Hi All,
Been caught up in these winter storms and I got the interrupter kit installed to my panel to be able to put power in my home from my 6500 watt generator. A little background on my home, most of it runs on gas, dryer, oven, range, water heater, furnace. 2300 sq foot home, and the Portland weather is generally pretty mild so my furnace isn't all that beefy. A Trane XL80 with a 1/3 hp motor on the blower running on a 20 amp circuit. Runs fine with the power on.
While on the generator though, it would do something funny. The thermostat would call for heat and it would start up and heat the house, the first time. Then once it hit temp it would shut off.
The second time the thermostat called for temp, I would see the ignitor fire up, but then it would power down and get an ignitor error (9 flashes) on the furnace. When I would pull apart the panel and toggle the gas switch on and off (no idea if this actually did anything) and put it all back together, it would fire fine again.
Now the power is back on, and the furnace is working 100% fine, so clearly there is no ignitor issue.
But I want to set up the generator for a more permanent solution, and want to resolve this. The generator is of the ground-neutral bonded type. 6500 startup watts. Grounded with a post into the ground, wired from the 25 amp 240v plug to a 25 amp 2 post breaker in the panel. Ground and neutral are also bonded at the panel. I've read 100 posts about grounding, dirty power, sine waves - just wanted to see if anyone had come up with a concrete solution.
Best.
Been caught up in these winter storms and I got the interrupter kit installed to my panel to be able to put power in my home from my 6500 watt generator. A little background on my home, most of it runs on gas, dryer, oven, range, water heater, furnace. 2300 sq foot home, and the Portland weather is generally pretty mild so my furnace isn't all that beefy. A Trane XL80 with a 1/3 hp motor on the blower running on a 20 amp circuit. Runs fine with the power on.
While on the generator though, it would do something funny. The thermostat would call for heat and it would start up and heat the house, the first time. Then once it hit temp it would shut off.
The second time the thermostat called for temp, I would see the ignitor fire up, but then it would power down and get an ignitor error (9 flashes) on the furnace. When I would pull apart the panel and toggle the gas switch on and off (no idea if this actually did anything) and put it all back together, it would fire fine again.
Now the power is back on, and the furnace is working 100% fine, so clearly there is no ignitor issue.
But I want to set up the generator for a more permanent solution, and want to resolve this. The generator is of the ground-neutral bonded type. 6500 startup watts. Grounded with a post into the ground, wired from the 25 amp 240v plug to a 25 amp 2 post breaker in the panel. Ground and neutral are also bonded at the panel. I've read 100 posts about grounding, dirty power, sine waves - just wanted to see if anyone had come up with a concrete solution.
Best.