I have a two ton ductless split

Unit is rated for 208 VAC.. L1 L2 and gnd are the only terminals at the unit.. there is no neutral terminal

I ran 220V AC 30 Amp service from the panel 8/3 wire L1 Black L2 Red Nuetral White GND Bare copper. There is no place to connect the neutral wire in the unit

Can anyone offer advice?

Thanks,
 
To avoid these ads, REGISTER NOW!

Fixin'Stuff

Well-known member
Joined
Jun 14, 2016
Messages
584
Location
HotterNHellHouston
Neutral isn't used. Just connect L1, L2 and ground. You only need neutral for devices that also use 120 volts (some stoves use 120 volts to power the clock and controls).
 
OP
S

shillamus

Well-known member
Joined
Sep 6, 2015
Messages
75
Thanks for the quick response

Guess I have an extra conductor and I ran 8 GA for 25A.. looks way to beefy.. 10 would have been fine
 
To avoid these ads, REGISTER NOW!

gtae07

Well-known member
Joined
Mar 6, 2015
Messages
2,979
Location
Fayetteville, GA
Cap and stow the neutral in your disconnect box.

I ran 8 gauge wire, too. And 6 gauge to the 50A welder sockets. I didn't know what the next person might want to install (or what else I might want to use) so I figured it was best to assume 100% duty cycle.
 