The inspector came by while I was at work and told my wife it all looked fine except I didn't caulk the sill and he said that anywhere two boards are sistered, it needs to be caulked. Where exactly am I supposed to be caulking the sill? This is one large 18x27 addition we're doing to the end of our house.
 
To avoid these ads, REGISTER NOW!

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,124
Location
Northern Virginia
Here is an example picture of what the inspector is looking for regarding air sealing.

Note how the sill plate has been caulked to the sub-floor, any ganged studs are caulked together, and the double top plates are caulked.

Normal white latex caulk works fine but DOW makes a specific product for this.

This caulking effort helps greatly to seal homes and make them less drafty.

In this picture the window still needs to be foam sealed.

1693420020467.jpeg
 
OP
W

wcp0611

Well-known member
Joined
Nov 25, 2014
Messages
643
Location
Rockvale, TN
Here is an example picture of what the inspector is looking for regarding air sealing.

Note how the sill plate has been caulked to the sub-floor, any ganged studs are caulked together, and the double top plates are caulked.

Normal white latex caulk works fine but DOW makes a specific product for this.

This caulking effort helps greatly to seal homes and make them less drafty.

In this picture the window still needs to be foam sealed.

1693420020467.jpeg
Thanks! That's exactly what I'm looking for.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
31,932
Location
Coronado, CA
The builder did not caulk the sill plates when my house was built (1988) and we had a lot of dust soil the edges of the carpet. Later when the carpet was replaced we had the sill plates caulked.

It also makes a difference in the HVAC
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
That makes no sense at all. 4 trimmers under a 3' window? And solid OSB covering them ostensibly with house wrap over the whole thing? What air leak can you expect there? Building officials need to relax and take a course in reason. @nadogail makes a point about older construction. Wall cavities and intersections at floors, etc., need attention.

4 trimmers and a 5th to the header — give me a friggen break.
 

Old Man Roger

Well-known member
Joined
Apr 6, 2017
Messages
17,471
Location
Palm Coast Florida
That makes no sense at all. 4 trimmers under a 3' window? And solid OSB covering them ostensibly with house wrap over the whole thing? What air leak can you expect there? Building officials need to relax and take a course in reason. @nadogail makes a point about older construction. Wall cavities and intersections at floors, etc., need attention.

4 trimmers and a 5th to the header — give me a friggen break.

I saw that too...I hope it was due to a blocking required callout in the drawing for grab rail or similar roomside mounted element
I’m glad you guys said something, I thought it was waaaay over kill too, but thought I was just not educated enough to say anything.
 

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,956
Location
Thousand Islands NYS
At your electrical boxes in the walls, your inspector may want spray foam applied to the back side of the box where the Romex comes in. Our crews typically use the orange fire foam here. Sorry no picture.
I am planning to use these:
1693441361368.png
Any reason other than expense not to? Everything is sealed with little fuss.
 

loganb

ALLIANCE MEMBER
Joined
Dec 29, 2011
Messages
5,514
Location
Omaha, NE
I’m glad you guys said something, I thought it was waaaay over kill too, but thought I was just not educated enough to say anything.

From a framing perspective for the window only...it's exceptional overkill. 1 cripple under that rough sill would've been standard(and overkill) and just toenailing that rough sill to the jackstud would've been perfectly acceptable to most requirements. 4 cripples, done pretty cleanly, under what appears to be a roughly 36 x 18" window make me assume(possibly falsely) that there is another reason for it...such as interior grab rails, towel bars or something else that benefited from the extra framing being there...because that maybe 30 pound window did not need it!
 

Firebrick43

Well-known member
Joined
May 12, 2015
Messages
14,015
Location
West central Indiana
I saw that too...I hope it was due to a blocking required callout in the drawing for grab rail or similar roomside mounted element
I am trying to figure out all the horizontal blocking in some places and none in others. It will be tight and strong but no place left for actual insulation. The thermal bridging is horrendous
 
To avoid these ads, REGISTER NOW!

