Hi All,

Been caught up in these winter storms and I got the interrupter kit installed to my panel to be able to put power in my home from my 6500 watt generator. A little background on my home, most of it runs on gas, dryer, oven, range, water heater, furnace. 2300 sq foot home, and the Portland weather is generally pretty mild so my furnace isn't all that beefy. A Trane XL80 with a 1/3 hp motor on the blower running on a 20 amp circuit. Runs fine with the power on.

While on the generator though, it would do something funny. The thermostat would call for heat and it would start up and heat the house, the first time. Then once it hit temp it would shut off.

The second time the thermostat called for temp, I would see the ignitor fire up, but then it would power down and get an ignitor error (9 flashes) on the furnace. When I would pull apart the panel and toggle the gas switch on and off (no idea if this actually did anything) and put it all back together, it would fire fine again.

Now the power is back on, and the furnace is working 100% fine, so clearly there is no ignitor issue.

But I want to set up the generator for a more permanent solution, and want to resolve this. The generator is of the ground-neutral bonded type. 6500 startup watts. Grounded with a post into the ground, wired from the 25 amp 240v plug to a 25 amp 2 post breaker in the panel. Ground and neutral are also bonded at the panel. I've read 100 posts about grounding, dirty power, sine waves - just wanted to see if anyone had come up with a concrete solution.

Best.
 
Last edited:
To avoid these ads, REGISTER NOW!

NETexas

Well-known member
Joined
Aug 20, 2015
Messages
96
Location
Attached
Do you have a Nest thermostat? I could run mine fine on a generator until I got a Nest.


Sent from my iPad using Garage Journal
 

Hot shot

Well-known member
Joined
Jul 10, 2019
Messages
420
Location
Virginia
Don’t know if this pertains to your situation but I have a gas kitchen range. I’ve been running generator for going on 6 days due to ice storm. The oven part will not heat. What I think is going on is the igniter is not reaching the proper temperature to allow the gas valve to open. It’s getting hot, I looked under the bottom tray and seen it glowing but maybe not quite hot enough. I wish it had a pilot light like they used to make them
 
Last edited:

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,591
Location
Long Island
Don’t know if this pertains to your situation but I have a gas kitchen range. I’ve been running generator for going on 6 days due to ice storm. The oven part will not heat. What I think is going on is the igniter is not reaching the proper temperature to allow the gas valve to open. It’s getting hot, I looked under the bottom tray and seen it glowing but maybe not quite hot enough. I wish it had a pilot light like they used to make them

It's the same issue. The fail-safe nature of the gas valve hot-surface-igniter system depends on clean electricity. A circuit monitors the current flowing through the HSI, and shuts the valve if it isn't good enough. The harmonic distortion from generator power may be enough to prevent it from thinking that the igniter is working properly.
 
OP
K

Kyngfish

Member
Joined
Jan 29, 2017
Messages
19
People use generators to power their houses right? is there a solve for this other than buying a totally other generator? Can I clean up the signal somehow? Also, odd that it works on the first ignition EVERY time, but not the second, then fine after a reset. Is there something about the overall heat of the ignitor? I'm stumped.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
I just had the pretty much the same thing happen the other day. I was doing a service change and brought a small harbor freight inverter 2000 watt honda clone generator to keep his gas furnace going. The furnace tried to come one, but stopped. I was getting 8 or 9 blinks. It was saying the hot and neutral was switched. I switched them, but nothing changed. Homeowner was worried the generator ruined the board, but once I restored power, all was good. It could be a bonding issue inside the generator
 
OP
K

Kyngfish

Member
Joined
Jan 29, 2017
Messages
19
Do you have a Nest thermostat? I could run mine fine on a generator until I got a Nest.


Sent from my iPad using Garage Journal

I have an ecobee. I had a nest thermostat that I'm convinced was effing with my AC function somehow and I've never had issues with the ecobee so far, but who knows.
 
OP
K

Kyngfish

Member
Joined
Jan 29, 2017
Messages
19
I just had the pretty much the same thing happen the other day. I was doing a service change and brought a small harbor freight inverter 2000 watt honda clone generator to keep his gas furnace going. The furnace tried to come one, but stopped. I was getting 8 or 9 blinks. It was saying the hot and neutral was switched. I switched them, but nothing changed. Homeowner was worried the generator ruined the board, but once I restored power, all was good. It could be a bonding issue inside the generator

Generator is showing good as far as grounding, it IS bonded sort of twice, once at the panel and once at the generator, I suppose since the generator is really for panel use I can unbond it and then modify a cut up extension cord to bond in a pinch, but I don't know how that would be causing an issue.

