sberry
Banned
Since it's in the basement spoke we need gfci for laundry, washer?
The standard outlet (15/20A) needs GFCI protection.
If you have a 30A 240V "electric dryer" socket - I do not think that needs protection, but I stand to be corrected.
My understanding is a GFCI is require if you are "near" a water appliance (sink) or if the floor is concrete.
The price of GFCI/AFCI combo breakers is nuts !
My understanding is a GFCI is require if you are "near" a water appliance (sink) or if the floor is concrete.
The price of GFCI/AFCI combo breakers is nuts !
You are correct. Everything I said in my last post applies only to the 120V receptacles. The 240V dryer receptacle does not require AFCI or GFCI.

NEC seems to demand AFCI or GFCI on so many circuits anyway, so why not go all the way for safety's sake, and simplicity?
GFCI protection for 240v equipment and appliances is coming.
Nec 2020 will require it for air conditioning compressors
To make housing unaffordable.
For what purpose? Will most manufacturers just install it as part of the compressor/condenser assembly?
Any equipment cord and plug connected(50amps) in a deli, restaurant kitchen etc has to be GFCI
To make housing unaffordable.
Hmmm
I recently worked on a starbucks and the brand new espresso machines (cord and plug connected 208v) and their circuits were not required to be GFCI protected.
To protect someone from getting shocked or electrocuted.
From what i recall on the Facebook code discussion group where i read about it, someone was either shocked or electrocuted working on a compressor.
That would be a silly reason. If a unit is open and being serviced, isn't that out of scope for normal use per se?
Weird.
Out of scope for normal?
Have you ever seen someone service an AC unit?
Servicing of AC units often times requires the unit to be powered on to service it.
Such as adding refrigerant, checking pressures etc...
I see. So you think it should be equipped with GFCI in case the electrician that hooked it up failed to ground it properly or something like that?
That's understandable for that reason then household circuits like water heaters, ovens, stove tops etc should also have it then.
That would be a silly reason. If a unit is open and being serviced, isn't that out of scope for normal use per se?
Weird.