69gp

Well-known member
Joined
Jan 1, 2013
Messages
255
Location
MA
I could be wrong but I don't believe that caulking is not part of the rough framing. Fire caulking would be. I am having a rough inspection next week and only have fire caulking done. Once the rough framing is inspected my insulator is going to be coming in and is doing all the caulking when he spray foams. I then will have an insulation inspection where the inspector can check to make sure everything is sealed.
 

loganb

ALLIANCE MEMBER
Joined
Dec 29, 2011
Messages
5,514
Location
Omaha, NE
I am trying to figure out all the horizontal blocking in some places and none in others. It will be tight and strong but no place left for actual insulation. The thermal bridging is horrendous
Scratched my head at all that as well... its 2x6 framing and was done cleanly so I'm assuming it has a purpose as otherwise a lot of labor and material for nothing
 

inphx

Well-known member
Joined
Feb 23, 2012
Messages
1,275
Location
Phoenix/Scottsdale AZ
On my build on slab i recall the lower wood was special green pressure treated and there was a thin foam sheet/gasket between the wood and the slab .. i guess that equates to caulk in my town.
 

Pexto

Well-known member
Joined
May 5, 2018
Messages
638
That makes no sense at all. 4 trimmers under a 3' window? And solid OSB covering them ostensibly with house wrap over the whole thing? What air leak can you expect there? Building officials need to relax and take a course in reason. @nadogail makes a point about older construction. Wall cavities and intersections at floors, etc., need attention.

4 trimmers and a 5th to the header — give me a friggen break.

Those cripples are needed to support the weight of the four top plates.
 

jives

Well-known member
Joined
Jan 4, 2013
Messages
2,804
Location
Central NY
Okay, let's get past the excessive number of cripples, trimmers, and top plates, and get to the caulking. Perhaps I'm not up on the latest, but I've never heard of caulking between sandwiched cripples and trimmers and top plates. Is that caulk placed on the faces and then squeezes out when the boards are nailed together, or just the joint caulked after the fact? Same with the bottom and top plates. . . and if the bottom plate has a foam underlayment is caulking still necessary?
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,124
Location
Northern Virginia
Okay, let's get past the excessive number of cripples, trimmers, and top plates, and get to the caulking. Perhaps I'm not up on the latest, but I've never heard of caulking between sandwiched cripples and trimmers and top plates. Is that caulk placed on the faces and then squeezes out when the boards are nailed together, or just the joint caulked after the fact? Same with the bottom and top plates. . . and if the bottom plate has a foam underlayment is caulking still necessary?
When all rough trades are done, sweep out the unit, then the air seal (caulk) is done.

Rough crowd here. All of the blocking (studs) was for a customer’s wall mounted fold out closet setup post closing. My office couldn’t get a definitive layout so framer went ape **** on blocking.

For those that have never drilled out a house for wiring (from the comments there are a few), when drilling thru ganged studs and another stud is near and in the way, the drill has no choice but to be at an angle relative to the plane of the wall. Thus the first few studs the wire hole was shallow requiring kick plates while the last stud was deep enough and not needed. Drilling started at left and ended at right.

Energy Star and blower door testing drives the need for air sealing. Todays building Codes are requiring “tight” houses as proven by blower door testing at the completion of construction. Finding and fixing leakage paths at the end is a nightmare, so it’s best to be diligent up front and across the board.
 
OP
W

wcp0611

Well-known member
Joined
Nov 25, 2014
Messages
643
Location
Rockvale, TN
That makes no sense at all. 4 trimmers under a 3' window? And solid OSB covering them ostensibly with house wrap over the whole thing? What air leak can you expect there? Building officials need to relax and take a course in reason. @nadogail makes a point about older construction. Wall cavities and intersections at floors, etc., need attention.

4 trimmers and a 5th to the header — give me a friggen break.
I think what you all are forgetting is the possibility that the foundation has crumbled and those are there to keep the subfloor, rim joist, and possible block wall from falling into an endless pit. Genius solution I say!
 

