wssix99
Well-known member
This was reminding me about the other threads where we talk about vacuum cleaner cords that appear to be undersized...
There is a section of the electric code that deals with flexible cords, specifically for this type of equipment: Article 400
http://ecmweb.com/code-basics/flexible-cords-cables-and-fixture-wire
Table 400.5(A) of the NEC calls allows 18A on a 14 gauge flexible cord where only two conductors carry current.
There is a section of the electric code that deals with flexible cords, specifically for this type of equipment: Article 400
http://ecmweb.com/code-basics/flexible-cords-cables-and-fixture-wire
Take a closer look and see the 3" lead is only SJOOW 14/3. On a 25 amp circuit? Can that be right?
Table 400.5(A) of the NEC calls allows 18A on a 14 gauge flexible cord where only two conductors carry current.