Fixing broken panel ground

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,349
Location
Alexandria, VA
When the electrician installed a new 200 amp panel he ran a large (1 gauge?) solid copper ground from the panel to the point inside the house where the water line enters the basement. There is also a new ground wire that runs outside to a several ground stakes.

While doing some demolition I accidentally cut the ground wire inside the house bout two feet before it is grounded on the copper water pipe entrance point. What is the best method to fix the break? I remember reading that this wire is supposed to be continuous from the panel to the ground point, but I assume there must be some approved way to splice the wire and fix my mistake.

Thanks,

Bruce
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Just use a split bolt and add a longer end to fix it. The grounding electrode wire to the rods is the one that needs to be continuous.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
The water pipe is a grounding electrode and just like rods, the wire must be continuous. Split bolts do not meet the requirements of 250.64(C)1.

For a diy'er without the proper crimping tools or exothermic molds to be able to splice it legally, the only code compliant method would be to run another wire from the panel to the water pipe.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
The water pipe is a grounding electrode and just like rods, the wire must be continuous. Split bolts do not meet the requirements of 250.64(C)1.

For a diy'er without the proper crimping tools or exothermic molds to be able to splice it legally, the only code compliant method would be to run another wire from the panel to the water pipe.


+1:thumbup:
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,241
Location
Modesto, CA
The split bolt will work in a pinch but not code compliant. However, arguably the water pipe might only be a bond and might not be used as an electrode in the OPs case...
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,241
Location
Modesto, CA
What kind of material is the water pipe made of (in the ground

that is) copper, galv, poly ? It would seem to make a difference

in this case. If it is not metal, then it is not a "ground rod," No ?

Uncle Bob

This is what i was alluding to but didnt expound on it. Thx

And a metal water pipe wouldnt be called a ground rod but instead a grounding electrode if it was being used as one...
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
The water pipe is a grounding electrode and just like rods, the wire must be continuous. Split bolts do not meet the requirements of 250.64(C)1.

The split bolt will work in a pinch but not code compliant. However, arguably the water pipe might only be a bond and might not be used as an electrode in the OPs case...

Since the OP said he had a ground wire going to several ground rods I was assuming the ground wire to the plumbing was just a grounding bond.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
This is what i was alluding to but didnt expound on it. Thx

And a metal water pipe wouldnt be called a ground rod but instead a grounding electrode if it was being used as one...[/QUOTE

If metal underground water pipe exists it must be used as a grounding electrode.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Now that everyone has made clear that a buried metal water supply pipe is to be used as a grounding electrode, I'll add that it also has to have at least 10 ft of direct contact with the earth. So if that's your case then the electrode conductor connected to the pipe needs to be continuous. Around here I see a lot of plastic pipe being used on the supply side.
 

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
OP if you're doing other electrical work, you may be forced to update that ground to water line to most current code for your city. My local city code requires water line being grounded within 6 ft of entering the house ; when I upgrade my main panel I'll need to upgrade to that local code.

Call your AHJ / inspector's office and get the low down on grounding water lines in your city.

Fix it somehow now, but overall you may actually need a much longer continuous run to ground water pipe within 6 ft of entering the house to meet current code.
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
Normally it will be a continuous wire from the panel to street side of water service past the water meter if it inside the house,I also install a ground clamp on house side of the copper water service to bond it also.
That way if meter is removed youre still protected.;)
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
OP if you're doing other electrical work, you may be forced to update that ground to water line to most current code for your city. My local city code requires water line being grounded within 6 ft of entering the house ; when I upgrade my main panel I'll need to upgrade to that local code.

Call your AHJ / inspector's office and get the low down on grounding water lines in your city.

Fix it somehow now, but overall you may actually need a much longer continuous run to ground water pipe within 6 ft of entering the house to meet current code.

I took this to mean the panel was recently replaced by a competent electrician with the grounding updated, I see no reason to involve the AHJ in a simple ground wire replacement:

When the electrician installed a new 200 amp panel he ran a large (1 gauge?) solid copper ground from the panel to the point inside the house where the water line enters the basement. There is also a new ground wire that runs outside to a several ground stakes.
 

C96

Well-known member
Joined
Nov 30, 2013
Messages
1,251
Just curious, did the electrician run a bond to the gas piping system?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,241
Location
Modesto, CA
Just curious, did the electrician run a bond to the gas piping system?

Its crazy how so many newer houses dont even have this done. This must have been required decades ago and yet i see house from the 60's 70's 80's and 90's missing this. Of course, gas 3-prong appliances such as furnaces, dryers and cooktops provide a grounding path for the gas line!
 

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
I took this to mean the panel was recently replaced by a competent electrician with the grounding updated, I see no reason to involve the AHJ in a simple ground wire replacement:

Oh **** . . . you're right !! Duh, I must have been fixated on the next paragraph where OP said he demo'd some stuff and broke the ground.

My bad.

+1 to just Re-Run continuous ground to water line that electrician had installed.

SIDE NOTE: Previous house built new in '88 did not have any ground to NG black pipe steel (now the ex-wife owns). Now, my '55 built house has no ground for NG black pipe steel. Looks like more upgrades needed !! ;)
 