Failed my rough inspection

To avoid these ads, REGISTER NOW!

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,948
Location
Thousand Islands NYS
My experience is the inspector wants nail plates on all pipes and conduit, regardless of depth.
I had an electrical final inspection today (all EMT so no nail plates) but I asked. Rural area, inspection service works in many jurisdictions. NYS (amended 2017 NEC) says 1 1/4", and it applies where I live. Some jurisdictions require nail plates on all holes regardless of depth. Local jurisdictions can be more restrictive than state code but not less.
 

Mandres

Well-known member
Joined
Jun 22, 2006
Messages
1,152
I had an electrical final inspection today (all EMT so no nail plates) but I asked. Rural area, inspection service works in many jurisdictions. NYS (amended 2017 NEC) says 1 1/4", and it applies where I live. Some jurisdictions require nail plates on all holes regardless of depth. Local jurisdictions can be more restrictive than state code but not less.

I use nailer plates over all wiring and plumbing holes regardless. It's just cheap insurance.
 

reader2580

Well-known member
Joined
Dec 31, 2014
Messages
14,516
Location
Minneapolis, MN
You know what the ironic part is? All this sealing creates tight buildings, the air goes stale, and you have to add forced ventilation to maintain air quality.
Air exchangers have been required in Minnesota since 2000. The outgoing air conditions the incoming air. There is always going to be some loss, but I assume it is less than letting the building breath on its own.
 

CraigStu

Well-known member
Joined
May 22, 2014
Messages
4,018
Location
Blacksburg, Va
We don't have a whole house air ventilation system but the heat pump does. The heat pump has propane backup heat so there is a 3" pvc pipe to the inlet side that runs to the outside of the house. I was told this was a code requirement and wasn't needed if we had electric backup heat.
 

dutchgray

Well-known member
Joined
Sep 28, 2014
Messages
6,465
Location
Dorset. England.
We don't have a whole house air ventilation system but the heat pump does. The heat pump has propane backup heat so there is a 3" pvc pipe to the inlet side that runs to the outside of the house. I was told this was a code requirement and wasn't needed if we had electric backup heat.
Is that so the propane burner can always get combustion air.
 

Jeepster04

Well-known member
Joined
Jun 25, 2013
Messages
3,094
When I'm in my crawlspace, I can see light between the block and the seal plate. I've found dead snakes that tried to squeeze in there but became stuck.

Wonder how long the foam would last sandwiched in there? I think I would rather have a good quality caulk in there than foam. Maybe something like a butyl rubber.
 

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,948
Location
Thousand Islands NYS
I see a rodent proof insulating spray foam. No idea if it does any more than basic foam in a can. Also have read of stuffing steel wool in gaps and then caulk. Seems plausible it would stop rodents from chewing through.
 

CraigStu

Well-known member
Joined
May 22, 2014
Messages
4,018
Location
Blacksburg, Va
Is that so the propane burner can always get combustion air.
Could be. The heat pump inside unit is a big aluminum box that I have not had a need to get inside of so I am not exactly sure where the pvc pipe goes. After we moved in I thought it might be a good idea to label all the pipes, hoses etc that feed the heat/AC and the water heater which is about 2ft away. So I followed all of them to determine where they went and remembered that comment from the builder.
 

Firebrick43

Well-known member
Joined
May 12, 2015
Messages
14,010
Location
West central Indiana
Is that so the propane burner can always get combustion air.
Yes, but outside air for two reasons. One is if it pulled from inside the house would depressurize and pull in cold air to replace what was sent up the exhaust flue.

The other is safety. Say you have another appliances like a traditional gas water heater with a NA flue.

If you pulled air from inside, it could try to bring air from outside down the chimney and cause carbon monoxide to be pulled down with it.
 

dutchgray

Well-known member
Joined
Sep 28, 2014
Messages
6,465
Location
Dorset. England.
Yes, but outside air for two reasons. One is if it pulled from inside the house would depressurize and pull in cold air to replace what was sent up the exhaust flue.

The other is safety. Say you have another appliances like a traditional gas water heater with a NA flue.

