So, we just got a solid 1/2 inch of snow / sleet in TX and as usual, the world is ending.
I get "generator" calls all the time about this and that, hopefully in advance, but this one has me stumped:
I got a call from a buddy running the Ford Lightening (EV). He was testing his EVSE (EV charger) and his Firman generator. It would work in 120V configuration, but as soon as it was switched to the 14-50R, the (Ford) EVSE would go blue, but not charge the truck.
I have the same generator as a manual back up for my shop. First thing I suggested was that the generator might be un-bonded and as EVSE's are sensitive little devices. Turns out the Firman T07573 has a neutral ground bond. So, I believe this should be the "right" configuration for an EVSE plugged in directly.
The generator is probed as 63 Hz, a little fast. But it works on 120V. EVSE does not go into charge mode on 240V. Is there something about the "full cycle" on 120V that might make 240V "more sensitive" to over-frequency?
I assume the wave form on any non-inverter generator is decent, but I haven't put it on a scope.
It's a mystery to me until the EVSE gives up it's detailed error code.
I've had the same issues plugging EVSE's into Ford F-150 Hybrid inverters (7500 watt) - they indicate ground fault.
You sparkies have a theory?
I get "generator" calls all the time about this and that, hopefully in advance, but this one has me stumped:
I got a call from a buddy running the Ford Lightening (EV). He was testing his EVSE (EV charger) and his Firman generator. It would work in 120V configuration, but as soon as it was switched to the 14-50R, the (Ford) EVSE would go blue, but not charge the truck.
I have the same generator as a manual back up for my shop. First thing I suggested was that the generator might be un-bonded and as EVSE's are sensitive little devices. Turns out the Firman T07573 has a neutral ground bond. So, I believe this should be the "right" configuration for an EVSE plugged in directly.
The generator is probed as 63 Hz, a little fast. But it works on 120V. EVSE does not go into charge mode on 240V. Is there something about the "full cycle" on 120V that might make 240V "more sensitive" to over-frequency?
I assume the wave form on any non-inverter generator is decent, but I haven't put it on a scope.
It's a mystery to me until the EVSE gives up it's detailed error code.
I've had the same issues plugging EVSE's into Ford F-150 Hybrid inverters (7500 watt) - they indicate ground fault.
You sparkies have a theory?