I have a Generac generator (5500 watts) 6875 peak or something. Is there a plug adapter available to use for a 230v/30a welder ??? The 240/30 amp receptacle on the generator has 4 locking prongs? Thanks.
 
Last edited:
To avoid these ads, REGISTER NOW!
OP
D

DonnyT

Well-known member
Joined
Dec 15, 2012
Messages
236
Location
Upstate
Awesome, thank you very much!! I think I need to go from L14-30 to 6-50 for the Hobart 190?? Thanks again!! I think the generator can handle it?
 
OP
D

DonnyT

Well-known member
Joined
Dec 15, 2012
Messages
236
Location
Upstate
I know!!! Now I'm not sure my Generac will be able to handle the Hobart 190 though ???
 
OP
D

DonnyT

Well-known member
Joined
Dec 15, 2012
Messages
236
Location
Upstate
Thank you very much Ish. The guys over at Hobart stated I need a 6500 to 7500 generator to achieve full power?? I Probably wouldnt ever be at full power anyway ?
 
To avoid these ads, REGISTER NOW!

Zrexxer

Well-known member
Joined
Jan 23, 2007
Messages
5,058
Location
Pflugerville, TX
Takes about 15 minutes to make. I've got several I've made to adapt all kinds of plug/outlet combinations.

Cord.jpg
 
OP
D

DonnyT

Well-known member
Joined
Dec 15, 2012
Messages
236
Location
Upstate
Very nice. Thanks. Hobart states at full power (190 amps) the welder is at 5.8kw's. Hmmmm. My generator is 5.5 kw's. :dunno:
 

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
Very nice. Thanks. Hobart states at full power (190 amps) the welder is at 5.8kw's. Hmmmm. My generator is 5.5 kw's. :dunno:

Yes, but the rated output is 3.8kw. The duty cycle at 190a will be much smaller than the 30% it's rated for - ie, you'll probably only see 15% duty cycle. If you really are welding 190a with this on a regular basis, this is where the "peak power" of the generator comes in to play - it can handle that load for a similar smaller duty cycle just as the welder can.

The 190 gives 190 amps at ~19 volts...that gets you 3.8kw. A welder is only so efficient... but 5.8kw vs 3.8kw would get you a 65% efficiency where I think it's much closer to 75%. Again, these are just peak ratings.
 

Tre900

Well-known member
Joined
Dec 18, 2012
Messages
131
Location
Wooster
Most Generators suggest not have anything plugged into your Generator when your starting it. at the very least make sure your welder is powered off if you have it connected when restarting your generator.
 
OP
D

DonnyT

Well-known member
Joined
Dec 15, 2012
Messages
236
Location
Upstate
Thanks again everyone. Ish, thanks for clearing that up. I feel better now, lol.
 