If you pulled air from inside, it could try to bring air from outside down the chimney and cause carbon monoxide to be pulled down with it.
We have the same reasons and very similar building regulations in the UK, since houses have been made much more air tight actual ventilation has to be calculated and added to all for air changes.

Gas boilers and such all have balanced flues so intake is fresh out side air.
Stoves, solid fuel fires etc have to have an air vent of suitable size in the room.
Only very small appliances which are classified as unvented (dont have flues) don't have to have a specific air supply.

Of course it doesn't stop occupiers doing the same thing they have done for years, tape up those drafty air vents and save on the heating bill.
 

CraigStu

Well-known member
Joined
May 22, 2014
Messages
4,018
Location
Blacksburg, Va
Yes, but outside air for two reasons. One is if it pulled from inside the house would depressurize and pull in cold air to replace what was sent up the exhaust flue.

The other is safety. Say you have another appliances like a traditional gas water heater with a NA flue.

If you pulled air from inside, it could try to bring air from outside down the chimney and cause carbon monoxide to be pulled down with it.
I think this may be the reason since the propane water heater is right next to the heat/ac inside unit. The water heater has a squirrel cage fan for it's exhaust but it has a small inlet on it also.
Water heater exhaust.jpg
 
OP
W

wcp0611

Well-known member
Joined
Nov 25, 2014
Messages
643
Location
Rockvale, TN
Does anyone know if you can sit your HVAC on a drainage easement? The addition we built is about three foot from a drainage easement (think a swell in the yard for water to flow to the street from the back). Mind you this is due to a 10 foot easement on both sides of the bottom of that ditch. I'll have to pour the HVAC slab about three foot into that. I'm thinking this may be a good example of asking forgiveness not permission, but I am curious if an HVAC counts as something installed that is immovable, which is what our codes office said is the no-no on anything put in a drainage easement.
 

jollygreengiant

Well-known member
Joined
Nov 10, 2013
Messages
2,354
Location
Ontario, Canada
Does anyone know if you can sit your HVAC on a drainage easement? The addition we built is about three foot from a drainage easement (think a swell in the yard for water to flow to the street from the back). Mind you this is due to a 10 foot easement on both sides of the bottom of that ditch. I'll have to pour the HVAC slab about three foot into that. I'm thinking this may be a good example of asking forgiveness not permission, but I am curious if an HVAC counts as something installed that is immovable, which is what our codes office said is the no-no on anything put in a drainage easement.

When you say HVAC are you meaning a heat pump or something similar? If so and it's not a huge unit I'd look into mounting it on your external wall instead of on a small slab.
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,089
Location
Northern Virginia
Does anyone know if you can sit your HVAC on a drainage easement? The addition we built is about three foot from a drainage easement (think a swell in the yard for water to flow to the street from the back). Mind you this is due to a 10 foot easement on both sides of the bottom of that ditch. I'll have to pour the HVAC slab about three foot into that. I'm thinking this may be a good example of asking forgiveness not permission, but I am curious if an HVAC counts as something installed that is immovable, which is what our codes office said is the no-no on anything put in a drainage easement.
Rather than a pad on the ground, can you bolt brackets to the house and elevate it off the ground?

We did a townhouse project and the end units of adjacent buildings butted a drainage easement. We bracket mounted the outdoor units in an elevated manner so would not be in the way should earthwork be needed to maintain the drainage. Not sure if what we did was legit or not but 6 years later nothing has come of it even though they had to dig up the drainage pipe for unknown reasons. 🤷‍♂️
 
OP
W

wcp0611

Well-known member
Joined
Nov 25, 2014
Messages
643
Location
Rockvale, TN
When you say HVAC are you meaning a heat pump or something similar? If so and it's not a huge unit I'd look into mounting it on your external wall instead of on a small slab.
Its a honkin' 4 ton. We have a 2.5 very crudely installed to just work for now, but I closed in my garage last year for the kids playroom. It added 483sqft and now the addition which will add another 486 sqft. Those bumped our house up from 1400 sqft to just over 2300 sq ft. The garage has a mini-split I installed but with all of this work and the fact that the new unit had to be bought anyway, I opted to have the HVAC guy (aka, my neighbor giving me a deal) install 10 new needed floor registers in the additions and one inlet in the main house. Also, we had to "settle" for a HEIL unit. 4 and 5 ton Rheems are on an insane backorder.
 
