Electrical panel model for purchasing new breaker?

dutch724

Member
Joined
May 22, 2017
Messages
10
Location
Middlesex, NC
I am in the process of adding a subpanel for my garage I'm building. I would like to purchase a new 100a breaker for this old panel that is my main that I'm pull 100a off of, but I'm not sure what siemens breaker to buy. If I could get a little help in this area it would be appreciated. Or is there a place I can look to see what model it would be?
20250611_184920.jpg20250622_172119.jpg
 
To avoid these ads, REGISTER NOW!

Codyboy

Well-known member
Joined
Jan 31, 2019
Messages
1,734
Location
S.E. TEXAS
Are there any spaces left? That's a long panel for only those 4 spaces.
If there are empty spaces not pictured..
I would pull the cover and look at it, take a couple pictures or just pop a breaker out and head to home depot.
 

Codyboy

Well-known member
Joined
Jan 31, 2019
Messages
1,734
Location
S.E. TEXAS
There should be a label on the inside of the cover.

Where are you going to put it?

Why 100a?

Considering you have a challenger and a Siemens breaker, I'd say you need more than a new breaker. I'd recommend an electrician

25 years ago on a house we had It had challenger and siemens breakers mixed as I recall. It was a 100A panel. Whether that was wrong IDK.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,080
Location
Richmond, VA
25 years ago on a house we had It had challenger and siemens breakers mixed as I recall. It was a 100A panel. Whether that was wrong IDK.
Lots of breakers fit in lots of panels but aren't rated for it.

Not a sparky, but AFAIK, they are not cross compatible. Could be wrong but it would be the first time ever...
 

kctgb

Well-known member
Joined
Jul 7, 2024
Messages
305
Pull a breaker out and take it to the electrical store. Your service panel looks like it needs work, is it falling off the wall? In my state a sub panel has to have 4 wires to it. 2 hot wires(220), a neutral, and a ground. The neutral and ground have to have separate buse bars, code doesn’t allow the neutral and ground to use the same buse bars. According to the national electric code any panel after the main service panel has to have 4 wires. Having the neutral and ground separated doesn’t allow the neutral to be used as a ground. If you don’t know what you are doing call an electrician.
 
Last edited:

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,080
Location
Richmond, VA
Pull a breaker out and take it to the store. Your service panel looks like it needs work, is it falling off the wall? In my state a sub panel has to have 4 wires to it. 2 hot wires(220), a neutral, and a ground. The neutral and ground have to have separate buse bars, code doesn’t allow the neutral and ground to use the same buse bars. Having the neutral and ground separated doesn’t allow the neutral to be used as a ground.
Pulling a breaker only tells you what could be stuffed in there not what is the right one
 

kctgb

Well-known member
Joined
Jul 7, 2024
Messages
305
Pulling a breaker only tells you what could be stuffed in there not what is the right one
Pulling a breaker tells him what 220 breaker will fit the two main buse bars in the panel. A service panel has two hot bars in the middle, each one is 120 volts. He needs a 220 breaker that connects to both sides of the buse bars to feed 220 to the sub panel.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,080
Location
Richmond, VA
Pulling a breaker tells him what 220 breaker will fit the two main buse bars in the panel. A service panel has two hot bars in the middle, each one is 120 volts. He needs a breaker that connects to both sides of the buse bars to feed 220 to the sub panel.
You are missing the problem.

Panels are rated for specific model breakers. What fits is not sufficient.
 

kctgb

Well-known member
Joined
Jul 7, 2024
Messages
305
Pulling a breaker only tells you what could be stuffed in there not what is the right one
If it was me I would replace his service panel with a square D panel. Everyone has parts and breakers for square D.
 

kctgb

Well-known member
Joined
Jul 7, 2024
Messages
305
You are missing the problem.

Panels are rated for specific model breakers. What fits is not sufficient.
If he has a seaman’s service panel he needs to buy a 220 breaker for a seaman’s service panel. It not rocket science!
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,080
Location
Richmond, VA
If he has a seaman’s service panel he needs to buy a 220 breaker for a seaman’s service panel. It not rocket science!
Does he?

