Ok so upon discussion with other members here I've discovered my salesperson lied and I need to convert my generator to floating neutral to use it with my Generator Inlet w/interlock setup. I read up on how to do that on Generatorbible.com's writeup.
I bought this guy;
Popped the cover off;
Found the bonding wire;
Removed it from the frame;
And secured it back to the originating post;
Now the only wire going to the frame...
... goes up to the grounding post, and then onto the ground pins of my outlets;
And I popped the front panel just to look;
Before I fire this up, does everything look acceptable? And in this configuration will I need to have a grounding rod if I use the generator by itself / not hooked to a home grid? Or should I set it up with a switch so I can do both?