Generator connection to home

zendriver

Well-known member
Joined
Dec 10, 2014
Messages
29,839
Location
Indiana
I have a 3500 working watt gen 120/240V, for emergency use.

Right now, even to keep the fridge going, I'd have to raise the stabilizer legs and roll it away from the wall just to plug in.

I'll have my electrician wire stuff in, but could I start with something like this, put in a cross-over switch and then just switch circuits on/off using the existing 200A circuit breaker?


I Oil furnace, well pump , water heater, central A/C (probably just use 1 windows a/c unit or portable heaters) Mainly want refrigeration and water.

Better ideas? Thanks.
 
To avoid these ads, REGISTER NOW!

Firebrick43

Well-known member
Joined
May 12, 2015
Messages
14,024
Location
West central Indiana
I have a 3500 working watt gen 120/240V, for emergency use.

Right now, even to keep the fridge going, I'd have to raise the stabilizer legs and roll it away from the wall just to plug in.

I'll have my electrician wire stuff in, but could I start with something like this, put in a cross-over switch and then just switch circuits on/off using the existing 200A circuit breaker?


I Oil furnace, well pump , water heater, central A/C (probably just use 1 windows a/c unit or portable heaters) Mainly want refrigeration and water.

Better ideas? Thanks.
Is your well 120v? That is all the cord is good for. And if you did use a 120v cord you would only have half the breakers on the panel function.

There is a lot more to it.
 

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,969
Location
Peace Valley,mo
This is my generator panel have a outdoor generator plug uses a 6' premade cord to a 7k gen converted to lp. Being rural lp doesn't go bad and since having a 500 gallon tank been without power for 9 days and comfortable. Lp stove for heat, cook stove. Gen, some lights, refrigerator, tv, internet water heater, well pump, microwave, 5k btu window unit ( keep in closest) for summer. Not all at the same time.
IMG_20220902_191934.jpg
 

Firebrick43

Well-known member
Joined
May 12, 2015
Messages
14,024
Location
West central Indiana
It's basically all I do. Dump the main and then back-feed a 240v welder outlet in my garage. Maybe against code, but I think there are exceptions during emergency times.
No there isn't

You are putting lineman's lives at risk. Why would you do that? Would you be upset if someone killed your spouse, kids, or parent because of pure laziness?
 
OP
Z

zendriver

Well-known member
Joined
Dec 10, 2014
Messages
29,839
Location
Indiana
Is your well 120v? That is all the cord is good for. And if you did use a 120v cord you would only have half the breakers on the panel function.

There is a lot more to it.
I didn't notice the cord was only 120v which my well pump does need 240v.

Thanks for the heads up.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,896
Location
NJ
That is incorrect, it's a 240 volt cord and connectors.
The cord will support 120v loads, 240v loads and 120/240v loads since it has L14-30 cap ends = 4 wire caps and cord.

Get a 30a power inlet box and add a 2pole 30a cb interlocked with the panel main cb.

This way you can manually select any load in the panel to operate under 30a total.
 

manwithtools

ALLIANCE MEMBER
Joined
Aug 24, 2015
Messages
13,772
Location
Lebanon, TN
The cord will support 120v loads, 240v loads and 120/240v loads
Isn't that what I typed? Zen said it was 120 only, I corrected that its 240, which by inference with the included neutral it will support both 240 and 120 volts. BTW, the referenced Item comes with a 30 amp inlet box. See post #1
 
To avoid these ads, REGISTER NOW!

manwithtools

ALLIANCE MEMBER
Joined
Aug 24, 2015
Messages
13,772
Location
Lebanon, TN
Sure, that's the way it could be interpreted if one chose to do do that. With all the back and forth in this thread, anything is possible. I'll let you guys wrap this up. I would hate to mislead...
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
but could I start with something like this, put in a cross-over switch and then just switch circuits on/off using the existing 200A circuit breaker?
gonna have to be more specific here. by crossover switch did you mean transfer switch? what type? make/model?

and the 200a breaker is the main? that should be off if you have a generator feeding the panel.
 
OP
Z

zendriver

Well-known member
Joined
Dec 10, 2014
Messages
29,839
Location
Indiana
gonna have to be more specific here. by crossover switch did you mean transfer switch? what type? make/model?

and the 200a breaker is the main? that should be off if you have a generator feeding the panel.
Then that would be a transfer switch. as far as which one, guess I'll ask here. :dunno:

It is a 200A main breaker in the main (only) circuit breaker box.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,635
Location
VT
Looks like a square D homeline.

Top right breaker needs to be moved, you have plenty of space. 30A or 50A goes in it's place. The homeline interlock kit will include a template, drills bits and bolts. It only allows the main OR the generator indeed breaker to be "on".


Then get a generator inlet sized to the breaker you added:


Connect the two with the appropriate 4 wires (individual wires need conduit, or watch the ratings on NM-B/UF-B).

Now in an outage flip the main "off", slide the interconnect, generator breaker "on", shut off large loads (as needed) and go fire up the generator.

