I've been wanting to get into welding for a long time, I've been reading the pro's and cons of each type, the best welder yada yada yada, but I never end up with a welder. So I just bit the bullet and ordered a Titanium Stick 225 Welder. For better or for worse, that will be my welder.
The specs are confusing. I'm pretty sure it says it will run at 20a for both 120v and 240v, but then the specs seem to show it can pull 42a? I assume that means I am best off running a 50a circuit for this. right?

My garage has a 125a sub panel in it (And a 200a main is on the other side of the wall, too) and I happen to have a bunch of 6/3 Copper. The 6/3 is very old, it used to connect my garage to my house before I upgraded the electrical, but the majority of the wire was just sitting in a straight run, so its in good shape
First, should I re-use this 6/3 copper? My concern is the ground is much smaller than the other conductors, is this going to be a problem?
My plan was to install a NEMA 14-50R. Good idea? Or should I go with a NEMA 6-50R?
Assuming that small ground wire is an issue, I could go with a NEMA 6-50R and just re-ruse the neutral conductor as the ground. Good idea?
Would love any input
Here are some pictures of the cable



The specs are confusing. I'm pretty sure it says it will run at 20a for both 120v and 240v, but then the specs seem to show it can pull 42a? I assume that means I am best off running a 50a circuit for this. right?

My garage has a 125a sub panel in it (And a 200a main is on the other side of the wall, too) and I happen to have a bunch of 6/3 Copper. The 6/3 is very old, it used to connect my garage to my house before I upgraded the electrical, but the majority of the wire was just sitting in a straight run, so its in good shape
First, should I re-use this 6/3 copper? My concern is the ground is much smaller than the other conductors, is this going to be a problem?
My plan was to install a NEMA 14-50R. Good idea? Or should I go with a NEMA 6-50R?
Assuming that small ground wire is an issue, I could go with a NEMA 6-50R and just re-ruse the neutral conductor as the ground. Good idea?
Would love any input