Have an enclosed cargo trailer. Ready to wire 2 flourescent lights inside. Being I don't have a fuse box, I have power coming into trailer with a waterproof 15a input, can I use a gfci receptacle to act as a fuse for the inside power supply? I'll run the power from the gfci to light switch to power the lights. Is this possible? Thanks for all the input, Paul
 
To avoid these ads, REGISTER NOW!

AntonLargiader

Well-known member
Joined
Nov 20, 2016
Messages
1,372
Location
Charlottesville, VA
GFCI does not act like a fuse. Does not trip on overcurrent.

Personally I would skip it*, and rely on the overcurrent protection of whatever is powering it. Run 12 AWG cables so they are protected even when plugged into a 20A circuit. Basically the trailer is just a light fixture at that point. Possibly with a receptacle (which some light fixtures have).

*EDIT: I'd skip the overcurrent protection. Running the power through a GFCI receptacle is a fine idea for ground fault safety.
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,038
Location
Modesto, CA
Thats a popular misconception.

Receptacle GFCIs DO NOT provide any sort of overcurrent protection.

However, i WOULD put one in the race trailer to protect against electric shocks.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Run number 12 cord, the reason is you can use multiple outlets without further over current protection. If you use 14 it really needs a fuse like a power strip has.
Same thing Anton said really.
 

mikegt4

Well-known member
Joined
Sep 12, 2005
Messages
3,274
Location
sw ohio
When I converted my van to a class B camper I used a 2 space breaker box. They are small, cheap and available at the big box stores.

Saw this trailer the other day with a 4 space box on the wall and a door in the floor to drop the RV style cable out. Other trailers had a RV electrical inlet on the outside of the trailer.
 

Attachments

  • 20170328_155045.jpg
    20170328_155045.jpg
    140.4 KB · Views: 24
To avoid these ads, REGISTER NOW!

tfi racing

Well-known member
Joined
Apr 19, 2008
Messages
2,907
Location
Cedar,BC
120V fluorescent fixtures in a cargo trailer are a dumb idea,just way too many LED options out there right now.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
If you are going to 30A service then you do need breakers, if its 120vg and has a 15 end on it to plug in to a common circuit you don't.
 
OP
S

scotty95

Active member
Joined
Mar 20, 2017
Messages
41
Location
mid michigan
Not putting 30a in this. Keeping 110. Can you just replace the flourescent tubes with LED? Or is the fixtures different for led. Thanks again.
 

Dick in Wisconsin

Well-known member
Joined
Mar 3, 2012
Messages
3,048
Location
Shawano, Wisconsin
110 can be 30a. 30a can be 100.

I would start out with LED fixtures in a trailer and NOT screw around with fluorescent fixture and then later try to adapt LED to those legacy fixtures.
 