I see a challenger breaker and a Siemens breaker. One is right, one is wrong.

I bet it isn't a Siemens
 

mikedodge

Well-known member
Joined
Jun 27, 2017
Messages
2,879
If there's no visible label on the panel there might be with the cover off.

Those Siemens QP breakers have a lot of compatibility physically but if they are listed or not for those panels is another story.
 

kctgb

Well-known member
Joined
Jul 7, 2024
Messages
305
That is Mike's point.......or any approved mfr with classified cb's.
I’ll bet square D makes a breaker that will fit in his seaman’s service panel. Probably lots of manufacturers make breakers that will fit his panel. Do you understand why I said to take a breaker out and take it to an electrical supply store???
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,072
Location
NJ
Are there any spaces left? That's a long panel for only those 4 spaces.
If there are empty spaces not pictured..
I would pull the cover and look at it, take a couple pictures or just pop a breaker out and head to home depot.
OP, w/o better pics, no one knows.

Include a pic of the mfr's label (or what is left of it).
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,072
Location
NJ
I’ll bet square D makes a breaker that will fit in his seaman’s service panel. Probably lots of manufacturers make breakers that will fit his panel. Do you understand why I said to take a breaker out and take it to an electrical supply store???
I'm not a mind reader, No. Wal-mart doesn't sell crystal balls (that work).

The parts jockey at the supply house is not always as well versed as one may hope for. First question to ask is who is the panel mfr.
 

kctgb

Well-known member
Joined
Jul 7, 2024
Messages
305
From the picture I would advise he fix the service panel first. The local electrical inspector would jump three feet in the air without bending his knees after seeing the service panel.
 
OP
D

dutch724

Member
Joined
May 22, 2017
Messages
10
Location
Middlesex, NC
Ok, ok, you guys have me laughing. I'm going to pull the panel apart this evening when I get home. I was just going to Lowes on the way home and wonder if anyone was able to tell me which model that panel was. I was not sure if there was any sticker that said what it was.
I didn't want to leave the house without water or A/C to take the breaker to the hardware store to figure out which breaker it was, but if it needs to be done so be it.
Why 100a.... why not? Its all I need in my garage.
Panel leans a bit, but will be fixed once I begin the work on it. There will be no city inspections on this project, just a licensed electrician over my shoulder the whole way.
The subpanels I buy are all Square D. Bought this house a few yrs ago and when I bought it the panel was leaning then. When the inspector saw it then he said it needed to be fixed. They put a screw in it and called it a day. That's why I say it will be fixed right when I'm adding a subpanel. It's while your in there kind of work. :) The whole area needs to be cleaned up and will get done. This is the first major project that I have been able to afford to do to this house. In the past history of this house it has been abused and not taken care of. My wife and I slowly fixing it up to where we like it to be.
I really appreciate the help and the comments. Thanks everyone.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,110
Location
Modesto, CA
Pulling a breaker tells him what 220 breaker will fit the two main buse bars in the panel. A service panel has two hot bars in the middle, each one is 120 volts. He needs a 220 breaker that connects to both sides of the buse bars to feed 220 to the sub panel.
incorrect way to go about it. code requires you to use listed breakers for that panel. merely pulling an existing breaker that could be the wrong breaker (not listed for that panel) is not the way to go about it. just because it fits doesnt mean its correct.

need to read the panel label or if missing look at the main breaker...
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,110
Location
Modesto, CA
I’ll bet square D makes a breaker that will fit in his seaman’s service panel.
again, its not about FITS, its about listings.....