OP
W

wcp0611

Well-known member
Joined
Nov 25, 2014
Messages
643
Location
Rockvale, TN
Rather than a pad on the ground, can you bolt brackets to the house and elevate it off the ground?

We did a townhouse project and the end units of adjacent buildings butted a drainage easement. We bracket mounted the outdoor units in an elevated manner so would not be in the way should earthwork be needed to maintain the drainage. Not sure if what we did was legit or not but 6 years later nothing has come of it even though they had to dig up the drainage pipe for unknown reasons. 🤷‍♂️
I would, but that 4 ton is very large and heavy. I'm going to just do the slab and hope the inspector doesn't look at the plat info again. He really has no reason I wouldn't think given the foundation inspection has already been done.
 

loganb

ALLIANCE MEMBER
Joined
Dec 29, 2011
Messages
5,510
Location
Omaha, NE
I would, but that 4 ton is very large and heavy. I'm going to just do the slab and hope the inspector doesn't look at the plat info again. He really has no reason I wouldn't think given the foundation inspection has already been done.

My Trane 6 ton unit is mounted to the foundation with a metal frame

1694113768140.jpeg


It was replaced 6 or 7 years ago before we bought so not sure if its been on that mount since it was built but it's rock solid and no issues
 
To avoid these ads, REGISTER NOW!
OP
W

wcp0611

Well-known member
Joined
Nov 25, 2014
Messages
643
Location
Rockvale, TN
My Trane 6 ton unit is mounted to the foundation with a metal frame

1694113768140.jpeg


It was replaced 6 or 7 years ago before we bought so not sure if its been on that mount since it was built but it's rock solid and no issues
Mine is a all-in-one heat pump ducted into the crawlspace. If I was to go your route, I don't trust the bracket sitting right below a void in the wall for the ducts.
 

loganb

ALLIANCE MEMBER
Joined
Dec 29, 2011
Messages
5,510
Location
Omaha, NE
Mine is a all-in-one heat pump ducted into the crawlspace. If I was to go your route, I don't trust the bracket sitting right below a void in the wall for the ducts.
Makes sense, getting enough blocking and support in there with wood framing be more challenging
 
OP
W

wcp0611

Well-known member
Joined
Nov 25, 2014
Messages
643
Location
Rockvale, TN
Not sure how to state ownership. Its a little ditch that runs from the back of my property to the front street. The engineers that built my neighborhood put it in, but I guess the easement is mine. It splits my yard in two, but all resides inside my property lines.
 

jkuro

Well-known member
Joined
Apr 28, 2009
Messages
552
If it's yours, you should have no problem with it. You're the only one who would get flooded out if it gets blocked. You could always reroute it away from the new building.
 
OP
W

wcp0611

Well-known member
Joined
Nov 25, 2014
Messages
643
Location
Rockvale, TN
Welp, I chose to go the "ask forgiveness, not permission" route with that HVAC slab. Poured it yesterday. Left the house side open gravel because my HVAC guy said that it would be tight clearance to run the flex under the house if the slab was poured level all the way to the house. I go on vacation Thursday. They are supposed to come do all the work while I'm gone so its a smooth transition.
 
OP
W

wcp0611

Well-known member
Joined
Nov 25, 2014
Messages
643
Location
Rockvale, TN
You know, this is very late to the game, but in looking at pictures my wife (who is fairly ignorant to how homes are built) took of the addition build as a whole, I just realized that the concrete foundation was poured, but there is no rebar installed that ties it to the block wall above. This was all done in two days while I was at work. I sent a text to the concrete GC and he said that because it is not a retainage wall, it doesn't require rebar installed or tying it to the concrete underneath. Does this sound right for a mid-TN foundation?
 