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,286
Location
Illinois near St. Louis, Missouri
My inspector commented "well, you have enough wood..." as I had added a few extra braces and blocking but no where near what is shown. Still had me put a block in one place up in the attic. That's a crazy amount of wood. There had to be a better way to do what was needed.
 

jollygreengiant

Well-known member
Joined
Nov 10, 2013
Messages
2,354
Location
Ontario, Canada
Okay, let's get past the excessive number of cripples, trimmers, and top plates, and get to the caulking. Perhaps I'm not up on the latest, but I've never heard of caulking between sandwiched cripples and trimmers and top plates. Is that caulk placed on the faces and then squeezes out when the boards are nailed together, or just the joint caulked after the fact? Same with the bottom and top plates. . . and if the bottom plate has a foam underlayment is caulking still necessary?

To answer your questions, here the joints are sealed after, and yes caulking is still necessary if using a foam gasket.

As larry4406 mentioned this is all because of stricter air sealing requirements. You get much better air sealing if you do it during construction instead of later.

One interesting thing here is that our building inspectors are rather insistent on using a product called acousti-seal instead of caulking. It seals well since it stays flexible but it's miserable stuff to work with.
 

Old tool guy

Well-known member
Joined
Apr 13, 2023
Messages
3,211
My experience is the inspector wants nail plates on all pipes and conduit, regardless of depth.
 

jives

Well-known member
Joined
Jan 4, 2013
Messages
2,804
Location
Central NY
To answer your questions, here the joints are sealed after, and yes caulking is still necessary if using a foam gasket.

As larry4406 mentioned this is all because of stricter air sealing requirements. You get much better air sealing if you do it during construction instead of later.

One interesting thing here is that our building inspectors are rather insistent on using a product called acousti-seal instead of caulking. It seals well since it stays flexible but it's miserable stuff to work with.
Learn sumpin' new evry'day. Will this code change state to state, or universal in Canada and US?
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,124
Location
Northern Virginia
On any floor that has a roof above, we also caulk seal all ceiling penetrations (recess cans, smoke detector boxes, fan boxes, etc).

We also caulk any hvac returns, transfer grilles, and stack heads on that level with roof above to the drywall to reduce air in leakage (the blower door test will pull air down stud cavities from the attic and into the living space).

Lastly the insulation contractor is supposed to foam seal the drywall penetrations before attic blow from the attic side. Nasty job and I don’t always spot check so we also seal from below before trims are installed; access is easier and I can see it so I know it’s done.
 
Last edited:

67CarGuy

Well-known member
Joined
Feb 6, 2008
Messages
763
Location
Outside Boston, MA
Larry's got it - and with structure (framing), we generally don't question what gets called for /drawn, we just inspect it and call out what still needs to be air sealed (caulk, foam, backer rod and caulk, whatever). You don't have to get too fancy to get a reasonably tight building, but you can't skip the details either.

@billconner make sure those foam gaskets are tight to the drywall. Even then you can still get leakage around them, because if any air can get into the wall cavity (from some other place), it can still find its way out through the box by following the romex into the box. Foam or a putty pad is probably your best bet, but even those can be fussy. I think foaming the back of the box after the wires are all run is the way to go, myself.

@Old tool guy you're right that tighter buildings require forced ventilation, which means greater expense, but you can now control where your "fresh" air comes from, and you can also precondition it with an ERV or HRV. Yes, it's more complicated, and more expensive, but hopefully it creates a better indoor living environment.
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,124
Location
Northern Virginia
You know what the ironic part is? All this sealing creates tight buildings, the air goes stale, and you have to add forced ventilation to maintain air quality.
You are exactly right!

Now our homes have fresh air systems that connect an insulated 6" duct from the furnace cold air return to an exterior wall cap (screen only, no flapper). There is a controller which is programmed to run for X minutes per hour and cycles the air handler regardless of temperature demand and pulls "fresh air" into the home. The fresh air run cycle is based on the volume of the home.

On our homes that also have 400CFM kitchen hood or more, there is also an interlock from the hood pressure switch to activate the same controller which forces an air handler run cycle while the hood is running to draw air in for hood makeup air.
 