Probably lots of manufacturers make breakers that will fit his panel. Do you understand why I said to take a breaker out and take it to an electrical supply store???
lots of manufacturers DO NOT make classified breakers for other panels. you are incorrect.... bringing a breaker to a supply counter person will not net you the correct breaker. it will net you a breaker of the same brand you have in your hand. the supply counter people wont know what panel you have or what is listed to go into it..... again completely wrong way to go about this...
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,072
Location
NJ
Ok, ok, you guys have me laughing. I'm going to pull the panel apart this evening when I get home. I was just going to Lowes on the way home and wonder if anyone was able to tell me which model that panel was. I was not sure if there was any sticker that said what it was.
I didn't want to leave the house without water or A/C to take the breaker to the hardware store to figure out which breaker it was, but if it needs to be done so be it.
Why 100a.... why not? Its all I need in my garage.
Panel leans a bit, but will be fixed once I begin the work on it. There will be no city inspections on this project, just a licensed electrician over my shoulder the whole way.
The subpanels I buy are all Square D. Bought this house a few yrs ago and when I bought it the panel was leaning then. When the inspector saw it then he said it needed to be fixed. They put a screw in it and called it a day. That's why I say it will be fixed right when I'm adding a subpanel. It's while your in there kind of work. :)
I really appreciate the help and the comments. Thanks everyone.
The form factor of the cb is already figured out.........if a Siemens QP is in there now, another siemens will fit, as will a SQ D Homeline, EatonBR, Challeger, Zinsco, Bryant, Murray, etc.

Need the panel mfr info first to do it correctly.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,110
Location
Modesto, CA
Ok, ok, you guys have me laughing. I'm going to pull the panel apart this evening when I get home. I was just going to Lowes on the way home and wonder if anyone was able to tell me which model that panel was. I was not sure if there was any sticker that said what it was.
I didn't want to leave the house without water or A/C to take the breaker to the hardware store to figure out which breaker it was, but if it needs to be done so be it.
Why 100a.... why not? Its all I need in my garage.
Panel leans a bit, but will be fixed once I begin the work on it. There will be no city inspections on this project, just a licensed electrician over my shoulder the whole way.
The subpanels I buy are all Square D. Bought this house a few yrs ago and when I bought it the panel was leaning then. When the inspector saw it then he said it needed to be fixed. They put a screw in it and called it a day. That's why I say it will be fixed right when I'm adding a subpanel. It's while your in there kind of work. :) The whole area needs to be cleaned up and will get done. This is the first major project that I have been able to afford to do to this house. In the past history of this house it has been abused and not taken care of. My wife and I slowly fixing it up to where we like it to be.
I really appreciate the help and the comments. Thanks everyone.
Take a pic of the entire panel with the door open, a pic of the main breaker close up, and a pic of the entire panel with the deadfront removed (if you feel comfortable).
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
I’ll bet square D makes a breaker that will fit in his seaman’s service panel. Probably lots of manufacturers make breakers that will fit his panel. Do you understand why I said to take a breaker out and take it to an electrical supply store???
Sq D breakers are not UL classified to be used in ANY competitive make of panel.

 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,048
Location
Central Iowa
I’ll bet square D makes a breaker that will fit in his seaman’s service panel. Probably lots of manufacturers make breakers that will fit his panel. Do you understand why I said to take a breaker out and take it to an electrical supply store???
Square D makes breakers that are listed for Square D panels and nothing else. Eaton and Connecticut Electric are the two companies I know of that make classified breakers to fit oddball panels.

I'd throw a Siemens QP2100 in it and be done.
 
OP
D

dutch724

Member
Joined
May 22, 2017
Messages
10
Location
Middlesex, NC
Above all I want to do this correctly and safe. I am a person that wants to replace parts with what the manufacture requires. This is electricity and my family's safety is important. If the well pump breaker is not the correct breaker for this panel it will be replaced.
I will pull the panel cover and get some good pics for everyone to see. I can do this work, but I want it up to code this is why I hired an electrician to watch and approve everything I'm doing.
I'm ready for lots more question and comments..... let them rip!:p
 

kctgb

Well-known member
Joined
Jul 7, 2024
Messages
305
Seimans make QD breakers for square D that are UL listed, I’ve used them a number of times.
 

kctgb

Well-known member
Joined
Jul 7, 2024
Messages
305
I wonder how many different ways we can spell Siemens. I count three so far

Is seagrams pushing it?
AI *****! I hated auto correct and I hate artificial intelligence. Something we all can live without.
 