This is very abbreviated
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,263
Location
Coastal NJ
Then that would be a transfer switch. as far as which one, guess I'll ask here. :dunno:

It is a 200A main breaker in the main (only) circuit breaker box.
Sounds like you are headed toward an interlock and generator inlet as described in post #29 and #30. And that is a good plan.


A transfer switch is often a double throw device ahead of the main breaker. When that is the case, it becomes the first disconnect and you have to isolate ground and neutral in the panel. The old "main" panel becomes a subpanel. An automatic transfer switch is another case. A manual transfer switch might look like this:

1744999037805.png
 

Codyboy

Well-known member
Joined
Jan 31, 2019
Messages
1,641
Location
S.E. TEXAS
Of course, I'd never do that.

No there isn't

You are putting lineman's lives at risk. Why would you do that? Would you be upset if someone killed your spouse, kids, or parent because of pure laziness?
Has that ever really happened?
I cannot think of one instance that it did .
I know its precautionary and as a lineman of 39 years I've never seen it.
As soon as I put my grounds on it will trip the generator breaker or choke the engine out.
But I or no one I know has seen it in action.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,635
Location
VT
Has that ever really happened?
I cannot think of one instance that it did .
I know its precautionary and as a lineman of 39 years I've never seen it.
As soon as I put my grounds on it will trip the generator breaker or choke the engine out.
But I or no one I know has seen it in action.
Why chance it?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
Has that ever really happened?
I cannot think of one instance that it did .
I know its precautionary and as a lineman of 39 years I've never seen it.
As soon as I put my grounds on it will trip the generator breaker or choke the engine out.
But I or no one I know has seen it in action.
Yes it has happened.

I have read several articles about it over the years.
 

WildBill

ALLIANCE MEMBER
Joined
Aug 20, 2021
Messages
2,003
Location
PNW
Has that ever really happened?
I cannot think of one instance that it did .
I know its precautionary and as a lineman of 39 years I've never seen it.
As soon as I put my grounds on it will trip the generator breaker or choke the engine out.
But I or no one I know has seen it in action.
It happened in my neighborhood when I was young. During hurricane Alicia in Houston a guy hooked up a generator by using a two male ended 240v cable and killed a fireman when they were helping the power company clean up downed lines. They were both from our neighborhood and we went to school with the fireman's kids, so it was a big deal.
 

Eric Brown

ALLIANCE MEMBER
Joined
Jun 14, 2024
Messages
672
I had a problem where my main overhead feed was draped over the gutter. I also have a lot of trees. So I decided to have the main buried and relocated to the end of the house. Then I had a whole house generator put in. It had to be located at least five feet from any windows or doors. Automatic transfer switch will kick the natural gas generator on after five seconds of a power outage. When power restored the generator shuts off. Talking with the electrical inspector he said a lot of new housing developers in the area are installing generators on the new houses as a selling point. So while more expensive than using your generator and some switching device, it adds to your property value and can run on natural gas. The generator is rated 22KW which can run my whole house. I will also offer to run some 20 amp extensions for my neighbors if needed. While I was at it, I also had a surge protector put in for the main panel. For me it was a good investment.

Bottom line: Safety first.
 

Firebrick43

Well-known member
Joined
May 12, 2015
Messages
14,024
Location
West central Indiana
Has that ever really happened?
I cannot think of one instance that it did .
I know its precautionary and as a lineman of 39 years I've never seen it.
As soon as I put my grounds on it will trip the generator breaker or choke the engine out.
But I or no one I know has seen it in action.

"July 13, 2005
South Carolina Lineman Killed by Generator Back Feed
Victim Helping Restore Power in Alabama

Sumter Electric Cooperative (SECO) officials report that a South Carolina lineman helping to restore power in Alabama after the damage caused by Hurricane Dennis was killed late Tuesday, reportedly by an improperly installed customer generator.

According to SECO Director of Public Affairs Barry Bowman, the lineman was helping to restore power lost during Hurricane Dennis to customers in Alabama. The report Bowman received indicated the lineman was working on a power line that was supposed to be dead. It was not.

?Tragically, the line this technician was working on was not dead,? said Bowman, ?The line he was trying to repair had been re-energized by a customer who had improperly hooked up a generator and created a back feed of electricity from the generator into the supposedly dead line. The death of a lineman who was there to help the victims of Hurricane Dennis was the horrible result.?

Bowman noted that the lineman?s name was not immediately released, but he was from South Carolina and worked for Pike Electric, Inc. in North Carolina.

Alabama authorities are looking for the person responsible and indicate that charges are pending."
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,896
Location
NJ
This is the key..........if it ain't grounded it ain't dead.......it's as simple as that.
You are either working it in one of two states, hot or dead, really no in between. Hot means every procedure executed is with that in mind, full PPE, isolation, etc.

Dead means you have grounds provided on both sides of the work area AND you still have some level of PPE. There is capacitive coupling that also occurs from close proximity lines as well as unintentional connections made by tree limbs, car bodies, crossed lines, etc.

With all of the possible sources that could (intentionally or unintentionally )energize a line, it's impossible to have a full lockout under that person's control, so you work it as considered hot. I can't believe any company EHS group or Union Rep would allow anything less.
 