Has anyone converted a 65k natural gas heater to propane.I read the instructions but is there any tuning involved with the gas valve.It`s a carrier comform 90 heater.Suppose to be a high effiency heater because the exhaust vent is pcv.

Tony
 
To avoid these ads, REGISTER NOW!

Mike007

Well-known member
Joined
Dec 4, 2010
Messages
2,593
Without seeing it or the instructions, I'm going to say yes. Typically the spring in the regulator gets replaced and the pressure set to what the instructions indicate. 11" H20 most likely.
 

BTI

Well-known member
Joined
Feb 4, 2010
Messages
82
Location
SE Ohio
I coverted mine for my house...it was an easy job.
If the kit is available, you should be fine.

BTI
 

TheNerd

Well-known member
Joined
Mar 15, 2009
Messages
144
Location
The Mitten State
You will need to replace the orifice in the gas valve. The Natural gas furnace uses a larger orifice than the Propane furnace.

Also, natural gas is usually set at 3 to 3.5 in. W.C. Where as Propane is set at 10.5 to 11 in. W.C. You will need a manometer to adjust the Water column pressure. This is bassically the pressure at wich the gas enters the gas valve..

The orifice is a little brass threaded thing with a small hole in it that the gas passes through as it enters in through the gas valve.

Any HVAC guy should be able to tell ya if the parts are still available. I no longer work in that field. Let us know what you find out.
 
To avoid these ads, REGISTER NOW!

ambenz

Well-known member
Joined
Dec 12, 2010
Messages
4,236
Location
NW Chicago Suburbs
I agree with "The Nerd".
I worked making converorized pizza ovens for Blodgett and we made them for natural and propane.
If I remember right, the kit includes different springs for the regulator and a correct size orafice.
Good info right there!!!
 

fishheds

Well-known member
Joined
Apr 30, 2010
Messages
164
Location
Outer Banks,NC
Frequently,when converting simply inverting the cap will adjust spring pressure.LP has a "bump" to raise the tension while the natural side is sorta countersunk to lower to the 3.5-7 in.range.Read the directions and it's pretty simple and straightforward.
Also,if it's going in the garage,check code on minimum floor clearance,usually 18 inches.The reason being,flammable vapors usually(natural gas excepted) have a specific gravity higher than 1 and getting the appliance off the floor reduces the likelihhod of a fire/explosion from gasoline vapor pooling along the floor.This is the reason gas water heaters in the garage are always sitting on platforms.You also want to be careful while using volatile chemicals for the same reason.
I'm not familiar with the unit you're looking into,but if it's just a garage heater,I'd recommend vent free.99.9% efficient,versus whatever the Carrier is rated.
 
OP
9

91.5mm

New member
Joined
Oct 3, 2010
Messages
3
Thanks for all the replys.It going in to garage with 12 ft ceilings.The heater will be about 8-9 ft in the air.They said this heater is very efficient.It has a condensation hose and plastic pcv exhaust.Just need it to take the chill out of the shop.
Tony
 

rickairmedic

Well-known member
Joined
May 31, 2005
Messages
4,165
Location
louisville ,Ky
Tony if you put that heater in the garage. ( Make sure you keep the garage above freezing at all times in the winter ). Condensing gas furnaces can freeze and crack the secondary heat exchanger . This is why you cannot put them in an unconditioned airspace such as an attic or crawlspace.