8k peak watt Champion. 4 wire plug. Have a generator sub panel off of the main panel with both generator and main tied to the grounding bar. Lost power from one leg at the generator cord to house. The leg with power jumped to 240 vac. With luckily only blew up a ground fault receptacle. Thinking that it has to do with the floating ground. Installed three volt, amp and 2 with amp reading on the gen side of the generator panel to that the voltage is good 120-240-120.
 
To avoid these ads, REGISTER NOW!

ihateminimumwage

Well-known member
Joined
Jan 26, 2012
Messages
3,961
Agree with wyliesdiesels, sounds like a loss of neutral issue. Check the output at the generator receptacle and check continuity through your cord to start.
 

Codyboy

Well-known member
Joined
Jan 31, 2019
Messages
1,708
Location
S.E. TEXAS
"Installed three volt, amp and 2 with amp reading on the gen side of the generator panel to that the voltage is good 120-240-120."

Wth does that even mean?

But yeah I agree with a neutral issue if you're getting or were getting 0-240-240.

That would indicate to me any how that you have no neutral at the panel and only 1 leg is loaded up . The other leg has 0 load.
 

Captain Spaulding

Well-known member
Joined
Feb 13, 2017
Messages
754
Location
Southern Indiana
Open Neutrals can cause weird symptoms
Not really weird. 120V loads are wired in series across the 240V lines with the loads on each side of the transformer in parallel. The neutral wire provides a bypass path for current flow to balance while keeping the voltage at the neutral junction constant. Without a neutral wire, the voltage of the neutral point moves toward the leg that’s most lightly loaded. If the loads are equal, everything works fine, but as soon as one side gets a heavier load the voltage on the other side goes up.
 
OP
F

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,992
Location
Peace Valley,mo
Three meters are wired line side of the generator at the generator panel in the house.
That way the power from generator will be correct before flipping the breakers from house to generator power.
120 vac meters line to neutral
240 vac meter line to line
 

Codyboy

Well-known member
Joined
Jan 31, 2019
Messages
1,708
Location
S.E. TEXAS
Did you ever figure out where you lost the neutral connection?
Was the issue in the main panel, subpanel, or affected both?
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,052
Location
NJ
Three meters are wired line side of the generator at the generator panel in the house.
That way the power from generator will be correct before flipping the breakers from house to generator power.
120 vac meters line to neutral
240 vac meter line to line
That's a good starting point, but.........high resistance connections can easily cause a voltage drop to occur across it and the load may see a different voltage than seen at no load. Watch the vm's as you apply the loads....they shouldn't swing too far from no load readings.
 

Captain Spaulding

Well-known member
Joined
Feb 13, 2017
Messages
754
Location
Southern Indiana
Three meters are wired line side of the generator at the generator panel in the house.
That way the power from generator will be correct before flipping the breakers from house to generator power.
120 vac meters line to neutral
240 vac meter line to line
A missing neutral does not show up on an unloaded circuit. Your meters will read exactly the same unloaded with or without a neutral in place.
 
To avoid these ads, REGISTER NOW!

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,313
Location
Dutzow Missouri
Not really weird. 120V loads are wired in series across the 240V lines with the loads on each side of the transformer in parallel. The neutral wire provides a bypass path for current flow to balance while keeping the voltage at the neutral junction constant. Without a neutral wire, the voltage of the neutral point moves toward the leg that’s most lightly loaded. If the loads are equal, everything works fine, but as soon as one side gets a heavier load the voltage on the other side goes up.
If you have not done the math it is very weird. the 500 Watt lamp will not light and the 5 Watt lamp will be super bright for a short time. 2025-07-30_20-11-43.jpg2025-07-30_20-11-43a.jpg
 
Last edited:

Codyboy

Well-known member
Joined
Jan 31, 2019
Messages
1,708
Location
S.E. TEXAS
A missing neutral does not show up on an unloaded circuit. Your meters will read exactly the same unloaded with or without a neutral in place.
Very true. Those voltmeter with no load only provide a false sense of what's going on.
Maybe add a small resistive 120 volt load like small heater or even a hairdryer. A clothes iron would work too.
We would use a small hairdryer when checking for open neutrals at a customer's home.
Shut off the main to keep from damaging customers equipment.

Weird. I posted this or at least thought I did yesterday.
Phone service *****.
 
OP
F

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,992
Location
Peace Valley,mo
Very true. Those voltmeter with no load only provide a false sense of what's going on.
Maybe add a small resistive 120 volt load like small heater or even a hairdryer. A clothes iron would work too.
We would use a small hairdryer when checking for open neutrals at a customer's home.
Shut off the main to keep from damaging customers equipment.

Weird. I posted this or at least thought I did yesterday.
Phone service *****.
If neutral is lost the 120vac meters would read 240 or a very little less because of the very little or no vac lost across two two meters would put them in series.
 
OP
F

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,992
Location
Peace Valley,mo
not how a series circuit works
Have three meters. Meters are wired before the generator sub panel with its own breaker/ safety disconnect to two watt meters. Two 120vac meters wired from each watt meter to neutral panel bar. 240 vax meter is wired across each watt meter. If neutral from panel to gen is lost the 120vac meters are across 240 vac and the two meters are in series.
 

Captain Spaulding

Well-known member
Joined
Feb 13, 2017
Messages
754
Location
Southern Indiana
Have three meters. Meters are wired before the generator sub panel with its own breaker/ safety disconnect to two watt meters. Two 120vac meters wired from each watt meter to neutral panel bar. 240 vax meter is wired across each watt meter. If neutral from panel to gen is lost the 120vac meters are across 240 vac and the two meters are in series.
and two meters in series across 240V will each measure 120V.
 