11, 2011
Messages
4,338
Location
Pasquotank, NC
I have two welding machines on a cart. I only use one at a time. I have an extension cord for plugging the machines in. I would like to put two 6-50R receptacles on the end of the cord, I am tired of unplugging one machine to use the other. I am looking for an elegant solution to make up a good cord end. I am thinking a 3 gang box with two 6-50R receptacles in it. I have been unable to find a cover plate for the two. I can make one up, but would rather use an over the counter solution. Ideas?
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,786
2 deep 4X4 boxes nippled together w/ a 1/2" raised cover for 30/50A devices.



No need to reinvent the wheel when off the shelf will work, put a 3rd box between the two to splice the cables w/ a blank cover on it.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
I looked at the Hubbell catalog a bit and didn't see an off the shelf solution.

I'd do what Norcal suggested and just use two boxes.
 

BukitCase

Well-known member
Joined
Apr 11, 2017
Messages
1,075
Location
Oregon
I made an 85' 8/4 SOOW cord (the extra wire is if I ever decide I want 120 volts also) just as Norcal suggests - 2 deep 4x4 boxes locked together with 2 chase *******, clamp at input of first box - plenty of room to strip some cable and use BOTH chases to wire the SECOND 6-50R.

Even my mm252 runs fine at any setting, the mm211 and or PM45 don't even know they're on an extension... Steve
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
I made an 85' 8/4 SOOW cord (the extra wire is if I ever decide I want 120 volts also) just as Norcal suggests - 2 deep 4x4 boxes locked together with 2 chase *******, clamp at input of first box - plenty of room to strip some cable and use BOTH chases to wire the SECOND 6-50R.

Even my mm252 runs fine at any setting, the mm211 and or PM45 don't even know they're on an extension... Steve

Why 2 *******, did you run 2 strands of #8 through each one?
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
2 deep 4X4 boxes nippled together w/ a 1/2" raised cover for 30/50A devices.
Over time the movement of the cable will loosen the locknuts on the sheet metal boxes.
Additionally the remaining KO's are too easily knocked in.
I'd use deep boxes with threaded hubs (like Bell boxes).
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Over time the movement of the cable will loosen the locknuts on the sheet metal boxes.
Additionally the remaining KO's are too easily knocked in.
I'd use deep boxes with threaded hubs (like Bell boxes).
I think part of the point of this setup is to not need to plug and unplug anything at the cart
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,786
I made an 85' 8/4 SOOW cord (the extra wire is if I ever decide I want 120 volts also) just as Norcal suggests - 2 deep 4x4 boxes locked together with 2 chase *******, clamp at input of first box - plenty of room to strip some cable and use BOTH chases to wire the SECOND 6-50R.

Even my mm252 runs fine at any setting, the mm211 and or PM45 don't even know they're on an extension... Steve
Going to add a circuit breaker for the 120V, or use a 50A,125V receptacle? If you do it....
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,229
Location
NJ
Over time the movement of the cable will loosen the locknuts on the sheet metal boxes.
Additionally the remaining KO's are too easily knocked in.
I'd use deep boxes with threaded hubs (like Bell boxes).
I use bonding locknuts so that doesn't happen. Can also get boxes w/o ko's.
 

BukitCase

Well-known member
Joined
Apr 11, 2017
Messages
1,075
Location
Oregon
Probably will NOT do 120 on this cord, other end is just a single 50P. Main reason for the extra conductor is the old hotrodder adage, "run whut ya brung" :D

Can't find non-knockout boxes here, couple quick tacks with mig works.

mm08822 got the reason for 2 ******* - IME that also lessens likelihood of lock nuts loosening.

Yeah, IIRC I ran ground and the "spare" thru the second ******.

I also back up nuts with the smooth plastic nuts, less likelihood of chafing AND tends to (sorta) act as a lock nut.

I have 3 hard-wired 6-50Rs within 10-15 feet of where I do probably 95% of my welding, the 85' hangs on a garden hose hanger unless I need it for the rare exception... Steve
 
Last edited:

Noltz

Well-known member
Joined
Mar 10, 2020
Messages
377
Location
Ontario, Canada
3D printing would solve this. I had a similar situation and this is what I came up with when the newb electrician left me with no cover & none to be found. This is a backup compressor outlet that's used while we're servicing the main one.
 

Attachments

  • 20230627_140401.jpg
    20230627_140401.jpg
    406.8 KB · Views: 27

jpaw

Well-known member
Joined
Dec 23, 2018
Messages
527
Location
Michigan
There are always surface mount receptacles that could be made into a splitter cable. But I agree that 2 deep boxes attached to each other is probably the best diy way.
A custom touch would be some rubberized undercoating or bed liner for a durable finish.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,786
There are always surface mount receptacles that could be made into a splitter cable. But I agree that 2 deep boxes attached to each other is probably the best diy way.
A custom touch would be some rubberized undercoating or bed liner for a durable finish.
Surface mount receptacles are rather fragile, used one on a extension cord 40 years ago or so before I knew better, it worked great for me, but when someone else used it they dropped it rendering it into trash, even a 4X4 box fares poorly for the same reasons plus not compliant to use either one that way, it would not take much to crack them on a welding cart, a previous suggestion to use Bell boxes is good, with a chrome or stainless plate to trim it out makes it look pretty good.
 

jpaw

Well-known member
Joined
Dec 23, 2018
Messages
527
Location
Michigan
Surface mount receptacles are rather fragile, used one on a extension cord 40 years ago or so before I knew better, it worked great for me, but when someone else used it they dropped it rendering it into trash, even a 4X4 box fares poorly for the same reasons plus not compliant to use either one that way, it would not take much to crack them on a welding cart, a previous suggestion to use Bell boxes is good, with a chrome or stainless plate to trim it out makes it look pretty good.
I completely agree with your first post.
I have been using a modified surface mount as an adapter for my generator cord for years without an issue. However I do agree that it is not the most durable option.
In the op's situation I would look at permanently mounting what ever he uses to the welding cart. It makes plugging and unplugging much easier when you just have to hold the cart. Also offers some protection to the boxes.
 