600SL
Well-known member
I'm in kind of an emergency situation at the moment with temps dropping down to near 0°F. Two days ago I smelt a burning smell and was unable to determine there it was coming from. Then yesterday I tripped the 2 pole 240V 60 amp e-heat CB, which in turn shuts down the entire heat pump system. I reset the CB and everything was fine until last night when the CB tripped again. So reset it and I took a non contact temperature measurement at the screw terminals on the CB. One terminal was running at ~ 125°F the other one was running ~90°F. Occasionally I would notice a bussing noise. I removed the hot side but really didn't find anything loose or incorrect. Re-torqued it in place and temperature is still about 20 degrees higher on one pole. I ordered a new CB but it wont be in until Wednesday. My question is would this definitely be caused by a bad CB or could the heating coil be a problem. My work around for the next few days will be to steel a 125A breaker from somewhere else but I would really hate to do that if there is a problem with the heating coils