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,948
Location
Thousand Islands NYS
You know, this is very late to the game, but in looking at pictures my wife (who is fairly ignorant to how homes are built) took of the addition build as a whole, I just realized that the concrete foundation was poured, but there is no rebar installed that ties it to the block wall above. This was all done in two days while I was at work. I sent a text to the concrete GC and he said that because it is not a retainage wall, it doesn't require rebar installed or tying it to the concrete underneath. Does this sound right for a mid-TN foundation?
Probably. Unless in seismic zones C, or D2, D2, or D3, very little rebar is actually required by the IRC. A lot of builders will add it - "cheap insurance" - but the experts that write the code say it's not necessary. None in footings and none in shorter walls unless there is unbalanced fill and no dowels connecting footings and stem walls.
 
OP
W

wcp0611

Well-known member
Joined
Nov 25, 2014
Messages
643
Location
Rockvale, TN
Probably. Unless in seismic zones C, or D2, D2, or D3, very little rebar is actually required by the IRC. A lot of builders will add it - "cheap insurance" - but the experts that write the code say it's not necessary. None in footings and none in shorter walls unless there is unbalanced fill and no dowels connecting footings and stem walls.
Well, I guess that's good to know that they didn't eff up that part. Lord knows they had to come back and fix many issues.
 
OP
W

wcp0611

Well-known member
Joined
Nov 25, 2014
Messages
643
Location
Rockvale, TN
I'm not by any means an electrician, but I'm wiring my 400amp panels this weekend. Can someone help me out on my wiring? For the 3/0 copper wire I'm using to run from the meter to each of my 200amp disconnects, I can't source a local mechanical lug to use today so I'm going to buy compression lugs instead. Can someone reading this tell me what compression lug is code compliant in a disconnect? It might be all of them sold but I want to be sure I'm using the right one.
 
OP
W

wcp0611

Well-known member
Joined
Nov 25, 2014
Messages
643
Location
Rockvale, TN
Is a vapor barrier in the crawlspace necessary? My HVAC guy came and ran the ductwork while I was on vacation this weekend unannounced. I'm sure he was trying to be helpful, but my crawlspace floor is so close to the joists that with his ductwork that runs the length of the crawlspace and is amost touching the gravel floor, I can't get around it to install poly. Its about six inches of gravel packed on the floor. Is the poly necessary?
 

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,948
Location
Thousand Islands NYS
Is a vapor barrier in the crawlspace necessary? My HVAC guy came and ran the ductwork while I was on vacation this weekend unannounced. I'm sure he was trying to be helpful, but my crawlspace floor is so close to the joists that with his ductwork that runs the length of the crawlspace and is amost touching the gravel floor, I can't get around it to install poly. Its about six inches of gravel packed on the floor. Is the poly necessary?
I think in TN absolutely.
 
OP
W

wcp0611

Well-known member
Joined
Nov 25, 2014
Messages
643
Location
Rockvale, TN
There is a 1/4 gap between the original subfloor and the additions subflooring due to working around a few wires I couldn't get removed when they stared building the addition. The wires are removed now but I need to seal it up. Its a run of about 1/4" x 27'. Would you use caulk or spray foam insulation?
 
OP
W

wcp0611

Well-known member
Joined
Nov 25, 2014
Messages
643
Location
Rockvale, TN
I white caulked it last night. It was so close to the edge that I just caulked it all the way to the bottom plate of the walls so the inspector can't fail me for not caulking that seam.
 

mrbill55

Well-known member
Joined
Jun 23, 2016
Messages
1,261
Location
Greenville, SC
There is a 1/4 gap between the original subfloor and the additions subflooring due to working around a few wires I couldn't get removed when they stared building the addition. The wires are removed now but I need to seal it up. Its a run of about 1/4" x 27'. Would you use caulk or spray foam insulation?
I would use fireproof foam (orange).

Bill S.
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,660
Location
Austin, TX
Who's easement is it?
Meh. It's there for drainage. I'd put an HVAC on it, as they are not perm structures. That'd be my call.
Where it might get flagged is on a property survey related to future sale. Unlikely the inspector knows about the easement.
 