Model A Fan

Well-known member
Joined
Dec 1, 2011
Messages
1,223
Location
NW Washington
As others have said, install a better panel (SQ D makes the Toyota/Lexus of panels and products with their Homeline/QO), run some new wire for your garage, power your garage as needed. If you want to keep cost down, you can go with a smaller breaker and wire. What will you be powering in your garage?

At the very least, that box is very crusty and needing to be cleaned. If you don't want to replace the panel, can you steal the spot the pump is in for your garage breaker and then run the pump off the garage sub-panel? Then you're only having to do rewiring on the pump instead of the whole panel.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,110
Location
Modesto, CA
Why 100a.... why not? Its all I need in my garage.
but will you really need 100a? you'll need at minimum (depending on distance) #1 AL or #3 CU. If you step it down to 90a you could go with #2 AL and save some money using MHF.

what will you be running in there? how many people at the same time? this will play a big factor in required feeder size
 

Codyboy

Well-known member
Joined
Jan 31, 2019
Messages
1,734
Location
S.E. TEXAS
Ok, ok, you guys have me laughing. I'm going to pull the panel apart this evening when I get home. I was just going to Lowes on the way home and wonder if anyone was able to tell me which model that panel was. I was not sure if there was any sticker that said what it was.
I didn't want to leave the house without water or A/C to take the breaker to the hardware store to figure out which breaker it was, but if it needs to be done so be it.
Why 100a.... why not? Its all I need in my garage.
Panel leans a bit, but will be fixed once I begin the work on it. There will be no city inspections on this project, just a licensed electrician over my shoulder the whole way.
The subpanels I buy are all Square D. Bought this house a few yrs ago and when I bought it the panel was leaning then. When the inspector saw it then he said it needed to be fixed. They put a screw in it and called it a day. That's why I say it will be fixed right when I'm adding a subpanel. It's while your in there kind of work. :) The whole area needs to be cleaned up and will get done. This is the first major project that I have been able to afford to do to this house. In the past history of this house it has been abused and not taken care of. My wife and I slowly fixing it up to where we like it to be.
I really appreciate the help and the comments. Thanks everyone.
So those are the only spaces in there? Those two double poles?

Where will the new breaker go to feed the sub panel?
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,048
Location
Central Iowa
Seimans make QD breakers for square D that are UL listed, I’ve used them a number of times.
I've used them a number of years ago as well but that doesn't change the fact that SQD doesn't make a listed breaker for other brands even though a Homeline would fit in this situation.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,080
Location
Richmond, VA
Ok, ok, you guys have me laughing. I'm going to pull the panel apart this evening when I get home. I was just going to Lowes on the way home and wonder if anyone was able to tell me which model that panel was. I was not sure if there was any sticker that said what it was.
I didn't want to leave the house without water or A/C to take the breaker to the hardware store to figure out which breaker it was, but if it needs to be done so be it.
Why 100a.... why not? Its all I need in my garage.
Panel leans a bit, but will be fixed once I begin the work on it. There will be no city inspections on this project, just a licensed electrician over my shoulder the whole way.
The subpanels I buy are all Square D. Bought this house a few yrs ago and when I bought it the panel was leaning then. When the inspector saw it then he said it needed to be fixed. They put a screw in it and called it a day. That's why I say it will be fixed right when I'm adding a subpanel. It's while your in there kind of work. :) The whole area needs to be cleaned up and will get done. This is the first major project that I have been able to afford to do to this house. In the past history of this house it has been abused and not taken care of. My wife and I slowly fixing it up to where we like it to be.
I really appreciate the help and the comments. Thanks everyone.
100a is a decent amount more expensive than 90a. Also more than 60a and 60a will do nearly all single person shops
 
OP
D

dutch724

Member
Joined
May 22, 2017
Messages
10
Location
Middlesex, NC
I wanted 100a for expansion to another building but for now I will be adding a hot tub to the garage panel.
Here are the pictures as promised.