Hi everyone,

I just built a 30x40x16 spray foam insulated garage. I installed a 24” Exhaust fan on the far gable end. I noticed the fan did not like to run with the doors closed so I started installing some intake vents. I have 3 10” Round intakes, and I still have to open a door for the fan. I really don’t want to keep punching holes in the side of the garage, but am worried about burning out this fan. Any thoughts?IMG_3213.jpeg
 
Last edited:
To avoid these ads, REGISTER NOW!

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,381
Location
VT
Air in needs to equal air out.

If the air you're pulling in is hot (or cold in the winter) it's not really accomplishing anything
 

ItsNemo

Well-known member
Joined
Mar 5, 2016
Messages
4,805
Location
Canada
3 x 10" holes is around 240 square inches.
1 x 24" hole is around 450 square inches.

You have half as much intake area as you do exhaust....you either need a more powerful fan to **** the air through despite the restriction, or you need more intake.
 
To avoid these ads, REGISTER NOW!

CraigStu

Well-known member
Joined
May 22, 2014
Messages
4,014
Location
Blacksburg, Va
How are you deciding that you need to open a door for the fan? I understand your concern but I am not sure having some restriction on the intake side will automatically cause a fan problem. Think about all the bath exhaust fans in houses that basically have no inlet and that do not burn out.
 