Wondering if anyone has found any solutions tho.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Generator is showing good as far as grounding, it IS bonded sort of twice, once at the panel and once at the generator, I suppose since the generator is really for panel use I can unbond it and then modify a cut up extension cord to bond in a pinch, but I don't know how that would be causing an issue.

Wondering if anyone has found any solutions tho.

Just came across this. This could have been my problem. I had no reference to ground. The wiring to the furnace was just 2-wire romex

https://everythingwhat.com/do-you-h...out any connection to earth,earth from the AC
 
Last edited:

510ebl

Well-known member
Joined
Jan 20, 2015
Messages
518
Location
Southern New Jersey
Have you checked voltage and frequency at the furnace? While trying to ignite the second time?

I wouldn’t rule out THD. My water heater wouldn’t run on my conventional generator either. Runs fine on the new invertor type.
 

Hot shot

Well-known member
Joined
Jul 10, 2019
Messages
420
Location
Virginia
It's the same issue. The fail-safe nature of the gas valve hot-surface-igniter system depends on clean electricity. A circuit monitors the current flowing through the HSI, and shuts the valve if it isn't good enough. The harmonic distortion from generator power may be enough to prevent it from thinking that the igniter is working properly.

What is the hsi
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Generator is showing good as far as grounding, it IS bonded sort of twice, once at the panel and once at the generator, I suppose since the generator is really for panel use I can unbond it and then modify a cut up extension cord to bond in a pinch, but I don't know how that would be causing an issue.

Wondering if anyone has found any solutions tho.

this is dangerous. you do NOT want the neutral bonded in more than one place. it will cause neutral current to flow on the EGC.

When a portable generator is used to power a house, the neutral bond needs to be removed.

if you want a quick way to restore the bonding for standalone use, making a bonding plug, where you connect neutral and ground together with a jumper wire, and plug it into one of the generator receptacles.

My generator is not grounded to anything in the ground

Wonder if that would help

you mean like a grounding electrode?

wont do anything at all here. remember, grounding electrodes are for shunting lightning to earth, limiting voltage potential to earth and for shunting high voltage electricity when primary lines contact secondary lines.

BTW your generator SHOULD have a connection to earth via the EGC that connects to the main service panel and thus the GEC that goes to the rods at your panel....
 
OP
K

Kyngfish

Member
Joined
Jan 29, 2017
Messages
19
back to the question at hand - does anyone know if a voltage regulator would fix the frequency issue?
 

AP514

Well-known member
Joined
Jan 23, 2014
Messages
768
Location
Pearland, Tx
back to the question at hand - does anyone know if a voltage regulator would fix the frequency issue?

Are you talking THD or Hrz ?
Engine Speed can change your Hrz.
AVR for the Voltage...and a lot of them can not be adjusted (mine included)
 
To avoid these ads, REGISTER NOW!
OP
K

Kyngfish

Member
Joined
Jan 29, 2017
Messages
19
nope. A VR regulates the voltage and is not the circuitry needed for frequency correction

Got it, will ANYTHING compensate for the engine speed? Would going up to a larger generator help it hold steadier? Say up to 7500 watts from 5500 watts?
 
OP
K

Kyngfish

Member
Joined
Jan 29, 2017
Messages
19
also, why does it light up the ignitor the first time and never the subsequent times?
 

sms1974

Well-known member
Joined
Jul 9, 2014
Messages
210
Location
Grafton Ohio
also, why does it light up the ignitor the first time and never the subsequent times?

your problem is possibly / probably two fold...

Yes there some correlation with the generator supplying "clean" power its actually called a sine wave. we've seen this problem several times. The new equipment on the market has very sensitive electronics. this also goes along with the people that have experienced problems with the Nest thermostats.

The second part of your issue has to do with the way your furnace works. your model furnace has an "80 volt" igniter. the way these worked the first time the furnace had a call for heat it would light the igniter with a full 80 volts, on each cycle after it would drop the voltage by a percentage. after it had a failed ignition it would bump voltage back up and set that as the igniter voltage. The idea was to extend the life of the igniter by using the lowest voltage necessary. it was one of those ideas that worked great on paper but was somewhat problematic in real life.

