I have an out building with no power. I was thinking of putting in a service panel with ciruit breakers and having a circuit for ceiling lights and a circuit for a few plugs. Again, this building is not hooked into any electrical power grid.

I have a Generac GP5500 generator (120/240v). The frame is grounded to the ground terminals of the AC outlets on the generator. Can I just hook this up to the panel, using appropriate size wire (2 hots, neutral, and ground, or do I need a separate ground rod? There would be no transfer switch.
 
To avoid these ads, REGISTER NOW!
To avoid these ads, REGISTER NOW!

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,656
Location
SE MI
I would install the ground rod and then disconnect the ground from the frame of the generator.

Bond ground and neutral in the load center in the building.
 
OP
S

slime

New member
Joined
Sep 18, 2014
Messages
2
wizard....why would you disconnect the ground from the frame of the generator? It is not hooked up to any electrical grid.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,272
Location
Modesto, CA
wizard....why would you disconnect the ground from the frame of the generator? It is not hooked up to any electrical grid.

I was gonna say the same thing. The neutral and ground will be bonded in the panel since its a main panel....
 