Generally not a bad install, but could use some cleanup before you add your garage circuits.
#1, you have a huge bundle of 14/2 and 12/2 romex going through a single cable clamp. That's a code violation because most cable clamps are rated for a max of 2 (TWO) cables. That means you need to get a bag of 1/2" clamps and seperating the cables. You could use the bug one possibly for the large cable (electric heat?) that is missing a cable clamp entirely.
#1 Although not required, generally it's good practice to place your higher current (often double pole breakers) closer to your main breaker. This would mean moving a couple of your 120V breakers higher up, and making some open spaces down below for your air compressor, welder, etc.
Where did you buy your breakers from, an electrical distributor? The big box stores would have charged you under $150 for that breaker assortment! The box cost with main breaker isn't too bad of a deal though.
#1, you have a huge bundle of 14/2 and 12/2 romex going through a single cable clamp. That's a code violation because most cable clamps are rated for a max of 2 (TWO) cables. That means you need to get a bag of 1/2" clamps and seperating the cables. You could use the bug one possibly for the large cable (electric heat?) that is missing a cable clamp entirely.
#1 Although not required, generally it's good practice to place your higher current (often double pole breakers) closer to your main breaker. This would mean moving a couple of your 120V breakers higher up, and making some open spaces down below for your air compressor, welder, etc.
Where did you buy your breakers from, an electrical distributor? The big box stores would have charged you under $150 for that breaker assortment! The box cost with main breaker isn't too bad of a deal though.