I suspect the problem your having with it working on the first cycle but not on subsequent cycles is related to the ignitor voltage variance combined by a generator voltage or hertz rate variance...

some electronics just don't like generators...
 

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
I am surprised no one have come out with a inverter plugin for these generators... not inverter generators, just a converter that change it to AC --> DC --> clean AC.
 

slow

Well-known member
Joined
Feb 26, 2006
Messages
2,596
Location
near Orlando
I am surprised no one have come out with a inverter plugin for these generators... not inverter generators, just a converter that change it to AC --> DC --> clean AC.

I have something similar I built for mine. an APS-55 55 amp 13.8v regulated power supply that charges a deep cycle optima battery and connected to the output of that is an Xantrex 1000 watt pure sine inverter with GFCI plug. I use it for 2 purposes, 1 to run the fridge when the generator is not running and second (if needed) it would clean the power for sensitive items. In my case I lose a lot to the conversion, one could keep it all high voltage and possibly lose less in the conversion the way a VFD would work.
 

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
Xantrex are good stuff... usually solar power stuff...

but they don't take generator output power or alternator output power. 5000Watt would have cost an arm an a leg... well over $2000 maybe not the first born... I did look into those when I was interested in solar power and independent grid stuff..

what I was saying was ... we know inverter generator operated this same way... dirty AC --> DC --> Clean AC... I am surprised no one have a kit to build a plugin converter on the generator to put out clean AC. Hint hint wink wink, don't forget the dogs that give you this idea if you are marketing for one lol...
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,660
Location
Austin, TX
Some experience with this. I suspect the same thing as Finn and Rittman. These basic generators often provide a "grid like" signal. When you look at it under a oscilloscope, it the power curve is a set of squares - usually called "modified sine". It's not as smooth, and certain equipment won't accept these signals.

If you've ever tried daisy-chaining UPS (Battery power supplies) - they often won't work together for the same reason.

It *could* be a generator running off frequency (too fast or too slow RPM) - but I haven't seen that happen as much. Most volt meters can check frequency, so this is pretty easy to catch.

IF you have a buddy with a "inverter generator" - give it a try and see if it solves this problem.

Pure-vs-Modified-Sine-Wave.png
 

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,874
Location
oregon
It was asked above, what is the voltage output? This last outage I found that my generator was putting out ~100 vac. It ran most stuff but some items refused. I have a new regulator on order.

lg
no neat sig line
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,660
Location
Austin, TX
Agree. Measure both line voltage and frequency. IF those are close, you've likely got something fancy that doesn't like the modified sine wave.
 

Fasthotrod

Well-known member
Joined
Dec 14, 2015
Messages
218
Location
Oklahoma
back to the question at hand - does anyone know if a voltage regulator would fix the frequency issue?

No, it would not.

There are two different things in play here. They are related, but independent of each other.

The voltage regulator looks at the output voltage of the alternator and makes adjustments to the field current, increasing or decreasing the magnetic energy in the rotor to adjust the voltage.

The engine governor controls the engine speed (RPM) and speed is directly proportional to frequency output. (Hertz, or Hz for short.) The speed at which the engine should run is dependent on the type of alternator used, specifically the number of poles inside the alternator:

F = NP/120

F = Frequency
N = Speed of Rotation
P = Number of poles
120 = Converting Minutes to Seconds. (60 seconds in a minute)

So a 3,600 RPM generator with 2-poles:

F = (2 * 3,600)/120

F = 7,200/120

F = 60Hz

A 4-pole 60 HZ generator would run at 1,800 RPM.

Any time you place a load on an alternator, you get a dip in frequency as well as a dip in voltage. Here's what happens:

The engine governor will see the change in speed and increase fuel to compensate for the drop in speed... much like your car's cruise control when you head up a hill. The engine accelerates towards 60 Hz and will likely pass it, then will reduce the throttle to drop back to rated speed. If you were looking at the waveform, you would see frequency droop, then a slight overshoot, then settle back down to rated frequency.

The voltage regulator will see the drop in voltage and increase field current to bring the voltage back up to nominal. The voltage regulator is typically much faster than any changes with the engine speed, as it's electronic vs. mechanical.

On cheaper units, these devices to not 'talk' to each other. They work independently. On some of the higher priced units (typically not portable units) the voltage regulator has a, "Volts per Hz" function that will see both the voltage and frequency, and when it sees the drop in frequency it can 'dial back' the field current, reducing the effective load on the alternator/engine and allowing it to recover speed. As speed/Hz increases, the voltage regulator will increase current to the field to bring the voltage back into tolerance.

