Duct type for kitchen , bath and dryer

OP
B

branimal

Well-known member
Joined
May 31, 2016
Messages
1,938
Also do you guys think butterfly backdraft dampers are worth installing to keep the cold air out?
 

Attachments

  • BD__03930.1383137452.1280.1280 (1).gif
    BD__03930.1383137452.1280.1280 (1).gif
    22.3 KB · Views: 15
Last edited:
To avoid these ads, REGISTER NOW!
OP
B

branimal

Well-known member
Joined
May 31, 2016
Messages
1,938
Found a round roof vent in HD’s site.
c3a4219277440599b96b95fe7653f4cf.jpg


Sent from my iPhone using Tapatalk
 

Attachments

  • c3a4219277440599b96b95fe7653f4cf.jpg
    c3a4219277440599b96b95fe7653f4cf.jpg
    185.3 KB · Views: 0
OP
B

branimal

Well-known member
Joined
May 31, 2016
Messages
1,938
yeldogt; said:
With a low slope flat roof -- modified that's full torch down with granular coating. I would have used a torched down non granular a base -- attached the flange torching it down. Covered with granular torch down. You ahve to ver a flat roof as it will flood with water.

Just want to confirm the steps:

1. torch down the base sheet,
2. torch the flange of the pitch pan to the base sheet
3. torch the granular sheet

Also is cutting a hole in the sheets the size of the vent pipe preferable to laying sheets all around the sides?
 
OP
B

branimal

Well-known member
Joined
May 31, 2016
Messages
1,938
mrobins297aaa; said:
you need a damper for the kitchen hood either at the hood or at the roof if you don't your going to get a lot of cold air coming in.
you don't need them at both places

Thanks! Does the same logic apply to bathroom and dryer exhaust?
 
To avoid these ads, REGISTER NOW!

Elaheh

Member
Joined
Dec 13, 2020
Messages
5
Location
Dubai
Local exhaust ventilation is good for kitchens and bathrooms, but fans must be certified
to provide their rated airflow at 0.25 in w.c. Standard 62.2 requires that local exhaust ventilation be provided for:
Kitchens: 100 cfm or more if intermittently operated OR 5 air changes per hour (ACH) of kitchen volume if continuously operated
Bathrooms: 50 cfm or more if operated intermittently OR 20 cfm if continuously operated
if your budget is tight, a simple ventilation improvement such as an upgraded bath fan, though not ideal, can meet the minimum requirements for both local exhaust ventilation and whole-building ventilation.
 

Elaheh

Member
Joined
Dec 13, 2020
Messages
5
Location
Dubai
Also do you guys think butterfly backdraft dampers are worth installing to keep the cold air out?
Yeah for sure, butterfly dampers are installed in round ductwork to prevent damper protection from air leakage. They would reduce your energy consumption as well and make your ductwork perform in better way.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Local exhaust ventilation is good for kitchens and bathrooms, but fans must be certified
to provide their rated airflow at 0.25 in w.c. Standard 62.2 requires that local exhaust ventilation be provided for:
Kitchens: 100 cfm or more if intermittently operated OR 5 air changes per hour (ACH) of kitchen volume if continuously operated
Bathrooms: 50 cfm or more if operated intermittently OR 20 cfm if continuously operated
if your budget is tight, a simple ventilation improvement such as an upgraded bath fan, though not ideal, can meet the minimum requirements for both local exhaust ventilation and whole-building ventilation.

Just to let you know, you are posting in a thread that is almost 1 1/2 years old
 