Generator floating neutral conversion. Check my work!

Noltz

Well-known member
Joined
Mar 10, 2020
Messages
377
Location
Ontario, Canada
Ok so upon discussion with other members here I've discovered my salesperson lied and I need to convert my generator to floating neutral to use it with my Generator Inlet w/interlock setup. I read up on how to do that on Generatorbible.com's writeup.

I bought this guy;


Popped the cover off;


Found the bonding wire;


Removed it from the frame;


And secured it back to the originating post;


Now the only wire going to the frame...


... goes up to the grounding post, and then onto the ground pins of my outlets;





And I popped the front panel just to look;




Before I fire this up, does everything look acceptable? And in this configuration will I need to have a grounding rod if I use the generator by itself / not hooked to a home grid? Or should I set it up with a switch so I can do both?

Thanks again,
 
To avoid these ads, REGISTER NOW!

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,117
Location
Northern Virginia
Confirm with a multi meter no continuity between neutral and ground at an outlet.

I put a switch on mine.

With 4-wire feed I do not have a separate ground rod. I will let the sparkles chime in.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Confirm with a multi meter no continuity between neutral and ground at an outlet.

I put a switch on mine.

With 4-wire feed I do not have a separate ground rod. I will let the sparkles chime in.

looks good, however, as said above, verify there is no continuity between neutral and ground, as well as the frame.

Also, if you plan on using this as a portable standalone unit (eg. jobsite, etc), you will want the neutral bonded. Easiest way to do this is to make a neutral bonding plug, where you jump the neutral to the ground pin on the plug, and plug into one of the outlets on the generator. Keep in mind, you wont be able to do this on a GFCI outlet on the generator as it will trip. Find a non-GFCI outlet to use for the bonding plug.

Also, a ground rod is not needed regardless of the number of wires in the feeder.
 
OP
N

Noltz

Well-known member
Joined
Mar 10, 2020
Messages
377
Location
Ontario, Canada
looks good, however, as said above, verify there is no continuity between neutral and ground, as well as the frame.

Done and verified. Details below.

Also, if you plan on using this as a portable standalone unit (eg. jobsite, etc), you will want the neutral bonded. Easiest way to do this is to make a neutral bonding plug, where you jump the neutral to the ground pin on the plug, and plug into one of the outlets on the generator. Keep in mind, you wont be able to do this on a GFCI outlet on the generator as it will trip. Find a non-GFCI outlet to use for the bonding plug.

Also, a ground rod is not needed regardless of the number of wires in the feeder.

Yes I plan on using this generator off-grid in the future, so I added a switched circuit to complete a bond where appropriate. Then I don't need to worry about losing a bonding plug.

I didn't have an 10 ga on hand so I doubled up on 14. It also fits the tight space better.


The wires pass up to a heavy switch. I'd like to find something SPST in the future but my local electrical shop didn't have one.


The only permanent modification was a hole in the end cap for the wiring. I used a rubber grommet and a heat sleeve to protect the wiring.
20201110-172417.jpg


And now when the switch is UP (floating), there is no continuity between neutral and ground. When the switch is DOWN (bonded), there is continuity between neutral and ground.


That spray you see is Fluid Film rustproofing. I applied it to the bare metal before assembling, the welded points and the inside of the frame.
 

JOE.G

Well-known member
Joined
Feb 4, 2013
Messages
765
Location
Eastern ( Catskills ) NY
To do this switch mod, I would run a wire from the neutral wire I unbonded to a switch and then from the switch to the lug the neutral was hooked to? Does it matter what kind of switch and which lug on the switch I use?
 
To avoid these ads, REGISTER NOW!
OP
N

Noltz

Well-known member
Joined
Mar 10, 2020
Messages
377
Location
Ontario, Canada
Yes, that's exactly what I did. Put a switch in line with the wire that connects the neutral terminal with the body of the generator. I like to make modifications like this reversible so I did not cut the old wire but looped it back.

You want to use the largest toggle switch you can reasonably fit. It will never make or break a connection, but it need to be able to carry current long enough to let the circuit breaker do its job. If I were building one from scratch I'd use a automotive battery disconnect switch.
 