One thing that I try and remind people of is that a portable generator has a specific task in mind... providing power and maintaining portability. This means that the engineers that design it have to make compromises... often times it's quality of output vs. overall weight. One way to have better regulation of speed is to simply have a big, heavy flywheel. The rotational mass of the flywheel will retain rotational energy during a transient event, but the engine will need to work harder to get it up to speed, and push more power if/when the load is high enough to pull the frequency out of tolerance.

Another way is to have a larger engine with more rotational mass, or one that has a more consistent power application like a Diesel vs. Otto (gas/propane) system. More info here: https://vivadifferences.com/difference-between-diesel-cycle-and-otto-cycle/

A lot of modern electronics are sensitive to changes in both frequency and voltage. Most home appliances are designed with a rock solid commercial power input in mind... so if you have a newer home, you will likely want to invest in a generator that is designed to put out clean power to your home.

Hope this helps.

Mark
 

Noltz

Well-known member
Joined
Mar 10, 2020
Messages
377
Location
Ontario, Canada
I am surprised no one have come out with a inverter plugin for these generators... not inverter generators, just a converter that change it to AC --> DC --> clean AC.

They do. Probably OP's easiest solution is a sufficiently sized UPS for his furnace. They're a few hundred bucks but provides PC-safe power, brown-out protection and a few minutes at least of black-out protection. I'm not certain about codes though.

That is why I have my generator set to 61.5 Hrz with No-Load (3690RPM)

Mine is just about 60 as well, 62 I think unloaded, 61 with a 3k load. Buddy bought an identical genny and it too reads 62 on the panel.
 

Jeepster04

Well-known member
Joined
Jun 25, 2013
Messages
3,094
I had the exact same issue with my trane xl-80, sortve...

Power went out for 4 days and I ran it off a friends 7500 watt conventional crazy loud generator, no issues what so ever.

Power went off again and I tried to run it off my honda inverter generator, it never even tried to light and gave me the 9 flash error of bad igniter. I figured I screwed something up and just waited for the power to come back on. All is well now.

I found it strange a crappy loud conventional generator would run it but my honda inverter generator wouldn't. Ive not checked the HZ on the honda but I ran my tv and DVR today while the power was out again...
 

slow

Well-known member
Joined
Feb 26, 2006
Messages
2,596
Location
near Orlando
I had the exact same issue with my trane xl-80, sortve...

Power went out for 4 days and I ran it off a friends 7500 watt conventional crazy loud generator, no issues what so ever.

Power went off again and I tried to run it off my honda inverter generator, it never even tried to light and gave me the 9 flash error of bad igniter. I figured I screwed something up and just waited for the power to come back on. All is well now.

I found it strange a crappy loud conventional generator would run it but my honda inverter generator wouldn't. Ive not checked the HZ on the honda but I ran my tv and DVR today while the power was out again...

My Honda EU2000 puts out 60 volts on the hot and 60 volts on the neutral measuring between hot/neutral and ground. If you make a bonding plug to bond the ground to neutral, it makes 120 volts on the hot when measured from hot to ground. This could be part of the issue your seeing.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
My Honda EU2000 puts out 60 volts on the hot and 60 volts on the neutral measuring between hot/neutral and ground. If you make a bonding plug to bond the ground to neutral, it makes 120 volts on the hot when measured from hot to ground. This could be part of the issue your seeing.

something wrong with your generator then

the bonding of neutral has nothing to do with the voltage the alternator head generates.
 

jlv03

Well-known member
Joined
Jan 19, 2020
Messages
344
Location
SE IA

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,257
Location
Coastal NJ
something wrong with your generator then

the bonding of neutral has nothing to do with the voltage the alternator head generates.

Are you sure there is something wrong with the generator? If his generator is NOT bonded, then neutral is floating.

So when the measures from Hot to Ground he gets 60V.
Neutral to Ground also 60V.

If he bonds Neutral to ground - 120V from hot to neutral. And I suspect zero from neutral to ground.
 

slow

Well-known member
Joined
Feb 26, 2006
Messages
2,596
Location
near Orlando
from my research all Honda 120 inverter generators operate like this with a floating neutral. (except the 240 volt eu6000-eu7000 models) generating 60 volts with a 120 volt differential between the hot and neutral.
 