To supply power to my shop, I want to install a disconnect panel at my house meter base and then run cable from the disconnect panel to a load center inside the garage. Do I need to run the grounds as if I am coming off the house main load center or run the grounds as if coming straight from the meter base.

If I run the ground as if I am coming off the house main load center, do I have to have ground rods at the shop connected to the shop load center as well as the ground coming from the meter base via the quick disconnect.

Any help will be appreciated!

Mark
 
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
The disconnect at the house becomes the Main and thus you have to run four wires to the shop panel. Your meter may or may not have double taps to allow you to do this. Many 200 amp meter sockets or cans only have one set of taps.

Charles
 
OP
M

mkbrower

Active member
Joined
Aug 11, 2010
Messages
44
Location
Foot Hills of North Carolina
This is how my old outbuilding is run. Four wires from the meter to a fused disconnect and 4 wires to my out building to a small load center. All this was done a very long time ago with the meter supplying the ground to the out building via the disconnect. I guess what I am asking is "can I run the wires the same as my outbuilding or do I need ground rods at my new shop?" This set-up has been run this way for the last 40 years without any problems but I know the codes have probably changed since then.

Mark
 
To avoid these ads, REGISTER NOW!

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
you need 4 wires to the subpanel, and you need ground rods at the detached structure.
 
OP
M

mkbrower

Active member
Joined
Aug 11, 2010
Messages
44
Location
Foot Hills of North Carolina
Thanks MrB. Thats good to know cause I went ahead and put in the ground rods this afternoon. My gut told me I was going to need them, I just knew they were going to be alot of work putting them in and I wanted to be sure.
Thanks again!